Default TPR & Combusiton Air

Qusetion: Can two TPR extensions go in to one pipe?
And if burner chambers are sealed, is combustion air still required?
Attached Thumbnails
tpr-and-combusiton-air-sierra-012.jpg  
Reply With Quote
  #2  
Old 9/14/06, 4:30 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: TPR & Combusiton Air

Quote:
Originally Posted by thejnicki
Qusetion: Can two TPR extensions go in to one pipe?
I believe they have to go full size and separately to an acceptable location.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 9/14/06, 7:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: TPR & Combusiton Air

Quote:
Originally Posted by thejnicki
Qusetion: Can two TPR extensions go in to one pipe?
Absolutely not.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 9/14/06, 7:45 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR & Combusiton Air

Quote:
Originally Posted by thejnicki
And if burner chambers are sealed, is combustion air still required?
are you referring to a secondary form of combustion air?
Reply With Quote
  #5  
Old 9/14/06, 8:24 PM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: TPR & Combusiton Air

Jeff, do you have any refference for the TPRs?
Reply With Quote
  #6  
Old 9/14/06, 8:44 PM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,271
Default Re: TPR & Combusiton Air

Im not jeff but...

P2803.6.1 states that the tpr drain must:

7. Discharge to a termination point that is readily abservable by the building occupants.

10. Not terminate more than 6 inches above the floor or wase receptor.

Also there is a good illustration of "Water Heater in Attic" In Code Check Plumbing..Page 21.



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #7  
Old 9/14/06, 8:49 PM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: TPR & Combusiton Air

I know those TPR codes, I just want some solid info about two TPR extensions going into on line..Cant find anything that proves to me that the application is improper..
Reply With Quote
  #8  
Old 9/14/06, 9:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: TPR & Combusiton Air

Quote:
Originally Posted by thejnicki
Jeff, do you have any refference for the TPRs?
I can't find the CA reference that specifically prohibits this, but I'll keep looking.

In the mean time, here is the "generally accepted" rule.


IPC 504.6 Requirements for discharge piping.
The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall:

4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.





IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 9/14/06, 9:24 PM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,271
Default Re: TPR & Combusiton Air

If thats the case Tim then rule 4 would be:

4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #10  
Old 9/14/06, 9:37 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: TPR & Combusiton Air

2003 IRC:

P2803.6.1 Requirements of discharge pipe. The outlet of a
pressure relief valve, temperature relief valve or combination
thereof, shall not be directly connected to the drainage system.
The discharge from the relief valve shall be piped full size sepa-
rately to the floor, to the outside of the building or to an indirect
waste receptor located inside the building. In areas subject to
freezing, the relief valve shall discharge through an air gap into
an indirect waste receptor located within a heated space, or by
other approved means. The discharge shall be installed in a
manner that does not cause personal injury or property damage
and that is readily observable by the building occupants. The
discharge from a relief valve shall not be trapped. The diameter
of the discharge piping shall not be less than the diameter of the
relief valve outlet. The discharge pipe shall be installed so as to
drain by gravity flow and shall terminate atmospherically not
more than 6 inches (152 mm) above the floor. The outlet end of
the discharge pipe shall not be threaded and such discharge pipe
shall not have a valve installed.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 9/14/06, 10:05 PM
thejnicki's Avatar
thejnicki thejnicki is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Vacaville, CA
Posts: 251
Default Re: TPR & Combusiton Air

Thank to All for the help..
Reply With Quote
  #12  
Old 9/14/06, 11:10 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR & Combusiton Air

I don't like to see them combined either, but I called the City of Seattle and they say it is OK as long as the pipe increases in size (lots of town houses where the heaters are back to back use this set-up). So like many things, it may vary from jurisdiction to jurisdiction.
Reply With Quote
  #13  
Old 9/15/06, 2:11 AM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,271
Default Re: TPR & Combusiton Air

Tim,
did you check the underneath of the water heater to see if it had screening for ventilation?



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #14  
Old 9/15/06, 8:12 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: TPR & Combusiton Air

Fred Lambert
JADES Home Inspection Service, LLC
ICC Certification # 5166981-R5
Phone: 770-448-8726
Cell: 404-314-6339
Email: JADES_HIS@Bellsouth.com
Below is a technical notice that I found on the American Water Heater website. It deals with the thermocouple in the FVIR water heater.


TECHNICAL DIAGNOSIS AND SOLUTIONS BULLETIN
Flammable Vapor Ignition Resistant (FVIR) Gas Water Heaters
With the new safety standards that have mandated FVIR (Flammable Vapor Ignition Resistant) water
heaters, it is important for you (our customers and service technicians) to be able to easily diagnose and
implement solutions that will take care of operational problems with these types of water heaters. This
bulletin is intended to help you avoid typical installation issues with the water heater or the environment in
which it's installed, and to help you understand what to do when you are trying to solve a problem.
The pilot thermocouple used in FVIR water heaters includes a one-shot temperature switch that opens the
thermocouple circuit if the water heater is not receiving adequate combustion air for any reason. With
several thousand FVIR water heaters now installed in the field, data suggests burner and pilot shutdown
problems are being perceived as a thermocouple problem. Feedback regularly includes ?my old water
heater never had a problem?. Let?s examine the reasons the temperature switch in your thermocouple is
being activated:
1. The water heater may be starved for combustion air. This causes the burner flame to get lazy
and waiver around in the combustion chamber, causing the temperature switch inside the
thermocouple to trip. Here are the things to check for and correct:
a. The water heater may be located in a closet or space that does not have openings for
combustion air to get to the water heater. Openings in the closet must be provided per the
installation instructions, which tell you how much open area you need. IMPORTANT:
The instructions only cover the needs of the water heater. The air requirements of all
gas-fired or air-consuming appliances in the closet or space must also be considered.
Don?t forget an electric dryer, it also consumes air.
b. The openings in the closet are smaller than what is needed to supply adequate combustion
air. Review the installation instructions and information as noted in (a) above.
c. The water heater may be installed in a utility room or closet along with a furnace or air
handler, with a return air duct that has not been attached, or it may have leaks that are not
sealed. When this condition exists, the return air system creates a significant negative
pressure on the installed space and significant down draft of the flue occurs at the water
heater. Even if the utility room or closet has a door with louvers in it, a negative pressure
may still exist. (When checking, be sure the furnace or air handler is ON and the doors
are closed). When a down draft is created, the combustion products from the water heater
can no longer exit up through the vent system. The flame inside the water heater will
become lazy and wander around, causing the temperature sensor inside the thermocouple
to trip. If you can?t fix the problem, notify a water heater service organization. THIS IS
A SAFETY ISSUE AND THIS CONDITION MUST BE FIXED by having the return air
duct system corrected. For a temporary solution, keep any doors on the utility room or
closet wide open.
2. There may not be a draft at the water heater draft hood. With the water heater operating for 3
to 5 minutes, check for a draft at the inlet to the draft hood with a match or a small amount of
smoke. Remember, when checking, be sure all appliances in the installed space are on and the
doors are closed. If there isn?t a draft, and you have ruled out or corrected items a, b and c above,
check the vent system for restrictions or obstructions. Correct these and recheck for draft. You
should also check the vent termination to be sure it is the correct height when it exits the home or
structure. Refer to the installation instructions for how to evaluate this. Correct the vent height if
needed and re-check the draft.
6510350
March 2005
3. The installed environment may be dirty.
The flame arrestor (stainless steel slotted plate) in the bottom of the combustion chamber is
precision designed to combust flammable vapors safely inside the combustion chamber in the
event that flammable vapors are present around your water heater. Although the flame arrestor
tends to shed lint from the surface, in some cases it can become restricted. When this happens, the
burner flame will become lazy and overheat the combustion chamber causing the temperature
sensor inside the thermocouple to trip. You can diagnose this condition by inspecting the flame
arrestor. To correct this and improve the environmental condition, clean the flame arrestor using
a soft brush to clean the slots in the flame arrestor. A toothbrush works well. Be sure to clean
both sides of the flame arrestor. Then vacuum the area free of any lint, etc. If you think the
installation will be prone to repeated plugging, an external filter is available that can be easily
installed. This will greatly extend the run time of the water heater in a dirty environment and will
allow for easy periodic external cleaning. Call our service assistance number found in your
installation manual or on your water heater to request the filter and installation instructions.
4. A flammable vapor accident has occurred
Of course, our desire to reduce the likelihood of a flammable vapor incident is the main reason
that the new technology has entered the marketplace. So, if a flammable vapor event occurs, the
temperature inside the combustion chamber will increase, causing the temperature sensor inside
the thermocouple to trip. This event can be diagnosed as a flammable vapor accident if you see
that the flame arrestor has been discolored like it has been overheated. There is no repair for this
condition and the water heater must be replaced. If a flammable vapor incident has occurred, you
must call the service assistance number found in your installation manual or on your water heater
and report it. We will ask you to return the water heater to us at no cost to you.
Included in this kit, you?ll find all parts and instructions necessary to complete your installation of this kit.
PLEASE READ AND FOLLOW THE INSTRUCTIONS FULLY.
__________________

I would look at the instruction/service manual for the specific unit in question.

They are supposed to be in a protected pouch on the side of the unit.

Aren't they? YES



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #15  
Old 9/15/06, 10:16 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: TPR & Combusiton Air

This is what I saw on the roof. Then I went into the garage and saw the combustion air vent blocked on the garage wall and..... look at the HWT pic.
Attached Thumbnails
tpr-and-combusiton-air-100_8454-medium-small-.jpg (Small).JPG
Views:	75
Size:	21.5 KB
ID:	5579   tpr-and-combusiton-air-vent-covered-medium-small-.jpg (Small).JPG
Views:	84
Size:	38.3 KB
ID:	5580   tpr-and-combusiton-air-blanket-touches-flue-medium-small-.jpg (Small).JPG
Views:	78
Size:	26.7 KB
ID:	5581  




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On