Default TPR overflow pipe: limit to the # of bends?

Saw one today with 5 bends. Would this create too much back-pressure if the valve is activated?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #2  
Old 11/2/06, 2:32 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: TPR overflow pipe: limit to the # of bends?

Probably not, if the pipe/tube was joined correctly.
03 IRC P2803.6.1 does not call out maximum number of bends. As long as it is gravity drained.
Reply With Quote
  #3  
Old 11/2/06, 9:22 AM
Mark E. Bailey Mark E. Bailey is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Lakeland, Florida
Posts: 28
Send a message via AIM to mbailey
Default Re: TPR overflow pipe: limit to the # of bends?

You may want to check manufacturer installation requirements.

For example ...from AO Smith manual...
The discharge opening must not be blocked or reduced in size under any
circumstances. Excessive length, over 30 feet (9.14 m), or use of more
than four elbows can cause restriction and reduce the discharge
capacity of the valve, see Figure 10.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 36 10/27/10 11:21 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 9:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 7:39 PM
Pipe hangers Ian Gills Plumbing Inspections 4 5/11/07 6:17 PM


All times are GMT -4. The time now is 9:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts