Default Tpr Discharge line is PEX

Just wanted to know is pex line acceptable for use as the tpr discharge line on a water heater.
My thought is no because it is flexable. What are your thoughts please.tpr-discharge-line-cross-linked-polyethylene-100_0086.jpg





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America)
  #2  
Old 12/7/09, 11:38 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Tpr Discharge line is PEX

Can it handle 200 degrees?

Check search we just did this one)
Reply With Quote
  #3  
Old 12/7/09, 11:48 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Tpr Discharge line is PEX

From the Plastic Pipe and Fittings Association (PPFA)

http://www.ppfahome.org/pex/faqpex.html

What are temperature limitations for PEX?
PEX tubing can be used up to 200° Fahrenheit for heating applications. For plumbing, PEX is limited to 180° F. Temperature limitations are always noted on the print line of the PEX tubing.. PEX systems are tested to and can be used with standard T and P relief valves that operate at 210” F and 150 psi.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #4  
Old 12/7/09, 11:56 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Tpr Discharge line is PEX

Quote:
Originally Posted by sstanczyk View Post
From the Plastic Pipe and Fittings Association (PPFA)

http://www.ppfahome.org/pex/faqpex.html

What are temperature limitations for PEX?
PEX tubing can be used up to 200° Fahrenheit for heating applications. For plumbing, PEX is limited to 180° F. Temperature limitations are always noted on the print line of the PEX tubing.. PEX systems are tested to and can be used with standard T and P relief valves that operate at 210” F and 150 psi.
Thanks Shephen I figured the temp was ok just not sure if the hot water made the PEX line like a garden hose and would spray everywhere instead of down. And the fitting on the picture is reduced in size and on any other application you cannot reduce the size less than 3/4.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #5  
Old 12/8/09, 2:02 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Tpr Discharge line is PEX

Per the IRC, any pipe approved for water distribution is approved for the TPR discharge, for the 14,000th time.




“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 12/8/09, 4:37 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Tpr Discharge line is PEX

Quote:
Originally Posted by jfunderburk View Post
Per the IRC, any pipe approved for water distribution is approved for the TPR discharge, for the 14,000th time.

I must have told you a million times Joe, stop exaggerating.

Nice chart by the way, thanx.
Reply With Quote
  #7  
Old 12/8/09, 10:44 PM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,274
Default Re: Tpr Discharge line is PEX

Is the inside diameter of the elbow the same as the inside diameter of the pex? If not I would think this would not be allowed.



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #8  
Old 12/9/09, 12:15 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Tpr Discharge line is PEX

Quote:
Originally Posted by ppendley View Post
Is the inside diameter of the elbow the same as the inside diameter of the pex? If not I would think this would not be allowed.
Paul this is not in response to your post

The fitting goes inside of the pex line so it would be smaller. So if its inside diameter of the fitting meets the requirments than it would be ok but it does not seem that anyone here seems to know.
I understand the pipe is ok for the temp that is why it is installed in the house on the hot water side of the plumbing. But the graph, chart or diagram does not show if the pipe will flex under high pressure spraying everybody that is in its path and with the elbow fitting being smaller that will help to increase the steam and high pressure water as it is coming out and spraying. have you ever seen a fire hose under pressure out of control and it isn't hot water. I under stand that the pex pipe is ok temp wise. But they dont show installation insturctions for the fly by night contractors that use what ever they have left over to save money. Ie In some timelines outlets were not grounded, wires were covered with cloth, afci were not heard of. Just because it states that pex is ok to be used with tpr discharge lines does not tell me that the set up is ok and proper or safe for that matter.
Mark





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #9  
Old 12/9/09, 1:34 AM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,274
Default Re: Tpr Discharge line is PEX

Why would it not be in response to my post? If the elbow is a smaller diameter then it would not be correct...in my opinion.

Pex is ok if its rated for that purpose but should be continious to the exterior without restrictive fittings I would think.



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #10  
Old 12/9/09, 1:35 AM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,274
Default Re: Tpr Discharge line is PEX

Not to mention the connection methods



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #11  
Old 12/9/09, 11:09 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Tpr Discharge line is PEX

Quote:
Originally Posted by mnorthrup View Post
Just wanted to know is pex line acceptable for use as the tpr discharge line on a water heater.
My thought is no because it is flexable. What are your thoughts please.Attachment 33739
Did it terminate within 4-6" of the ground in a downward fashion? Did they put a pvc or copper elbow at the end?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #12  
Old 12/9/09, 11:48 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: Tpr Discharge line is PEX

No it had no fitting at the end and was tucked under the earthquake straps.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #13  
Old 11/12/10, 9:48 PM
bknowlton bknowlton is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Artesia, NM
Posts: 28
Default Re: Tpr Discharge line is PEX

I think it is not allowed to exit the wall to the exterior. It specifically states it cannot be used in contact with sunlight on most of the pipe I have seen, and is always broken off where the contractor has used it anyway. I would think it must have a copper elbow on the end that extends inside the wall to prevent sunlight from coming incontact with the PEX.
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/12/10, 10:41 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Tpr Discharge line is PEX

Quote:
Originally Posted by bknowlton View Post
I think it is not allowed to exit the wall to the exterior. It specifically states it cannot be used in contact with sunlight on most of the pipe I have seen, and is always broken off where the contractor has used it anyway. I would think it must have a copper elbow on the end that extends inside the wall to prevent sunlight from coming incontact with the PEX.
You are mistaken. Please post a copy of some literature from a manufacturer of pex that says it should not be exposed to daylight.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #15  
Old 11/12/10, 10:48 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Tpr Discharge line is PEX

Quote:
Originally Posted by ppendley View Post
Pex is ok if its rated for that purpose but should be continious to the exterior without restrictive fittings I would think.
There is nothing in the IRC that prohibits fittings. Can't speak for the UBC, but it's probably the same.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
And another A/C condensate line discharge question bwilliams Inspecting HVAC Systems 4 11/6/08 11:20 PM
Slope of waste drain line. mlong Plumbing Inspections 5 4/23/08 9:54 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical Inspections 0 12/2/07 1:43 PM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 7:59 AM


All times are GMT -4. The time now is 1:59 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts