I think this was a first for me. Thoughts?
I'd feel a little more comfortable if the pipe actually went inside the indirect waste receptor. 2nd floor location.
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
| Find an InterNACHI certified Arkansas Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Looks good to me. You want to be able to see if it has a leak and/or dripping.
|
|
#3
|
|||
|
|||
|
Looks fine. You especially don't want it touching.
|
|
#4
|
||||
|
||||
|
PVC pipe is not designed to withstand the temperature or preasure that may be comming from the hot water tank. The line should be replaced with ridged copper, Iron, or CVPC.
|
|
#5
|
||||
|
||||
|
It won't be exposed to pressure to speak of, but you are correct in that PVC is not allowed (not listed specifically in Table P2904.5).
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
|||
|
|||
|
That looks like CPVC to me. I'm going by the size and type of cement used.
|
|
#7
|
||||
|
||||
|
CPVC is slightly more yellowish in color.
Scott Gilligan Philadelphia Mold Inspections Philadelphia Home Inspections Philadelphia Commercial Inspections Philadelphia Licensed Home Inspector #34206 President The Greater Philadelphia Chapter of InterNACHI http://pa.nachi.org/greaterphiladelphia Philadelphia, Pennsylvania real estate professionals on ActiveRain.com |
|
#8
|
||||
|
||||
|
Indirect waste connection through and air-gap. Just as prescribed.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
|||
|
|||
|
That is what they require these days - although it is a lousy set up. Release water at full pressure and it will go all over the place. The justification that is given is that most times water will not release at full pressure or you will get steam. Just be careful if you test those things.
Bill Siegel Florida Home Inspection Team Inc. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Discharge into a vent? | Bob Smith, Jr. | Plumbing | 1 | 2/1/09 6:43 AM |
| Dryer vent & PVC discharge | dmacy | HVAC | 3 | 9/14/07 8:30 PM |
| TPR has PEX2 for discharge piping | jlybolt | Plumbing | 11 | 7/10/06 12:14 AM |