Is there potential for the TPR valve to not operate correctly with the stem being tight against the drywall like this? Or will the spring mechanism still function correctly? Thanks
|
|
#2
|
||||
|
||||
|
I guess testing it to see if it works or will work on its on is out of the question Mark.
Nice pick up. Marcel Cyr Home Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards Commercial Builder Ouellet Associaties Inc. |
|
#3
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's the before picture, this one is after they call the plumber back in.
John Kogel www.allsafehome.ca |
|
#4
|
|||
|
|||
|
It won't work. The TPR valve stem has to be able to move outwards.
|
|
#5
|
||||
|
||||
|
Quote:
That would be correct. It will not work. |
|
#6
|
||||
|
||||
|
Is it in a garage? Because the plumber just broke the firewall if it is by putting a hole in the drywall. He must be from here!!!
|
|
#7
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
John Kogel www.allsafehome.ca |
![]() |