  #16  
Old 5/21/07, 9:47 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: TPR valve

Thanks for all the info - Jeff, I thought that was true, and it definitely connects with the other pressure valve. I'm going to write it up with your citation above and recommend it be changed.

This house is out in the boonies, with a deep well water supply.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #17  
Old 5/21/07, 12:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: TPR valve

Quote:
Originally Posted by jpope
T-fittings are not specifically addressed, so the intent is somewhat subject to interpretation.


P2803.6.1 states "The discharge from the relief valve shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building."

So I guess one would have to ask, what is the purpose of a T-fitting?

Everyone needs to keep in mind that code requirements vary by state and even in smaller units of government within states. Check with your local AHJ for what's acceptable in your area.

In Wisconsin plumbing is regulated by Comm 82. I have posted the relevant section below.
---------------------------------------------------------------------------
From WI Comm 82


(d) Safety devices. Water heaters shall be equipped with safety
devices as specified in this paragraph.
1. All pressurized storage−type water heaters and unfired hot
water storage tanks shall be equipped with one or more combination
temperature and pressure relief valves. The temperature
steam rating of a combination temperature and pressure relief
valve or valves shall equal or exceed the energy input rating in
BTU per hour of the water heater. No shut off valve or other
restricting device may be installed between the water heater or
storage tank and the combination temperature and pressure relief
valve.
Note: The temperature steam rating of a combination temperature and pressure
relief valve is commonly referred to as the AGA temperature steam rating.
2. All pressurized non−storage type water heaters shall be
provided with a pressure relief valve installed at the hot water outlet
with no shut off valve between the heater and the relief valve.
3. Temperature and pressure relief valves shall be installed so
that the sensing element of the valve extends into the heater or tank
and monitors the temperature in the top 6”of the heater or tank.
4. A vacuum relief valve shall be installed in each water
heater and hot water storage tank which, when measured from the
bottom of the heater or tank, is located more than 20 feet above any
faucet or outlet served by the heater or tank.
5. Every relief valve which is designed to discharge water or
steam shall be connected to a discharge pipe.
a. The discharge pipe and fittings shall be made of a material
acceptable for water distribution piping in accordance with s.
Comm 84.30 (4) (e) 1.
b. The discharge pipe and fittings shall have a diameter not
less than the diameter of the relief valve outlet.
c. The discharge pipe may not be trapped.
d. No valve may be installed in the discharge pipe.
e. The discharge pipe shall be installed to drain by gravity
flow to a floor served by a floor drain or to a receptor in accordance
with s. Comm 82.33(. The outlet of the discharge pipe shall terminate
within 6”over the floor or receptor, but not less than a distance
equal to twice the diameter of the outlet pipe. The outlet of
the discharge pipe may not be threaded.
f. The discharge pipe for a water heater shall terminate within
the same room or enclosure within which the water heater or hot
water storage tank is located.
----------------------------------------------------------------------------
The the watts pressure regulator device in the original post would seem to be an allowed device but I have yet to see one in use. I do see expansion tanks in use on some newer construction.





Last edited by mlarson; 5/21/07 at 12:19 PM..
Reply With Quote
  #18  
Old 5/22/07, 12:17 AM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: TPR valve

I went over this with my client... I explained that there were differing opinions about the "correctness" of the T fitting, etc. I basically told them that the repair would be very cheap, and could be done quickly. For less money than a nice dinner, they would have peace of mind. I basically told them that if there ever WAS a problem, and the WH (and house) blew up, it would cost them a heck of a lot more - and they readily agreed it needed to be fixed! Nothing like putting it in perspective....!





http://www.smileycentral.com/sig.jsp?pc=ZSzeb096&pp=ZN



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #19  
Old 5/22/07, 7:32 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: TPR valve

Also check manufactures listings



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #20  
Old 5/27/07, 12:36 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,091
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR valve

Quote:
Originally Posted by jpope
Not necessarily "to the floor," but no T-fittings are allowed in the discharge piping. . .
To an approved and or acceptable discharge area. Drain line off the valve may not be elevated above the valve, (Must gravity drain away from the valve).
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mixing valve question cmettel Plumbing Inspections 2 6/17/07 10:03 PM
Backwater valve in new homes? ccrooker Canadian Inspectors 16 11/28/06 7:47 AM
Water Heater Pressure Valve wrosario Plumbing Inspections 3 7/7/06 7:27 PM
Pool inspections/ valve check dbucknavich Ancillary Inspection Services & Additional Topics 1 6/21/06 3:33 PM
Manifold connections, mixing valve question jclark1 Plumbing Inspections 14 6/15/06 10:46 PM