Does any have an illustration of how to change an unvented S-trap into an acceptable drain arrangement when venting is not possible. AAV's are allowed here but since they can't be installed in verticle piping, I'm not sure if that helps.
|
| Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Proper drainage cannot be accomplished without proper venting. If venting is "not possible," I would conclude that the fixture does not belong where it is.
"AAV's can't be installed in vertical piping?" What do you mean by that? AAV's are only installed in a vertical position. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Isn't the whole purpose of an AAV to provide venting where proper (ie the usual means of) venting is not possible.
Our plumbing code says horizontal Air admittance valves shall, (a) only vent fixtures located on the same storey, and (b) be connected to the horizontal fixture drain.
|
|
#4
|
||||
|
||||
|
Yes.
The AAV is installed vertically on a horizontal line. S-traps are improper. In order to properly install P-trap, there must be a horizontal line. (picture stolen from another thread)
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
So is there a way to convert an unvented S-trap to a P-trap and AAV?
|
|
#6
|
||||
|
||||
|
A way.
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#7
|
|||
|
|||
|
Yup, that will do it. Thanks.
|
|
#8
|
||||
|
||||
|
And this.
774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#9
|
|||
|
|||
|
|
|
#10
|
||||
|
||||
|
The horizontal pipe (distance requirement) breaks the siphon.
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#11
|
|||
|
|||
|
But that's not a particularly long horizontal arm. The horizontal arm on a conventionally vented P-trap arrangement is usually longer than that and venting is still required.
|
|
#12
|
||||
|
||||
|
Doesn't need to be longer than 2x trap diam.
On a conventional system, the vent must be within (3 or 5 ft) (US/Canada) (local AHJ). Same applies here. Adding the horiz. section breaks the s-trap configure. The horiz. section is needed before the vert. drop to break the siphon. Visualize the system from the fixture to where it connects to the waste/vent stack. Can you visually confirm the system to meet standards? If not, call it out. Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#13
|
||||
|
||||
|
Quote:
774 Manor Road Staten Island, NY 10314 718-514-3393 |
| Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Thanks guys, good thread.
|
|
#15
|
||||
|
||||
|
This configuration was in kitchen and bathroom of my last inspection. I think they tried their best to get good drainage, but they maybe didn't know about the serious uphill slope to the drain in the crawlspace...
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Condensation Drain line question | acassady | Inspecting HVAC Systems | 25 | 2/26/12 11:40 AM |
| Trap weird and crown weir | dpant | Plumbing Inspections | 22 | 1/24/11 11:41 PM |
| Trap Primer Question | jallingham | Plumbing Inspections | 5 | 2/15/08 7:36 PM |
| Negative angle trap arm issue | rlind | Plumbing Inspections | 4 | 4/14/06 11:00 PM |
| Grease Trap / Drum Trap | David White | Plumbing Inspections | 1 | 2/7/06 5:41 PM |