Default TPR connected to hose

Found this in yesterdays inspection. A hose was connected to TPR which lead to sump pit. Haven't seen this before and I don't think its a good idea. If tpr is leaking how will you know, so I called it out. Who else has a problem with this.
Attached Thumbnails
tpr-connected-hose-dscf0162.jpg  
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/30/11, 1:14 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: TPR connected to hose

I would hope that everyone here has a problem with it. I know I do.

Btw... I would take that as a clue that the TPRV is actually leaking.
Reply With Quote
  #3  
Old 12/30/11, 2:46 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: TPR connected to hose

The word Whip comes to mind



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #4  
Old 12/30/11, 2:48 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: TPR connected to hose

Quote:
Originally Posted by jjonas View Post
I would hope that everyone here has a problem with it. I know I do.

Btw... I would take that as a clue that the TPRV is actually leaking.
Maybe KEVIN will chime in.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 12/30/11, 2:49 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: TPR connected to hose

Piping has to be approved for distribution piping. "Hose" is not.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 12/30/11, 4:07 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: TPR connected to hose

Sorry I only follow the InterNachi plumbing inspection guidlines and am not a Code Inspector but right it up anyways and back it up by the 2006 RBC.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #7  
Old 12/30/11, 4:10 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: TPR connected to hose

Quote:
Originally Posted by kwood View Post
Sorry I only follow the InterNachi plumbing inspection guidlines and am not a Code Inspector but right it up anyways and back it up by the 2006 RBC.
So, since you are not a code inspector, you are saying this is okay???

Kevin, meet "The Meeker". "The Meeker", meet Kevin.

I don't know what else to say!!!
Reply With Quote
  #8  
Old 12/30/11, 4:11 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: TPR connected to hose

Quote:
Originally Posted by jjonas View Post
Kevin, meet "The Meeker". "The Meeker", meet Kevin.

I don't know what else to say!!!
Funny, I don't care who you are!



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 12/30/11, 4:16 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: TPR connected to hose

Quote:
Originally Posted by jfunderburk View Post
Funny, I don't care who you are!
I suspect "The Meeker" may take issue with it!
Reply With Quote
  #10  
Old 12/30/11, 4:36 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: TPR connected to hose

Does InterNachi say it is OK! I think not.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #11  
Old 12/30/11, 4:43 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: TPR connected to hose

Quote:
Originally Posted by kwood View Post
Does InterNachi say it is OK! I think not.
And the back-peddaling begins...!
Reply With Quote
  #12  
Old 12/30/11, 6:44 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: TPR connected to hose

End of hose is not visible to view leaking ,pipe should be the same as that approved for water supply pipe,see no required 1/4" per foot slope.(no threaded pipe allowed to prevent additions is allowed)(Nice workaround attempt)

Last that thing can be kinked.

Note: get a battery backup on that sump and must be in the sticks as I see it is propane energized.

Last edited by belliott; 12/30/11 at 6:47 PM..
Reply With Quote
  #13  
Old 12/30/11, 6:57 PM
Rick Strand's Avatar
Rick Strand Rick Strand is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Calgary, Alberta, Canada
Posts: 266
Default Re: TPR connected to hose

No drip leg on the water heater either.



Rick Strand, CPI
CAHPI Associate
Strand Home Inspections Inc.
Calgary, Alberta, Canada
Serving Calgary, Okotoks, Airdrie, Chestermere and Cochrane Alberta
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/30/11, 8:16 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: TPR connected to hose

Wow! I can't believe how much I have learned from the MB today.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #15  
Old 12/31/11, 3:36 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: TPR connected to hose

The T&P (Test and Pressure) valve on water heater needs a 3/4 threaded pipe to extend within 6 inches of floor for safety. (PVC is not approved for hot water use). I recommend repair by a qualified person. You must also have an air gap on the end of it to make sure it is not defective.
You will have to look close on the discharge pipe to make sure it is not approved for the discharge temperature before assuming that the PVC will not be OK.
Remember for all those that are new 150 PSI and 210 degrees F is needed stamped or written on the discharge pipe itself.
Nice comment from Rick!
Attached Thumbnails
tpr-connected-hose-discharge-pipe-tpr-valve.jpg  



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 12/31/11 at 3:52 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flex hose connected to fireplace manifild....Need advice dnasser Inspecting HVAC Systems 3 8/28/11 10:28 AM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 2:00 PM
CPVC Connected to Water Heater krigler Plumbing Inspections 9 10/20/09 4:54 PM
Entran II Hose Class Action Suit jbushart Inspecting HVAC Systems 0 3/3/09 10:46 AM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM


All times are GMT -4. The time now is 1:59 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts