Just finished with this home - it's in great shape, but found this...that's the top of an electric water heater. This is as close as I could get because the owners have storage shelves in front of it. How can I report this... ?
Attached Thumbnails
tpr-valve-p1020515-528-x-396-.jpg.jpg
Views:	124
Size:	30.3 KB
ID:	11697  



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.

Last edited by acox; 5/20/07 at 3:14 PM..
Reply With Quote
  #2  
Old 5/20/07, 3:14 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: TPR valve

Quote:
Originally Posted by acox
Just finished with this home - it's in great shape, but found this...that's the top of an electric water heater. This is as close as I could get because the owners have storage shelves in front of it.
Do you have a question?
Reply With Quote
  #3  
Old 5/20/07, 3:15 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 919
Default Re: TPR valve

Sorry, I was in the process of editing my post - I went back and realized it didn't make sense. Any suggestions for wording the report?



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #4  
Old 5/20/07, 3:19 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: TPR valve

I see a nomal install if the overpressure device at the top is permitted in your area. That device takes the place of a bladder type expansion tank.
Reply With Quote
  #5  
Old 5/20/07, 3:23 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 919
Default Re: TPR valve

OK - I haven't seen this before. I just wasn't sure if it could be tied to the TPR outlet.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #6  
Old 5/20/07, 3:27 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: TPR valve

More information here
Reply With Quote
  #7  
Old 5/20/07, 3:46 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 919
Default Re: TPR valve

That helps alot - Thanks for the info!



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #8  
Old 5/20/07, 6:36 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: TPR valve

The TPR discharge must be separate from any other system. It appears to be tied into the other PR valve with a T-fitting.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 5/20/07, 7:10 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: TPR valve

Quote:
Originally Posted by jpope
The TPR discharge must be separate from any other system. It appears to be tied into the other PR valve with a T-fitting.
I agree, I thought that TPR discharge had to go directly to the floor with no T-fittings at all.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #10  
Old 5/20/07, 7:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: TPR valve

Quote:
Originally Posted by jsieg
I agree, I thought that TPR discharge had to go directly to the floor with no T-fittings at all.
Not necessarily "to the floor," but no T-fittings are allowed in the discharge piping. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 5/20/07, 8:04 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: TPR valve

Quote:
Originally Posted by jpope
Not necessarily "to the floor," but no T-fittings are allowed in the discharge piping. . .
Yes, I skipped a bit of info didn't I.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #12  
Old 5/20/07, 8:14 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 639
Default Re: TPR valve

Direct link to the Watts installation instructions:

http://www.watts.com/pdf/1910868.pdf
Reply With Quote
  #13  
Old 5/20/07, 8:15 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: TPR valve

Quote:
Originally Posted by jpope
Not necessarily "to the floor," but no T-fittings are allowed in the discharge piping. . .
Not to beat you up, just like to have references, do you remember one? See "common sense" is ofen not good enough.

tom
Reply With Quote
  #14  
Old 5/20/07, 8:39 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: TPR valve

They may drain to outside. It should still terminate < or = to 6", or to at drain pan.




Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #15  
Old 5/21/07, 12:37 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,039
Default Re: TPR valve

Quote:
Originally Posted by tdietrich1
Not to beat you up, just like to have references, do you remember one? See "common sense" is ofen not good enough.
T-fittings are not specifically addressed, so the intent is somewhat subject to interpretation.


P2803.6.1 states "The discharge from the relief valve shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building."

So I guess one would have to ask, what is the purpose of a T-fitting?





IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mixing valve question cmettel Plumbing 2 6/17/07 11:03 PM
Backwater valve in new homes? ccrooker Canadian Inspectors 16 11/28/06 8:47 AM
Water Heater Pressure Valve wrosario Plumbing 3 7/7/06 8:27 PM
Pool inspections/ valve check dbucknavich Ancillary Services & Additional Topics 1 6/21/06 4:33 PM
Manifold connections, mixing valve question jclark1 Plumbing 14 6/15/06 11:46 PM


All times are GMT -4. The time now is 2:19 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts