Default Trap question

Is the trap needed at the disposal? Shouldnt a straight pipe be used.

If there is a issue can someone explain or is this OK.

Last edited by dmacy; 8/3/07 at 6:16 PM..
Reply With Quote
  #2  
Old 6/26/07, 2:07 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Trap question

A trap at the disposal is fine.
Reply With Quote
  #3  
Old 6/26/07, 2:09 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,550
Default Re: Trap question

Thanks Dave
Reply With Quote
  #4  
Old 6/26/07, 2:14 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Trap question

Except that unless I'm looking at it wrong, you shouldn't have two traps in succession on the same drain line.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #5  
Old 6/26/07, 2:16 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Trap question

David,

They could have done it this way also...


Reply With Quote
  #6  
Old 6/26/07, 2:17 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,550
Default Re: Trap question

Quote:
Originally Posted by bwiley
Except that unless I'm looking at it wrong, you shouldn't have two traps in succession on the same drain line.
They are on the same line. What would the problem be with the extra trap?
Reply With Quote
  #7  
Old 6/26/07, 2:25 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Trap question

In this case, probably nothing because the second sink drain acts as a vent in-between the traps. Two traps in the line though can act as an S-trap, or can cause poor drainage.

In any case, it looks amateurish, which should raise red flags!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #8  
Old 6/26/07, 4:16 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Trap question

That is a double trap, plain and simple. A tail-piece cannot be used as a vent, and a trap is not allowed to drain to another trap (with few exceptions).

It's wrong and should be corrected.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 6/26/07, 4:22 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,929
Default Re: Trap question

Quote:
Originally Posted by dmacy
Is the trap needed at the dipsposal? Shouldnt a straight pipe be used.

If there is a issue can someone explain or is this OK.
If this is a Insinkerator Badger model, that is the way they recommend you install it.
In their installation instructions it says ( if you have a double sink, use separate traps for both sides) That is how i installed mine and have had know problems. It has a 3 yr. warranty, so i put it in the way they wanted it.

Last edited by ccurrins; 4/20/09 at 1:47 AM..
Reply With Quote
  #10  
Old 6/26/07, 4:42 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Trap question

Quote:
Originally Posted by ccurrins
If this is a Insinkerator Badger model, that is the way they recommend you install it.
In their installation instructions it says ( if you have a double sink, use separate traps for both sides) That is how i installed mine and have had know problems. It has a 3 yr. warranty, so i put it in the way they wanted it.
That is not the proper way to install the traps - period. Even if the manufacturer says "trap each sink separately," this is not the way to do it.

In areas where the IRC is used, a shared trap arm is allowed, but the traps are required to be at the same elevation and attached to the trap arm with a Wye or directional fitting, such as a back-to-back.

In areas where the UPC is used, you cannot have a shared trap arm and must use a common trap (a single trap) regardless of the manufacturers recommendations.

Where's the vent for your sink Christopher?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 6/26/07 at 4:47 PM..
Reply With Quote
  #11  
Old 6/26/07, 11:01 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trap question

Double-traps, as illustrated in the photo, is a plumbing code violation, and illegal, under the IRC/IPC plumbing regulations.

Double trapping can break the trap seal and allow sewer gas to enter a house.

Besides that, the trap for the garbage disposal is installed BACKWARDS <rolls eyes> and needs to be removed.
Reply With Quote
  #12  
Old 6/26/07, 11:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Trap question

Quote:
Originally Posted by homebild
Besides that, the trap for the garbage disposal is installed BACKWARDS <rolls eyes> and needs to be removed.
Yea, that too



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 6/26/07, 11:07 PM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trap question

Quote:
Originally Posted by bwiley
In this case, probably nothing because the second sink drain acts as a vent in-between the traps. Two traps in the line though can act as an S-trap, or can cause poor drainage.

In any case, it looks amateurish, which should raise red flags!
The second sink drain would only act as a 'vent' if the sink is not filled with water. If it is filled with water, then one or both traps could siphon breaking the trap seal and allowing potentially harmful sewer gases into the structure.

This is an illegal installation and needs to be corrected.

Double-trapping as illustrated here is a code violation under most all plumbing codes.
Reply With Quote
  #14  
Old 6/26/07, 11:28 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,929
Default Re: Trap question

Quote:
Originally Posted by homebild
The second sink drain would only act as a 'vent' if the sink is not filled with water. If it is filled with water, then one or both traps could siphon breaking the trap seal and allowing potentially harmful sewer gases into the structure.

This is an illegal installation and needs to be corrected.

Double-trapping as illustrated here is a code violation under most all plumbing codes.
How about this type of installation?

Last edited by ccurrins; 4/20/09 at 1:47 AM..
Reply With Quote
  #15  
Old 6/26/07, 11:55 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trap question

IMO, a lot of the confusion is the result of the InSinkErator instructions, specifically step 11.4 :

"If you have a double sink, use separate drain traps for both sides."

here:

http://www.insinkerator.com/pdfs/US_ICU1.pdf
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 10:57 PM
Quick and easy trap question Danny Castellano Plumbing Inspections 4 8/14/06 1:17 PM
Negative angle trap arm issue rlind Plumbing Inspections 4 4/15/06 12:00 AM
Grease Trap / Drum Trap David White Plumbing Inspections 1 2/7/06 6:41 PM


All times are GMT -4. The time now is 6:59 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts