Default vent/cross connection/undersized waste

So I flush a toilet at today's inspection and see it swirl it's way up to the rim then finally go down, whewwwwww (slow drain, clog,vent or improperly sized waste line issue)... then I hear water running behind me (all fixtures are off) yet the tub has a fairly steady stream of water running from it's faucet for 10 - 15 seconds then it stops.

Flush the toilet again, water flows from the faucet again.
unfortunately the basement was finished so I could not confirm a definitive cross connection.

home was built in 1960, original water supply was a well - has since been changed to city water/sewer. One 2" vent visible on the roof, 3" main waste w/1 1/2 copper, 2" galvy branch lines coming into the tree.

What say you? agree, disagree?
Reply With Quote
  #2  
Old 8/4/08, 8:19 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,475
Default Re: vent/cross connection/undersized waste

Quote:
Originally Posted by cduphily
So I flush a toilet at today's inspection and see it swirl it's way up to the rim then finally go down, whewwwwww (slow drain, clog,vent or improperly sized waste line issue)... then I hear water running behind me (all fixtures are off) yet the tub has a fairly steady stream of water running from it's faucet for 10 - 15 seconds then it stops.

Flush the toilet again, water flows from the faucet again.
unfortunately the basement was finished so I could not confirm a definitive cross connection.

home was built in 1960, original water supply was a well - has since been changed to city water/sewer. One 2" vent visible on the roof, 3" main waste w/1 1/2 copper, 2" galvy branch lines coming into the tree.

What say you? agree, disagree?
I would write what you did here, more or less, and suggest a potential cross connection considering what you described but it does sound like it.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 8/4/08, 8:21 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,058
Default Re: vent/cross connection/undersized waste

Chris...you're freaking me out----

Water was coming out of the Tub spigot with the faucets shutoff when you flush the toilet......hmmm...interesting I do believe----
Reply With Quote
  #4  
Old 8/4/08, 9:12 PM
cduphily's Avatar
cduphily cduphily is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: vent/cross connection/undersized waste

Quote:
Originally Posted by dduffy
Chris...you're freaking me out----

Water was coming out of the Tub spigot with the faucets shutoff when you flush the toilet......hmmm...interesting I do believe----
Exactly!
Attached Thumbnails
vent-cross-connection-undersized-waste-5059taniteroad-stroudsburg_8208-006.jpg  
Reply With Quote
  #5  
Old 8/4/08, 9:52 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: vent/cross connection/undersized waste

Hey Chris I think you have 2 separate problems. It sounds like you have a problem with the diverter and a problem with the toilet. Slow flushing toilet is a sign of partial blockage in waste line (kids flushed a tooth brush or something). Then also a problem with the diverter, pressure or balancing valve.
To be sure though you could flush some food coloring down the toilet to see if the drip from the spout changes color. If it does the water supply is contaminated and unsafe to drink (among other things). If it doesn't see paragraph 1.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #6  
Old 8/5/08, 1:10 AM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: vent/cross connection/undersized waste

Quote:
Originally Posted by cduphily
So I flush a toilet at today's inspection and see it swirl it's way up to the rim then finally go down, whewwwwww (slow drain, clog,vent or improperly sized waste line issue)... then I hear water running behind me (all fixtures are off) yet the tub has a fairly steady stream of water running from it's faucet for 10 - 15 seconds then it stops.

I could not confirm a definitive cross connection.


What say you? agree, disagree?
Disagree .
Agree with Jack. Assuming it's a one-handle tub faucet, the pressure on the cold side drops when the toilet tank starts to fill, causing some hot water to leak past the valve. It's just a theory, but an easier one to accept than a toilet water cross connection.

John Kogel
www.allsafehome.ca
Reply With Quote
  #7  
Old 8/5/08, 12:00 PM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: vent/cross connection/undersized waste

I've seen water flow from Delta/Delex type faucets when toilet is flushed a few times myself.

The faucet depends on water pressure to keep the seals tight against their seats and when the pressure drops due to poor flow pressure, (sometimes caused by restricted pipes), the drop in pressure causes the seals to come away from their seats.

It has nothing to do with the drain problem.
Reply With Quote
  #8  
Old 8/5/08, 7:23 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,475
Default Re: vent/cross connection/undersized waste

Quote:
Originally Posted by sparksnmore
I've seen water flow from Delta/Delex type faucets when toilet is flushed a few times myself.

The faucet depends on water pressure to keep the seals tight against their seats and when the pressure drops due to poor flow pressure, (sometimes caused by restricted pipes), the drop in pressure causes the seals to come away from their seats.

It has nothing to do with the drain problem.
Good info...thanks.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slope of waste drain line. mlong Plumbing Inspections 5 4/23/08 10:54 PM
Waste line clean outs tcrosby Plumbing Inspections 2 2/29/08 11:55 PM
Waste line on OUTSIDE of house gkeene Plumbing Inspections 6 9/18/07 10:15 PM
Define "Indirect Waste Receptor" jfunderburk Plumbing Inspections 5 2/18/06 6:35 PM


All times are GMT -4. The time now is 7:12 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts