Default TPR expiration?

I was told yesterday by several seasoned HI's that water heater TPR valves have a 3 year life expectancy and, if older than that, should be recommended for replacement. I looked at my TPR valve and see no mfg nor expiration date on the metal tag. I can find no reference to such a thing on the Cash Acme website either. Were these old codgers pulling my leg?
Reply With Quote
  #2  
Old 12/15/07, 7:39 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: TPR expiration?

Quote:
Originally Posted by mboyett
I was told yesterday by several seasoned HI's that water heater TPR valves have a 3 year life expectancy and, if older than that, should be recommended for replacement. I looked at my TPR valve and see no mfg nor expiration date on the metal tag. I can find no reference to such a thing on the Cash Acme website either. Were these old codgers pulling my leg?
I think some one is pulling your keg .
Never read that never seen it in print and I read a lot .
Next time you see them ask where is a good place to get a good price as you do not like the idea of paying what the local hard ware stor wants .
.... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 12/15/07, 7:50 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: TPR expiration?

I've never heard such a thing. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 12/15/07, 8:00 PM
dpotts dpotts is offline
InterNACHI Member
 
Join Date: Dec 2007
Location: Winchester Springs, On
Posts: 60
Default Re: TPR expiration?

Now this is interesting......... 2 months ago I saw a failed valve that was installed 4 months ago. By failed I mean it could not be reset to stop cold water.

I don't believe this 3 year replacement is relevant.

Last edited by dpotts; 12/16/07 at 9:32 AM..
Reply With Quote
  #5  
Old 12/15/07, 8:00 PM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 351
Cool Re: TPR expiration?

Hi! Michael;
I beleive they are just having some fun, Iv'e never heard of that and I have been around for quiet some time.
Regards len
Reply With Quote
  #6  
Old 12/15/07, 8:15 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: TPR expiration?

Quote:
Originally Posted by mboyett
I was told yesterday by several seasoned HI's that water heater TPR valves have a 3 year life expectancy and, if older than that, should be recommended for replacement. I looked at my TPR valve and see no mfg nor expiration date on the metal tag. I can find no reference to such a thing on the Cash Acme website either. Were these old codgers pulling my leg?
LOL.

Don't let the Kentucky licensing board hear of you recommending replacement of something with no visible defects!!!!



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #7  
Old 12/15/07, 8:44 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: TPR expiration?

I just received a Watts TPR valve installation manual and in it there is the following statement:
Quote:
REINSPECTION OF T&P RELIEF VALVES:
WARNING: Temperature and Pressure Relief Valves should be inspected AT LEAST ONCE EVERY THREE YEARS, and replaced, if necessary, by a licensed plumbing contractor or qualified service technician, to ensure that the product has not been affected by corrosive water conditions and to ensure that the valve and discharge line have not been altered or tampered with illegally. Certain naturally occurring conditions may corrode the valve or its components over time, rendering the valve inoperative. Such conditions can only be detected if the valve and its components are physically removed and inspected.


Do not attempt to conduct an inspection on your own.

Contact your plumbing contractor for a reinspection to assure continuing safety.

FAILURE TO REINSPECT THIS VALVE AS DIRECTED COULD RESULT IN UNSAFE TEMPERATURE OR PRESSURE BUILD-UP WHICH CAN RESULT IN SERIOUS INJURY OR DEATH AND/OR SEVERE PROPERTY DAMAGE.

I believe that is where this 'old-wive's tale' may have started. Big difference between inspect and replace.
Reply With Quote
  #8  
Old 12/15/07, 8:52 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: TPR expiration?

Reminds me of the pair of old glasses where the "subscription ran out"

This was a saying from one of my mom's dear old country friends



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #9  
Old 12/15/07, 9:50 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: TPR expiration?

http://www.onehourplumbing.com.au/wh...es_it_tick.htm

Your hot water unit works hard at supplying your family with constant hot
water, yet unfortunately they tend to be neglected and taken for granted. And as a car, which if poorly maintained can cost more to run so too your hot water unit.
If you look at the safety devices that protect your tank, you will understand how preventative maintenance will go a long way to ensuring you get the maximum life expectancy and save a lot of money $$$ on running costs.
Temperature, Pressure, Relief Valve


The Temperature, Pressure, Relief valve (TPR) is there to stop the Hot Water Tank from expanding, or even exploding under pressure build up.
The TPR valve also releases water when the thermostat malfunctions and the temperature inside the tank exceeds 90 degrees Celsius.
It is the most important safety device on any Gas, Electric or Solar Hot Water Unit and should be checked for adequate performance. It should be replaced at intervals not exceeding 5 years or more frequently in areas where there is a high incidence of water deposits.
Another thing to look at is the relief valve drainpipe. It must not be blocked or restricted in any way, (wasps are notorious for building nests inside the pipe and completely blocking any overflow). The relief valve will release a small amount of water during its normal heating cycle. If the discharge is more than a bucket full over 24 hours, it will need to be checked.
The relief valve-easing lever should be activated every six months,



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #10  
Old 12/16/07, 10:41 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: TPR expiration?

Anyone check those during an inspections?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #11  
Old 12/16/07, 10:57 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: TPR expiration?

Quote:
Originally Posted by mnahrgang
Anyone check those during an inspections?
Yes, required in Texas (TREC SOP) but there are numerous reasons we may have for not activating the lever and add this info to our reports.

(k) Water heaters. The inspector shall:

(1) report the energy source;

(2) inspect the unit and report as in need of repair fittings that leak or are corroded;

(3) report as in need of repair temperature and pressure relief valve piping that lacks gravity drainage, is improperly sized (no smaller than the outlet fittings), has deficiencies in material, or lacks a correct termination;

(4) report as in need of repair a temperature and pressure relief valve that does not operate when the valve is of an operable type and operation will not cause damage to persons or property as reasonably determined by the inspector (for example, it would be reasonable not to operate the valve if there is improper or undetermined termination of the drain pipe, a corroded or damaged valve, improper installation of valve or drain pipe, the drain pipe is of inappropriate material or there is no water supply cut-off valve at the unit);

(5) report as in need of repair any broken or missing parts, covers or controls;

(6) report as in need of repair deficiencies in the burner, flame and burner compartment, the operation of heating elements and the condition of wiring;

(7) report as in need of repair deficiencies in materials used for the gas branch line and the connection to the appliance, the absence of a gas shut-off valve, or a valve that is not properly located, is inaccessible, or leaks;

( if applicable, report as in need of repair deficiencies in the vent pipe, draft diverter, draft hood and their condition, draft, proximity to combustibles and vent termination point, observing for adequate combustion and draft air;

(9) report as in need of repair the lack of a safety pan and drain (including the termination of the drain line) when applicable;

(10) report as in need of repair an unsafe location or installation; and

(11) inspect garage units or units which are located in rooms or enclosures opening into a garage and report as in need of repair the following:

(A) a lack of protection for physical damage to the unit; and

(B) burners, burner ignition devices or heating elements, switches or thermostats that are not a minimum of 18 inches above the lowest garage floor elevation.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 12/16/07 at 11:08 AM..
Reply With Quote
  #12  
Old 12/16/07, 2:58 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: TPR expiration?

http://www.nachi.org/waterheaterdisc...leased2007.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #13  
Old 12/16/07, 8:10 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: TPR expiration?

Quote:
Quote:
Originally Posted by mnahrgang
Anyone check those during an inspections?
I inspect how they're installed, but I never test them. That's from personal experience working on many rental properties and others. That many times, due to mineral deposit, they won't shut-off completely and continue to drip or slowly drain. I don't want to leave a house I inspected with water running from the discharge. And Thanks Nick.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 12/16/07 at 11:16 PM..
Reply With Quote
  #14  
Old 12/16/07, 10:24 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: TPR expiration?

Quote:
Originally Posted by dpotts
Now this is interesting......... 2 months ago I saw a failed valve that was installed 4 months ago. By failed I mean it could not be reset to stop cold water.

I don't believe this 3 year replacement is relevant.
I see alot of them fail on brand new heaters. Back when I was doing construction full time we use to carry an extra relief valve with us when we installed a new water heater. It is like carrying an extra thermocouple with the new sealed burner type Whirlpool heaters. Failures were just too common.
Reply With Quote
  #15  
Old 12/17/07, 1:54 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: TPR expiration?

Quote:
Originally Posted by ccurrins
I inspect how they're installed, but I never test them. That's from personal experience working on many rental properties and others. That many times, due to mineral deposit, they won't shut-off completely and continue to drip or slowly drain. I don't want to leave a house I inspected with water running from the discharge. And Thanks Nick.
Yea that's my thinking too. I've never done it in the past, but was wonding if maybe I should be.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:00 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts