Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information Kenton H. Shepard, CMI is very trusted source of information
Send a message via ICQ to kshepard
Default TPR overflow pipe: limit to the # of bends?

Saw one today with 5 bends. Would this create too much back-pressure if the valve is activated?




Kenton Shepard, NACHI member # 04082383
Peak to Prairie Inspection Service
Certified Master Inspector (CMI)

Inspection of Conventional,
Log, Strawbale and
Historic Homes
(303) 258-8289

Reply With Quote
  #2  
Old 11/2/06, 2:32 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 8,545
Brian E. Kelly .
Default Re: TPR overflow pipe: limit to the # of bends?

Probably not, if the pipe/tube was joined correctly.
03 IRC P2803.6.1 does not call out maximum number of bends. As long as it is gravity drained.





For my next trick I will need a volunteer

ps some of the opinions I have posted here may or may not be factually based.




AZ Cert # 39975
AZ Pest # 050898
Reply With Quote
  #3  
Old 11/2/06, 9:22 AM
mbailey mbailey is offline
New User
 
Join Date: Feb 2003
Location: Sioux Falls, SD
Posts: 25
mbailey hasn't had much positive or negative feedback
Please Note: mbailey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR overflow pipe: limit to the # of bends?

You may want to check manufacturer installation requirements.

For example ...from AO Smith manual...
The discharge opening must not be blocked or reduced in size under any
circumstances. Excessive length, over 30 feet (9.14 m), or use of more
than four elbows can cause restriction and reduce the discharge
capacity of the valve, see Figure 10.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing 36 11/27/07 12:56 AM
Identify ABS defective pipe mcyr Plumbing 5 10/28/07 11:18 PM
Pipe hangers Ian Gills Plumbing 4 5/11/07 6:17 PM
Help - Polybutylene Pipes Rick G Plumbing 37 9/12/06 4:10 AM


All times are GMT -4. The time now is 10:09 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics