Default TPR has PEX2 for discharge piping

New home construction - PEX 2 used for TPR discharge piping at tank. On the exterior it was plumbed with copper. From what I understand the discharge piping can only be galvanized steel, hard drawn copper or cpvc.
First time I have seen this setup. Any comments would be appreciated.
Also foam was used around flue. I dont think foam can be used for this purpose. Any comments would be appreciated.
Attached Thumbnails
tpr-has-pex2-discharge-piping-100_7077.jpg   tpr-has-pex2-discharge-piping-100_7078.jpg   tpr-has-pex2-discharge-piping-100_7076.jpg  
Reply With Quote
  #2  
Old 7/9/06, 12:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: TPR has PEX2 for discharge piping

James,

I don't have the IRC handy...but my understanding is the discharge pipe can be the following:

* Hard Drawn Copper, CPVC, polybutylene or steel......

polybutylene...imagine that......well thats because the pipe would be fine...but the fitting would blow to heck...thehehe



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 7/9/06, 12:44 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: TPR has PEX2 for discharge piping

The requirements for pipe material are at IRC P2803.6.1: "Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for such use in accordance with ASME A112.4.1."

A screen shot of the table is attached, and PEX is on the list. (Think about it, if PEX is suitable for distribution of hot water, why not as a discharge for it? About the fittings, don't they withstand all the pressure in the system under normal conditions and wouldn't you think there is a pretty high safety factor built in? I don't know the limitations on the fittings, but the table seems to be clear.)

P2904-05.pdf



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 7/9/06, 8:46 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: TPR has PEX2 for discharge piping

PEX is acceptable here.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #5  
Old 7/9/06, 10:04 AM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 229
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR has PEX2 for discharge piping

I personally think the TPR discharge piping should be rated for the same temperature and pressure that pops the valve. Most water heaters have valves that open at 150 psi, or 212 degrees. Is pex or cpvc rated that high?
Stu
Reply With Quote
  #6  
Old 7/9/06, 12:19 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: TPR has PEX2 for discharge piping

Quote:
Originally Posted by sspradling
I personally think the TPR discharge piping should be rated for the same temperature and pressure that pops the valve. Most water heaters have valves that open at 150 psi, or 212 degrees. Is pex or cpvc rated that high?
Stu
If the drain pipe were closed, I would agree with you. But with an open pipe, it won't have to take the pressure or the temperature for any extended period of time, usually something on the order of seconds. If you look at pressure and temperature ratings, the rating tests usually take place over minutes or hours.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year

Last edited by rray; 7/9/06 at 4:40 PM..
Reply With Quote
  #7  
Old 7/9/06, 1:35 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR has PEX2 for discharge piping

Piping is rated at 1000 psi at 180 degrees. I got that off the pex markings on the piping.
Reply With Quote
  #8  
Old 7/9/06, 3:46 PM
Peter Foxe Smothers's Avatar
Peter Foxe Smothers Peter Foxe Smothers is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Shreveport, LA
Posts: 873
Default Re: TPR has PEX2 for discharge piping

Joe,
Where did you get your copy of the IRC in pdf form?



Foxe Smothers ( Owner / Inspector )
Pelican State Inspection
Your Best Choice for Home Inspection in the Shreveport & Bossier City Area!

www.PelicanState.Net
www.ShreveportHomeInspector.net
www.BossierCityHomeInspector.net
foxe@pelicanstate.net
LSBHI #10399
Reply With Quote
  #9  
Old 7/9/06, 4:01 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR has PEX2 for discharge piping

what do you guys think about what appears to be can insulation around the vent in picture 3. Is this acceptable. Is this fire stop? (see first post)
Reply With Quote
  #10  
Old 7/9/06, 4:41 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: TPR has PEX2 for discharge piping

There is some foam that is rated for high temperatures, but could you verify that the foam used is the high-rated foam?



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 7/9/06, 11:21 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: TPR has PEX2 for discharge piping

Quote:
Originally Posted by psmothers
Joe,
Where did you get your copy of the IRC in pdf form?
ecodes.biz. Paid $54.50 to download the PDF file of the entire 2006 IRC.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 7/10/06, 12:14 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,733
Default Re: TPR has PEX2 for discharge piping

Quote:
Originally Posted by jfunderburk
ecodes.biz. Paid $54.50 to download the PDF file of the entire 2006 IRC.
Nice Joe

http://www.ecodes.biz/product.cfm?ca...1&cat_type=pay



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help - Polybutylene Pipes Rick G Plumbing 39 2/12/09 9:16 AM
Bonding both hot and hold supply pipes kshepard Plumbing 22 5/4/08 9:00 AM
Do you put polybutylene in the Summary? jfunderburk Plumbing 36 11/27/07 12:56 AM
Bonding Piping 101....Good To Know ! pabernathy Electrical 37 4/28/07 12:25 PM
plastic piping? Scott Schultz Plumbing 5 3/28/07 2:40 AM


All times are GMT -4. The time now is 3:25 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts