Default TPR pipe material?

its amazing how many TPR pipes i see that are improper. i pretty much have been writing up anything that isnt copper (rigid). i have also seen a few that are labeled "TPR Pipe" but are just flimsey, flexible, thin plastic.

the IRC and UPC are different and sometimes i get caught in between. ie, IRC states pipe has to teminate within 6" to floor, IRC is 6"-24". IRC says it can drain into a pan and UPC cannot, etc... without determining what code is for each community, how do you all determine what you use for refernce?
Reply With Quote
  #2  
Old 10/2/06, 12:23 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,927
Default Re: TPR pipe material?

Quote:
Originally Posted by bmargiotti
its amazing how many TPR pipes i see that are improper. i pretty much have been writing up anything that isnt copper (rigid). i have also seen a few that are labeled "TPR Pipe" but are just flimsey, flexible, thin plastic.

the IRC and UPC are different and sometimes i get caught in between. ie, IRC states pipe has to teminate within 6" to floor, IRC is 6"-24". IRC says it can drain into a pan and UPC cannot, etc... without determining what code is for each community, how do you all determine what you use for refernce?
Those flimsy are approved for TPR discharge Remember there is little pressure open discharge .Cost about $10:00 each
Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #3  
Old 10/2/06, 2:26 PM
Raymond N. Newman Raymond N. Newman is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Avondale, AZ
Posts: 128
Send a message via Skype™ to rnewman1
Default Re: TPR pipe material?

Quote:
Originally Posted by bmargiotti
... without determining what code is for each community, how do you all determine what you use for refernce?
In first line what is saver, but I also believe it is best to know what the local requirments are and just to clarify, I would not reference code.
Reply With Quote
  #4  
Old 10/2/06, 3:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: TPR pipe material?

The State of Ohio follows the IBC/IRC. So I would assume that most Counties and incorporated jurisdictions follow the same, or at least a close version. Therefore, it would make sense that you use the "within 6 inches" rule.

Personally, I prefer the "6 to 24 inch" rule which just happens to be what my area follows.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 10/3/06, 11:33 AM
bmargiotti bmargiotti is offline
New User
 
Join Date: Feb 2005
Location: Berea, OH
Posts: 66
Please Note: bmargiotti is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR pipe material?

thanks Jeff. makes sense to me!
Reply With Quote
  #6  
Old 10/9/06, 12:02 PM
bmargiotti bmargiotti is offline
New User
 
Join Date: Feb 2005
Location: Berea, OH
Posts: 66
Please Note: bmargiotti is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR pipe material?

ok then, so what about materials. both the IRC and UPC state:
"Same materials as allowed for water distribution" [2803.6.2]
"only galvanized, hard-drawn copper, CPVC" [608.5]

personally, i hate this because they sell those $10 POS and i know if a plumber came in they would tell the client or realtor that, "Your home inspector is an idiot, it says right on the pipe for TPRV drain!"
Reply With Quote
  #7  
Old 10/9/06, 12:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: TPR pipe material?

That's because you're relying on Code Check for your references.

Code Check is a great tool as a "refesher" if you are already familiar with the codes in your jurisdiction. These help to eliminate the need to carry around a library in your vehicle.

The problems with Code Check are - they give only partial information, and often they give the wrong reference. However, if you are already familiar with the codes, Code Check will get you close enough to find the applicable information.

Here is what the UPC actually states (bold is mine);

"galvanized steel, hard drawn copper piping and fittings, CPVC, or listed relief valve drain tube with fittings"

and here is the reference given from Code Check for the IRC;

"P2803.6.2 Relief valve drains. Relief valve drains shall comply with Section P2904.5 or ASME A112.4.1."

So that $10 POS is actually allowed.

If you are going to make definitive statements, you need to get the code books.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 10/9/06 at 12:52 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PVC waste lines lagudo Plumbing Inspections 10 3/6/11 2:57 AM
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 36 10/27/10 11:21 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 9:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 7:39 PM


All times are GMT -4. The time now is 8:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts