Default TPR and flush valve on T

Is it ok to have the tpr valve joined with the flush valve into the floor drain?

Will provide .a picture later after I down load.

Just do not recall seeing it before.

On a hot water tank of course
Reply With Quote
  #2  
Old 12/30/08, 4:26 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: TPR and flush valve on T

Waiting for pic Bob but it doesn't sound right.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 12/30/08, 5:18 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: TPR and flush valve on T

No, a TPRV discharge "shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building". But, then again you are in Chicago so who knows?



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #4  
Old 12/30/08, 6:26 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: TPR and flush valve on T

No it is not O.K.



"It's not what you believe that matters...it matters what you believe!"
Reply With Quote
  #5  
Old 12/30/08, 6:42 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: TPR and flush valve on T

Ok ,sorry but I took a nap.
Here is a picture and please explain the reasoning if you know it.

tpr-and-flush-valve-t-dsc06306-small-.jpg.JPG
Views:	122
Size:	41.0 KB
ID:	25875
Reply With Quote
  #6  
Old 12/30/08, 7:10 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: TPR and flush valve on T

Quote:
Originally Posted by relliott View Post
Ok ,sorry but I took a nap.
Here is a picture and please explain the reasoning if you know it.

Attachment 25875
Yeah i'd say that is obviously F 'ED up.

There needs to be an air gap, something to do with anti blockage. What if the drain clogs????

It looks like only efficiency was observed but with disregard for safety.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #7  
Old 12/30/08, 7:14 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: TPR and flush valve on T

Quote:
Originally Posted by jtribuzio View Post
Yeah i'd say that is obviously F 'ED up.

There needs to be an air gap, something to do with anti blockage. What if the drain clogs????

It looks like only efficiency was observed but with disregard for safety.
Yeah that was my first thought.
Lake point tower and they use FPE stab loc,plus lint buckets for dryers there.

Second time inspecting there and both had that.

Got any lingo to back me up?
Reply With Quote
  #8  
Old 12/30/08, 7:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: TPR and flush valve on T

The "reasoning" would be that the installer just didn't know any better.

I won't speculate as to "why" people do what they do, but I'm happy to point it out when they don't have a clue. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 12/30/08, 7:26 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: TPR and flush valve on T

Thanks Jeff but that is not straight enough.
I just found out I have part of IPC here on file from a Frank Carrio submission.

504.6 Requirements for discharge piping.
The discharge piping serving a pressure relief valve, temperature relief valve or combination thereof shall:
1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room as the water heater.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor through an air gap located in a conditioned area.
6. Discharge in a manner that does not cause personal injury or structural damage.
7. Discharge to a termination point that is readily observable by the building occupants.
8. Not be trapped.
9. Be installed so as to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above the floor or waste receptor.
11. Not have a threaded connection at the end of such piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section 605.4 or materials tested, rated and approved for such use in accordance with ASME A112.4.1.

Looks like #4 covers it and I wonder about #2 as it leaves me confused.

I would also note lack of a drain pan.

They have 2 heaters with one in the kitchen and one for the bathroom .
Both are electric with no gas in this 68 story building.
Reply With Quote
  #10  
Old 12/30/08, 7:26 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: TPR and flush valve on T

Quote:
Originally Posted by relliott View Post
Yeah that was my first thought.
Lake point tower and they use FPE stab loc,plus lint buckets for dryers there.

Second time inspecting there and both had that.

Got any lingo to back me up?
hmmmmmmm. here is some thing but still looking.

.....c) With the exception of special water heaters used for space heating in addition to hot water supply, as provided in subsection (a)(9) of this Section, water that leaves the potable water system for heating, cooling, use in equipment or other similar uses shall not be returned to the potable water distribution system. When such water is discharged to the building drainage system it shall be discharged through a fixed air gap.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting



Last edited by jtribuzio; 12/30/08 at 7:29 PM..
Reply With Quote
  #11  
Old 12/30/08, 7:29 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: TPR and flush valve on T

Quote:
Originally Posted by jtribuzio View Post
hmmmmmmm.
Yeah
I was suprised to and since the bottom 2 screws were missing on a loose cover I opened the FPE.
Reply With Quote
  #12  
Old 12/30/08, 7:34 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: TPR and flush valve on T

Section 890.APPENDIX H Indirect Waste Piping #1

Section 890.ILLUSTRATION E Indirect Waste Connection

(Referenced in Section 890.1010(b))

"TPR discharge pipe should have an air gap at the terminating end that is within 6 inches of floor. " hows that sound




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #13  
Old 12/30/08, 7:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: TPR and flush valve on T

Quote:
Originally Posted by relliott View Post
Looks like #4 covers it and I wonder about #2 as it leaves me confused.
Mike covered that in post #3. . .


An air-gap is used when the extension is routed to a point where it would be subject to freezing. Unfortunately, air-gaps are not very effective for the pressure and volume produced by a relief valve.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #14  
Old 12/30/08, 7:41 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: TPR and flush valve on T

that galv. ell sure looks threaded from texas, but who's writing this report



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #15  
Old 12/30/08, 7:47 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: TPR and flush valve on T

Quote:
Originally Posted by badair View Post
that galv. ell sure looks threaded from texas, but who's writing this report
Good catch,almost missed that (ha)

I had to move a little faster than normal and am looking at pics to make up for it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 1:59 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts