Default Vent elbows and flex drain line

The flippers are back!!!!
"S" trap with vent elbows, flex line at bath tub.
Attached Thumbnails
vent-elbows-and-flex-drain-line-img_3652.jpg   vent-elbows-and-flex-drain-line-img_3666.jpg   vent-elbows-and-flex-drain-line-img_3672.jpg  
Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/4/11, 9:52 PM
Robert Ernst Robert Ernst is online now
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Vent elbows and flex drain line

Looks like more work to do it wrong than to do it right.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #3  
Old 12/5/11, 11:42 AM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Vent elbows and flex drain line

I've never seen one of those flex lines before but it looks like they're made for plumbing. Is there anything wrong with them?
Reply With Quote
  #4  
Old 12/5/11, 1:13 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent elbows and flex drain line

Quote:
Originally Posted by jallingham View Post
I've never seen one of those flex lines before but it looks like they're made for plumbing. Is there anything wrong with them?
Yes,they all must be smooth wall I.D.

Granted easy to remove, but still wrong.
Reply With Quote
  #5  
Old 12/5/11, 1:44 PM
Gary D. Rowden Gary D. Rowden is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Hemet, CA
Posts: 148
Default Re: Vent elbows and flex drain line

Quote:
Originally Posted by jallingham View Post
I've never seen one of those flex lines before but it looks like they're made for plumbing. Is there anything wrong with them?
Here in CA this type of flexible plastic drain piping assembly can be found in pretty much any hardware store (Home depot, Lowes, Ace). I personally would not recommend this type of install, I prefer rigid piping myself, Even though the flex piping are quick and easy to install they are more likely to cause clogging (especially at disposal) and sagging along the flexible ribbing. Also in some states this may not be a proper install.
Reply With Quote
  #6  
Old 12/5/11, 1:58 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Vent elbows and flex drain line

Jeff,
This question comes up all the time, and the consensus is that they are not approved, yet they are sold in all hardware stores, and no one has ever been able to post anything that specifically states why (or where the info is) that they are not approved. This occurs on all the relevent MB's, not just here.
Reply With Quote
  #7  
Old 12/5/11, 3:54 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent elbows and flex drain line

From State code

j) No fittings having a hub in the direction opposite to flow, or tee branch, shall be used as a drainage fitting. No running threads, bands, or saddles shall be used in the drainage system. No drainage or vent pipe or fitting shall be drilled or tapped.

k) No fitting, connection, device or method of installation shall be used which obstructs or retards the flow of water, waste, or air in the drainage or venting system by an amount greater than the normal frictional resistance to flow. The enlargement of a 3 inch closet bend or stub to 4 inches shall not be considered an obstruction if it is necessary to increase the bend or stub at the floor line to 4 inches in diameter in order to accommodate the water closet outlet.

Section 890.370 Prohibited Joints and Connections in Drainage Systems

Drainage System. Any fitting or connection which has an enlargement, chamber, or recess with a ledge, shoulder, or reduction of pipe area that offers an obstruction to flow through the drain is prohibited. No fitting or connection that obstructs flow shall be used. In existing buildings only a flow control valve or device may be connected to the fixture drain and shall not be considered as an obstruction. The enlargement of a three (3) inch closet bend or stub to four (4) inches shall not be considered an obstruction.

Type of Traps. Traps shall have a uniform and smooth interior, and shall have no partitions or movable parts. The trap seal shall be non-adjustable. (See Appendix D: Illustration C.)
Reply With Quote
  #8  
Old 12/5/11, 4:08 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Vent elbows and flex drain line

Bob,
Thanks for posting the info, but, if you are applying the info to Jeff's pictures, I will bet that it does not apply. I would say the AHJ (if one was involved) approved the work. Carefully read and understand what each code states, and then look again at each pic. Yes, minor technicalities will get the builder/plumber approval almost every time, especially in Chicago.
Reply With Quote
  #9  
Old 12/5/11, 4:52 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent elbows and flex drain line

I call them out, but unlike you I am not a code inspector.

Illinois code as I listed above does not allow their install however.

The accordion violates portions I bolded Jeff, however next time I will add a flashing arrow.LOL.
Reply With Quote
  #10  
Old 12/5/11, 5:23 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Vent elbows and flex drain line

Quote:
Originally Posted by belliott View Post
From State code

j) No fittings having a hub in the direction opposite to flow, or tee branch, shall be used as a drainage fitting. No running threads,
these are not considered "running threads"

bands, or saddles shall be used in the drainage system. No drainage or vent pipe or fitting shall be drilled or tapped.

k) No fitting, connection, device or method of installation shall be used which obstructs or retards the flow of water, waste, or air in the drainage or venting system by an amount greater than the normal frictional resistance to flow.
AS PICTURED... there is little to no obstruction or retardation...by an amount greater than the normal frictional resistance to flow

The enlargement of a 3 inch closet bend or stub to 4 inches shall not be considered an obstruction if it is necessary to increase the bend or stub at the floor line to 4 inches in diameter in order to accommodate the water closet outlet.

Section 890.370 Prohibited Joints and Connections in Drainage Systems

Drainage System. Any fitting or connection which has an enlargement, chamber, or recess with a ledge, shoulder, or reduction of pipe area that offers an obstruction to flow through the drain is prohibited. No fitting or connection that obstructs flow shall be used.
AS PICTURED... there is no obstruction TO FLOW

In existing buildings only a flow control valve or device may be connected to the fixture drain and shall not be considered as an obstruction. The enlargement of a three (3) inch closet bend or stub to four (4) inches shall not be considered an obstruction.

Type of Traps. Traps shall have a uniform and smooth interior, and shall have no partitions or movable parts. The trap seal shall be non-adjustable.
AS PICTURED... the traps shown have a smooth interior, and no moveable parts, and is non-adjustable.
(See Appendix D: Illustration C.)
Note: On virtually every flexible P-trap that I have seen, the "flexible' section is at/above the straight/verticle/tailpiece section, and is not technically considered the trap. On the "soft rubberlike" P-traps, they are always "smooth" interiors.

Also note Bob: Running threads are more apt to electrical conduit, but technically applies to plumbing also...

"Running Thread"...

http://www.tpub.com/ceb/71.htm
Reply With Quote
  #11  
Old 12/5/11, 5:39 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Vent elbows and flex drain line

Quote:
Originally Posted by jjonas View Post
k) No fitting, connection, device or method of installation shall be used which obstructs or retards the flow of water, waste, or air in the drainage or venting system by an amount greater than the normal frictional resistance to flow.
AS PICTURED... there is little to no obstruction or retardation...by an amount greater than the normal frictional resistance to flow

You don't feel this design obstructs waste?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 12/5/11, 5:47 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent elbows and flex drain line

Jeff is trying to be difficult and must have stock in one of these companies....seriously dude
just use common sense.

If the inside diameter is 1-1/4 is that at the widest or the most narrow part of the accordion?
Do you even know and when you figure that out explain how the valley part does not constitute making the diameter smaller at any point.

The inside diameter is changing from small to big to small again and that is not allright even in laymans terms.

Perhaps in your opinion it is OK to go from 1-1/2 to 1-1/4 also ?
Reply With Quote
  #13  
Old 12/5/11, 8:13 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Vent elbows and flex drain line

Quote:
Originally Posted by ccurrins View Post

You don't feel this design obstructs waste?
Only minimally... AS SHOWN... the bellows are basically pushed together/closed, not extended open. Take a close look, and the next time you are in HD/Lowes/etc... check one out, and you will see what I mean.
Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/5/11, 8:21 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Vent elbows and flex drain line

Quote:
Originally Posted by belliott View Post
Jeff is trying to be difficult and must have stock in one of these companies....seriously dude
just use common sense.
I always do, and don't usually open my mouth unless I know what I am talking about, or I'm asking a question.

If the inside diameter is 1-1/4 is that at the widest or the most narrow part of the accordion?
Duh... who needs to use common sense?

Do you even know and when you figure that out explain how the valley part does not constitute making the diameter smaller at any point.

The inside diameter is changing from small to big to small again and that is not allright even in laymans terms.
Where do you see that occuring? Are you insinuating that inside the flex section it gets smaller? If you are, you're wrong. You can even see that in the pic if you look close enough.

Perhaps in your opinion it is OK to go from 1-1/2 to 1-1/4 also ?
If you are referring to the P-trap itself, it looks to be an appropriate size for the application.
This is from a post in 2009. Is this still a factor in Illinois?
Quote:
Not on the Illinois Department of Public Heath's approved materials for that purpose (Illinois Plumbing Code).

Last edited by jjonas; 12/5/11 at 8:24 PM..
Reply With Quote
  #15  
Old 12/5/11, 9:22 PM
Jeff Merritt Jeff Merritt is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 1,162
Default Re: Vent elbows and flex drain line

Not approved in IL, and no code inspector was involved, and even if one was, it's Chicago, that we we have work here. Just the tip of the iceberg in this house.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 2:04 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts