Default I thought the fork was in the road.

Is this right.
Attached Thumbnails
thought-fork-road-jsw_p1010035.jpg  
Reply With Quote
  #2  
Old 8/9/06, 10:51 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: I thought the fork was in the road.

No, it's left.
Reply With Quote
  #3  
Old 8/9/06, 12:14 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: I thought the fork was in the road.

Plumbing drains should have a 1/4" per. ft. downward slope. All bends should be no greater than 45 deg. or a long sweeping 90 deg. elbow. (Two 45 deg. elbows = 90 deg. long sweeping 90 deg. elbow.)

Note: Their are exceptions to every rule!!

Plumbing vents should have a 1/8" per. ft. downward slope. (Hard 90 deg. elbows are acceptable as long as the pipe is not used as a drain also.)

Special Note: When one or more drain lines merge to another drain line the connection should be on a downward slope. (I prefer a minimum of a 30 deg. slope to provent backups.)


These are just some simplified rules of thumb to go by. These are not the Be-All-End-All rules of plumbing.

If they need a clean-out there (That is under the sink) it should tell you that they have problems there. I like to see clean-outs on horizontal drains every 20+ ft. Longer than that you need a snake greater than 25' long and becomes hard to work with even if it is a power unit.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #4  
Old 8/9/06, 12:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: I thought the fork was in the road.

There is no problem with that configuration unless your state or city/county follows the UPC. . .

It is referred to as a "common trap arm," utilizing a double wye, which is allowed by the IRC but prohibited by the UPC.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 8/9/06 at 12:21 PM..
Reply With Quote
  #5  
Old 8/9/06, 12:28 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,927
Default Re: I thought the fork was in the road.

I do not like the plastic water feed lines had a friend have one break last Easter when she was away $60,000;00 damage and she could not live in the home foe 4 months .
I always recommend upgrade to burst proof for all appliances .
This includes Washers saw what happens when the rubber hose breaks.
Roy Cooke sr . Royshomeinspection.com
Reply With Quote
  #6  
Old 8/10/06, 12:08 PM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,271
Default Re: I thought the fork was in the road.

Im wondering if you zoom that pic out a little will it actually show a double trapped sink, which is not allowed. I dont think we are getting the whole picture.
Reply With Quote
  #7  
Old 8/10/06, 12:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: I thought the fork was in the road.

Paul,

There are two traps, but this is not considered a "double trap." A double trap is two traps in series (one after another).

This is a "shared trap arm." As you are in CA, you should know that the CPC specifically prohibits this type of installation.

Quote:
CPC 1001.1 Each plumbing fixture, excepting those having integral traps or as permitted in Section 1001.2, shall be separately trapped by an approved type waterseal trap. Not more than one (1) trap shall be permitted on a trap arm.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 8/10/06, 12:35 PM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,271
Default Re: I thought the fork was in the road.

Jeff,

Are you assuming that there is another trap? We can all assume that there is a trap off the "assumed disposal" which we again are assuming is there. Did you see a different pic than I did?....Its still not right no matter what you call it. Thats what I was getting at. Not a deal breaker tho....Lets not get to excited about something that is simple to fix.
Reply With Quote
  #9  
Old 8/10/06, 12:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: I thought the fork was in the road.

If there is no trap at the disposal/second-sink side, it's wrong.

If there is a trap at the disposal side (which I am assuming), the entire setup is allowed by the IRC.

Regardless of the presence of a trap at the disposal/second-sink side, it is wrong for CA and the UPC.

I'm not interested in fixing it, I'm only interested in making the right call.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 8/10/06, 12:52 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,024
Default Re: I thought the fork was in the road.

Thanks for your insite Jeff, this was in a condo 3rd floor I have never seen a configuration like this before. No there was not a double trap(back to back) both sides of the sink were individualy trapped.
Reply With Quote
  #11  
Old 8/10/06, 5:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: I thought the fork was in the road.

Quote:
Originally Posted by bgraham
No there was not a double trap(back to back) both sides of the sink were individualy trapped.
Which is perfectly acceptable for FL and the IRC. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 8/11/06, 10:02 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: I thought the fork was in the road.

Quote:
Originally Posted by rcooke
I do not like the plastic water feed lines...I always recommend upgrade to burst proof for all appliances .

Roy, please tell me what type of material is "burst proof"?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 8/12/06, 12:06 PM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 775
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: I thought the fork was in the road.

Quote:
Originally Posted by jfunderburk
Roy, please tell me what type of material is "burst proof"?
No such animal.
Larry
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Commercial Class on the Road jfarsetta Inspection Education & Training 6 9/20/07 2:57 AM
Commercial Class on the Road jfarsetta Miscellaneous Discussion for Inspectors 0 9/19/07 11:32 AM
Reasonable Apprehension of Bias and Vexatious Actions of OAHI rwand1 Canadian Inspectors 12 8/26/06 10:07 AM


All times are GMT -4. The time now is 9:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts