Default TPR Valve termination unknown

I could not find where this TPR valve terminated...why they did this I'd like to know.....lot of work for what benefit?

I couldn't see the termination because it was under the front porch which was a deck built just above the ground...and I'm too fat to squeeze under it....my flashlight couldn't see it either.

I don't plan to write it up unless somebody convinces me otherwise.....anybody? Main reason for posting is to see if anyone knows the reasoning behind running the TPR out of an unfinished crawl?
Attached Thumbnails
tpr-valve-termination-unknown-35navajo-023.jpg  
Reply With Quote
  #2  
Old 4/5/06, 5:47 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: TPR Valve termination unknown

That TPR has to run to the floor from what I understand & terminate 6 to 12 inch. from the floor. Temp & pressure will only let the water run so far... Any water in that pipe could freeze and provent the TPR from working properly.

If not freezing, animals, dirt or something else could block the flow of water.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #3  
Old 4/5/06, 5:55 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,067
Default Re: TPR Valve termination unknown

Quote:
Originally Posted by tneumann
I don't plan to write it up unless somebody convinces me otherwise.....anybody? Main reason for posting is to see if anyone knows the reasoning behind running the TPR out of an unfinished crawl?
It is probably what the building inspector and plans called for.

In case the TPR did open, the crawlspace wouldn't get flooded.
Reply With Quote
  #4  
Old 4/5/06, 5:58 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Valve termination unknown

I got this from code check...


.Temperature & Pressure Relief
Temperature-pressure relief required . . . . . . . . . . . .[2803.1] {506.2,608.3}
Drain ends outside <=6in. {6-24in.} from ground . . .[2803.6.1] {608.5}
win. min., no trap, no reduction, no thread on end [2803.6.1] {608.5}
Drain line may not run uphill . . . . . . . . . . . . . . . .[2803.6.1] {608.5}
Watts 210 also req's. pressure relief valve
.................................................. .....F-m11, F-m12 [2803.1] {Ř, check local}

It is okay like this, but that sounds like a reasonable explanation as to why....I wonder why the T with a cap on it then? hmmmm...it isn't holding up my report or nothing...I am just a curious fellow.
Reply With Quote
  #5  
Old 4/5/06, 7:21 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: TPR Valve termination unknown

Tony:

The installation of the TPRV drain violates Code if the point of termination is not visible.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 4/5/06, 7:23 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Valve termination unknown

i agree.....also violates common sense which is what I will write up....

If a TPR valve leaks and you cannot see it leak...did it in fact leak or not?
Reply With Quote
  #7  
Old 4/5/06, 7:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: TPR Valve termination unknown



Tony,

Your state follows the UPC and the end should be visible. . .

608.5. Relief valves located inside a building shall be provided with a drain, not smaller than the relief valve outlet, of galvanized steel, hard drawn copper piping and fittings, CPVC, or listed relief valve drain tube with fittings which will not reduce the internal bore of the pipe or tubing (straight lengths as opposed to coils) and shall extend from the valve to the outside of the building with the end of the pipe not more than two (2) feet (610 mm) nor less than six (6) inches (152 mm) above the ground or the flood level of the area receiving the discharge and pointing downward. Such drains may terminate at other approved locations. No part of such drain pipe shall be trapped or subject to freezing. The terminal end of the drain pipe shall not be threaded.





IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/5/06, 7:48 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Valve termination unknown

Thanks wirelessjeff.....
Reply With Quote
  #9  
Old 4/5/06, 7:53 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: TPR Valve termination unknown

Quote:
Originally Posted by tneumann
Thanks wirelessjeff.....
Next appointment is at 4:30. I have a few minutes to spare. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 4/5/06, 11:57 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Valve termination unknown

Tony. that "T" is a little odd on a TPR. looks like a "dirt leg". i learned that in another thread and have been dying to use it.
Reply With Quote
  #11  
Old 4/5/06, 11:58 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Valve termination unknown

LMAO.....after that crawl, my legs were dirt as well.
Reply With Quote
  #12  
Old 4/6/06, 12:03 AM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Valve termination unknown

Quote:
Originally Posted by tneumann
LMAO.....after that crawl, my legs were dirt as well.
nice.
Reply With Quote
  #13  
Old 4/6/06, 3:38 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: TPR Valve termination unknown

From my Interactive Report System Version 2:

Quote:
Water heater—TPR drain pipe terminated at exterior location. Maintenance and safety concerns. The water heater can explode under adverse conditions. With an exterior location that cannot be easily monitored regularly, the TPR valve and drain pipe should be inspected annually. Recommend annual inspection by a licensed plumbing professional. Since valves quite often get stuck if not tested annually, if it cannot be proven that the water heater has been inspected within the last twelve months, particularly the water and gas shutoff valves and the TPR valve, recommend inspection by a licensed plumbing professional before close of escrow.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dr. Shane says every home should be tested for mold. gromicko Ancillary Inspection Services & Additional Topics 106 6/7/09 4:36 AM
TPR valve acox Plumbing Inspections 19 5/27/07 1:36 PM
Backwater valve in new homes? ccrooker Canadian Inspectors 16 11/28/06 8:47 AM
Water Heater Pressure Valve wrosario Plumbing Inspections 3 7/7/06 8:27 PM
TRP Drain Line Question psmothers Plumbing Inspections 22 7/6/06 5:57 PM


All times are GMT -4. The time now is 10:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts