Just finished with this home - it's in great shape, but found this...that's the top of an electric water heater. This is as close as I could get because the owners have storage shelves in front of it. How can I report this... ?
Last edited by acox; 5/20/07 at 3:14 PM.. |
|
#2
|
||||
|
||||
|
Quote:
|
|
#3
|
|||
|
|||
|
Sorry, I was in the process of editing my post - I went back and realized it didn't make sense. Any suggestions for wording the report?
|
|
#4
|
||||
|
||||
|
I see a nomal install if the overpressure device at the top is permitted in your area. That device takes the place of a bladder type expansion tank.
|
|
#5
|
|||
|
|||
|
OK - I haven't seen this before. I just wasn't sure if it could be tied to the TPR outlet.
|
|
#6
|
||||
|
||||
|
|
|
#7
|
|||
|
|||
|
That helps alot - Thanks for the info!
|
|
#8
|
||||
|
||||
|
The TPR discharge must be separate from any other system. It appears to be tied into the other PR valve with a T-fitting.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Quote:
Jason Sieg, CMI Davison, MI NACHI05091399 Knowing the current condition, to make a wise decision.
President, Great Lakes-East Chapter Join NACHI Great Lakes - East Chapter http://mi.nachi.org/greatlakes-east/about.html ssieg@gfn.org |
|
#10
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
||||
|
||||
|
Quote:
Jason Sieg, CMI Davison, MI NACHI05091399 Knowing the current condition, to make a wise decision.
President, Great Lakes-East Chapter Join NACHI Great Lakes - East Chapter http://mi.nachi.org/greatlakes-east/about.html ssieg@gfn.org |
|
#12
|
|||
|
|||
|
|
|
#13
|
||||
|
||||
|
Quote:
tom |
|
#14
|
||||
|
||||
|
They may drain to outside. It should still terminate < or = to 6", or to at drain pan.
Jason Sieg, CMI Davison, MI NACHI05091399 Knowing the current condition, to make a wise decision.
President, Great Lakes-East Chapter Join NACHI Great Lakes - East Chapter http://mi.nachi.org/greatlakes-east/about.html ssieg@gfn.org |
|
#15
|
||||
|
||||
|
Quote:
P2803.6.1 states "The discharge from the relief valve shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building." So I guess one would have to ask, what is the purpose of a T-fitting? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Mixing valve question | cmettel | Plumbing | 2 | 6/17/07 11:03 PM |
| Backwater valve in new homes? | ccrooker | Canadian Inspectors | 16 | 11/28/06 8:47 AM |
| Water Heater Pressure Valve | wrosario | Plumbing | 3 | 7/7/06 8:27 PM |
| Pool inspections/ valve check | dbucknavich | Ancillary Services & Additional Topics | 1 | 6/21/06 4:33 PM |
| Manifold connections, mixing valve question | jclark1 | Plumbing | 14 | 6/15/06 11:46 PM |