I saw this today, this is a drain line coming from the tub from above and hangs down about 18" then a trap and gooes into the main sewer line. Not sure if this is ok? Give me your thoughts thanks
|
|
#2
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
I need your advise on this one guys, I always get great reponses from here, the more I learn the better HI I become, anyone have a comment on this situation?
|
|
#3
|
||||
|
||||
|
Looks fine to me. Just a little different. I have never seen one that far down before but IMO, should work just as well.
John J. Passailaigue Jr. NACHI05062580 Auburn Home Inspection Auburn, Alabama WAR EAGLE!
|
|
#4
|
||||
|
||||
|
24" is the maximum allowable length for the tail piece - except for a washing-machine standpipe, which can be 36".
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
THANK YOU THANK YOU Jeff where did you get your finding please
|
|
#6
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hey Jeff i have the code book and the best I can find is under section P3105.3 (5) Is this what your talking about? So do I state something within my report?
|
|
#7
|
||||
|
||||
|
I don't see a problem
|
|
#8
|
|||
|
|||
|
Please Note:
twasion is a non-member guest and is in no way affiliated with InterNACHI or its members.
If that 2" above it is a vent then it may be ok. If it is a drain and they used this as a wet vent it would depend on the plumbing code. In that case, under UPC, it would not be legal.
|
|
#9
|
||||
|
||||
|
Quote:
I can't find the IRC section, but 3105.3 is a different animal - a vertical leg. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#10
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
i'll keep looking but for now i stated nothing on the report.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Trap primer valve | dmacy | Plumbing | 2 | 12/27/06 2:21 PM |
| Potable Water Line to Trap | jcooper2 | Plumbing | 9 | 11/1/06 1:17 AM |
| Negative angle trap arm issue | rlind | Plumbing | 4 | 4/15/06 12:00 AM |
| Grease Trap / Drum Trap | David White | Plumbing | 1 | 2/7/06 6:41 PM |