Default TPR Valve: Odd Locations

This is now the second time I have seen these odd places for TPR Valves, and both times I wrote it up as needing correction.

However, I still believe that I am right that neither one of these is correct, because I can't find a code that justifies either of these, as well as just plain common sense on how TPR Valves work.

The first, if I am correct, will not work because it will never sense the over pressure of the water heater, especially if the water is shut off to the water heater, and it seems to me that the over pressure would come out of the water fixtures first.

See Photo 1464 (They connected to the water supply entrance at the front of the property)

Now the second, if I am correct, will not work because it could cause greater problems by forcing hot water into the gas line, causing greater issues that I do not want to get into (Just imagine hot water shooting out of the range burners or furnace).

See Photo 1465 (Yes, that is a TPR valve connected to the flex gas supply and going back into the gas inlet on the water heater.)

Well, let me know if I am wrong, I am about to write this up to be corrected, unless I hear otherwise.

P.S. I called a local plumber that had written a note on a previous similar inspection and he said that the one from the first image was to code, but when I asked him what the code was, he said he had to look it up, and he would call me. He never called back and has not returned any of my messages. I think he thought I was dumb.
Attached Thumbnails
tpr-valve-odd-locations-dscf1464-800x600-.jpg   tpr-valve-odd-locations-dscf1465-800x600-.jpg  



David K. Kraemer
Inspector Catch-it
http://www.inspectorcatchit.com
(661) 948-3375
Reply With Quote
Find an InterNACHI certified Wyoming Home Inspector (and anywhere else in North America)
  #2  
Old 3/26/09, 6:53 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 20,738
Default Re: TPR Valve: Odd Locations

It's a Watts 210 which shuts down the gas supply if the temp gets to high.

Installation Instructions(PDF)



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 3/26/09 at 7:09 PM.. Reason: edited to remove pressure
Reply With Quote
  #3  
Old 3/26/09, 6:59 PM
David K. Kraemer David K. Kraemer is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Lancaster, CA
Posts: 28
Default Re: TPR Valve: Odd Locations

Then does that supercede the need for a TPR Valve? According to the brochure, it still needs a TPR Valve.



David K. Kraemer
Inspector Catch-it
http://www.inspectorcatchit.com
(661) 948-3375

Last edited by dkraemer; 3/26/09 at 7:03 PM..
Reply With Quote
  #4  
Old 3/26/09, 7:05 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 20,738
Default Re: TPR Valve: Odd Locations

Quote:
Originally Posted by dkraemer View Post
Then does that supercede the need for a TPR Valve? According to the brochure, it still needs a TPR Valve.
You need to check with your local AHJ for your area.

Doesn't your first pic who the Pressure relief for the same system?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 3/26/09, 9:59 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,661
Default Re: TPR Valve: Odd Locations

:d:d:d:d:d
Attached Thumbnails
tpr-valve-odd-locations-jsw_p3180393.jpg  



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 3/26/09, 10:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,430
Default Re: TPR Valve: Odd Locations

David,

Watts 210 valves are not recognized by the State of CA. You are in Lancaster/Palmdale, which is unincorporated Los Angeles county. Your areas follow the CBC. The homeowner or plumber is required to obtain a variance from Building and Safety to install one of these.

The City of Santa Clarita (where I live) allows these.

If/when installed properly, these are a suitable alternative for the standard TPR valve. However, they MUST be used in conjunction with a pressure-relief valve on the water supply system. There can be NO shutoff valves between the PRV and the heater. This means, the PRV should be on the outlet side of the heater, because there is usually a shutoff valve on the inlet side of the heater.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Seisco TWH does not need a TPR valve? jyost Plumbing 4 10/6/08 8:01 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 1:26 AM
Nice One For You - Lesson 1 pabernathy Electrical 18 12/16/06 10:03 AM


All times are GMT -4. The time now is 7:46 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts