Default Trap weird and crown weir

I am kind of new to all this so please bare with me =).

I am a little confused and could someone help explain this to me.

"Standpipes should extend at least 18 inches and no more than 42 inches above the trap weir."

"The standpipe should be at least 30 inches high measured from the crown weir. "

The way I understood it was the trap weir is the part where the water leaves the trap, and the crown was the highest point of the trap.

Lets say a standpipe was 18" above the trap weir how could it possibly be 30 inches above the crown?

Thanks,

Dave
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/3/11, 10:58 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,795
Default Re: Trap weird and crown weir

You're referencing three different dimensions. 18" is the minimum, 42" is the maximum and 30" is "optimal."

The dimension is measured from the top of the weir.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE «
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/3/11, 11:29 AM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,259
Default Re: Trap weird and crown weir

http://www.nachi.org/gallery/
Attached Thumbnails
trap-weird-and-crown-weir-standpipe-1-.jpg.jpg
Views:	6242
Size:	33.0 KB
ID:	41041  




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #4  
Old 1/3/11, 11:44 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 20,238
Default Re: Trap weird and crown weir

Quote:
Originally Posted by rsmith24 View Post
David,

FYI... (ref: posted graphic)

Here in the land of basements, the trap is almost always located below the slab (95% of the time).

Always check with your local AHJ for the areas you operate in.

Jeff

PS... Welcome!
Reply With Quote
  #5  
Old 1/3/11, 12:09 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,601
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Trap weird and crown weir

Quote:
Originally Posted by jjonas View Post
David,

FYI... (ref: posted graphic)

Here in the land of basements, the trap is almost always located below the slab (95% of the time).

Always check with your local AHJ for the areas you operate in.

Jeff

PS... Welcome!
Interesting. .........

HERE in the land of basements, the trap is almost always located above the slab (99+% of the time).
Reply With Quote
  #6  
Old 1/3/11, 12:11 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,417
Default Re: Trap weird and crown weir

This one wasn't in the slab. I called it out as it was only 8" above the the top of the weir. Also I am thinking the tape is not allowed, correct?
Attached Thumbnails
trap-weird-and-crown-weir-144.jpg  



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
  #7  
Old 1/3/11, 1:03 PM
agallatin agallatin is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Trail BC
Posts: 193
Default Re: Trap weird and crown weir

They must have funny plumbing sytems in Mn. Here in the other land traps are throughout the the house , where needed !



galaxyhomeinspections.com



An amateur built the Ark !
Professionals built the Titanic !
Reply With Quote
  #8  
Old 1/3/11, 1:03 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,259
Default Re: Trap weird and crown weir

Quote:
Originally Posted by dokeefe View Post
This one wasn't in the slab. I called it out as it was only 8" above the the top of the weir. Also I am thinking the tape is not allowed, correct?
What did you say about the T being horizontal instead of vertical?




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #9  
Old 1/3/11, 4:11 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Minnesota & Northern Iowa
Posts: 20,238
Default Re: Trap weird and crown weir

So, the question remains, where is the OP located? (That be you David)
Reply With Quote
  #10  
Old 1/3/11, 4:28 PM
dpant dpant is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Burr Oak, MI
Posts: 74
Default Re: Trap weird and crown weir

Thanks guys I am located in Michigan but will be taking my NHIE exam soon to be able to do inspections in Indiana also.

I just want to make sure and know what I am talking about and to be honest I still think either I dont get it or what I read in the training materials here is not clear.

A response on here says that 30" is optimal but I cut and paste where it says 30" is minimal right out of the NACHI training here.

so still confused heh =)

Thanks,
Dave
Reply With Quote
  #11  
Old 1/3/11, 5:05 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,259
Default Re: Trap weird and crown weir

Quote:
Originally Posted by dpant View Post
Thanks guys I am located in Michigan but will be taking my NHIE exam soon to be able to do inspections in Indiana also.

I just want to make sure and know what I am talking about and to be honest I still think either I dont get it or what I read in the training materials here is not clear.

A response on here says that 30" is optimal but I cut and paste where it says 30" is minimal right out of the NACHI training here.

so still confused heh =)

Thanks,
Dave

A trap is designed to keep sewer gases and airborne bacteria from escaping the drainage system and entering the dwelling. Each plumbing fixture should be separately trapped by a water-seal trap, except as otherwise permitted by the plumbing standard. Fixtures such as water closets and urinals that have integral traps do not require an additional trap installed.
The vertical distance from the fixture outlet to the trap weir should not exceed 24 inches (610 mm). The vertical distance controls the drainage-flow velocity. If the trap has an excessively long vertical separation from the fixture, the velocity of the flow at the trap inlet can create siphoning.
The horizontal distance should not exceed 30 inches (610 mm), as measured from the center line of the fixture outlet to the center line of the inlet of the trap. The horizontal distance from a fixture to the trap limits the amount of bacterial growth and odor. It is desirable to locate the trap as close to the fixture as possible. A fixture should not be double-trapped.
Standpipes should be individually trapped. Standpipes, such as for a clothes washer, should have a minimum height above the trap of 18 inches (457 mm), and a maximum of 42 inches (1,066 mm). Access to all standpipes should be provided for cleaning and rodding.




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
  #12  
Old 1/3/11, 5:22 PM
dpant dpant is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Burr Oak, MI
Posts: 74
Default Re: Trap weird and crown weir

First I want to say thank you Robert for the illustrations and effort. I feel like I am being a pain in the *** but I dont see where it explains this.

"The standpipe should be at least 30 inches high measured from the crown weir. "


Dave
Reply With Quote
  #13  
Old 1/3/11, 6:07 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,259
Default Re: Trap weird and crown weir

Quote:
Originally Posted by dpant View Post
First I want to say thank you Robert for the illustrations and effort. I feel like I am being a pain in the *** but I dont see where it explains this.

"The standpipe should be at least 30 inches high measured from the crown weir. "


Dave
Where are you getting that quote from? I copied and pasted from the Residential Plumbing Overview for Inspectors




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/3/11, 6:26 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,417
Default Re: Trap weird and crown weir

Quote:
Originally Posted by rsmith24 View Post
What did you say about the T being horizontal instead of vertical?
I must confess I did not notice the horizontal T. I see now where it could back up into the standpipe. I shall lookout for this from now on, thank you Robert for pointing this out.



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
  #15  
Old 1/3/11, 6:38 PM
rsmith24 rsmith24 is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: Michigan
Posts: 1,259
Default Re: Trap weird and crown weir

Quote:
Originally Posted by dokeefe View Post
I must confess I did not notice the horizontal T. I see now where it could back up into the standpipe. I shall lookout for this from now on, thank you Robert for pointing this out.
Your welcome and when I see homeowner crap like this I also look at/for the cement used and in your attachment I don't see any purple or orange.




INSPECTIONLOGOS.COM

"I can keep explaining it for you, but I can't understand it for you".
Nick G.
Monroe Home Inspection
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are GMT -4. The time now is 9:03 PM.
no new posts