Default Vent Stack with Condensate Lines

I've researched the threads and found only one reference to substantiate not having condensate lines piped directly into vertical plumbing vent stacks.

It is in IRC 2003 P3101.3 Use Limitations. The plumbing vent system shall not be utlilized for purposes other than the venting of the plumbing system.

Is this improper? There are no traps and the units are located in the attic.

Can anyone support this with an appropriate code reference?

Hank
Attached Images
 
Reply With Quote
  #2  
Old 10/2/06, 5:11 PM
hspinnler's Avatar
hspinnler hspinnler is offline
Active Poster
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 149
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Vent Stack with Condensate Lines

Proper photo attached this time.
Attached Thumbnails
vent-stack-condensate-lines-ac-lines2.jpg  
Reply With Quote
  #3  
Old 10/2/06, 5:44 PM
Raymond N. Newman Raymond N. Newman is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Avondale, AZ
Posts: 128
Send a message via Skype™ to rnewman1
Default Re: Vent Stack with Condensate Lines

Is this the auxiliary and secondary drain ?
Reply With Quote
  #4  
Old 10/2/06, 7:43 PM
hspinnler's Avatar
hspinnler hspinnler is offline
Active Poster
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 149
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Vent Stack with Condensate Lines

These are Primary Condensate Lines.

Thanks.
Reply With Quote
  #5  
Old 10/2/06, 8:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Vent Stack with Condensate Lines

Whether it's allowed or not, those types of connections are prohibited. Without the proper fittings, it doesn't matter what the code says - it's wrong.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 10/2/06, 8:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Vent Stack with Condensate Lines

P3005.1 Drainage fittings and connections.
Changes in direction in drainage piping shall be made by the appropriate use of sanitary tees, wyes, sweeps, bends or by a combination of these drainage fittings in accordance with Table P3005.1.




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 10/2/06, 8:44 PM
hspinnler's Avatar
hspinnler hspinnler is offline
Active Poster
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 149
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Vent Stack with Condensate Lines

Good stuff Jeff. No thread drift with your posts. You're the best Left Coast inspector around. Hope you have a great 4th Quarter!
Reply With Quote
  #8  
Old 10/2/06, 9:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Vent Stack with Condensate Lines

Quote:
Originally Posted by jpope
P3005.1 Drainage fittings and connections. Changes in direction in drainage piping shall be made by the appropriate use of sanitary tees, wyes, sweeps, bends or by a combination of these drainage fittings in accordance with Table P3005.1.
Is this the best area to deal with this? This is vent piping is it not? I think you stated it best with your first post Hank.

I write soft water brine drains up all the time as being wrong.

Last edited by bkelly2; 6/12/09 at 7:47 PM..
Reply With Quote
  #9  
Old 10/2/06, 9:32 PM
hspinnler's Avatar
hspinnler hspinnler is offline
Active Poster
 
Join Date: Apr 2005
Location: Hoschton, GA
Posts: 149
Please Note: hspinnler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Vent Stack with Condensate Lines

Quote:
Originally Posted by bkelly2
Is this the best area to deal with this? This is vent piping is it not? I think you stated it best with your first post Hank.
I thought it was since we were talking about plumbing vent stacks. When I think of venting in HVAC, I think about flue vents for gas-fired appliance.
Reply With Quote
  #10  
Old 10/2/06, 9:41 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Vent Stack with Condensate Lines

Hank, I think you nailed it with your interpretation of the code in your first post.
I was refferring to Jeff's reply about drain piping, I do not think the drain piping part of the code Jeff mentioned is appropriate for the question you asked. The condensate is tied into vent piping and it is wrong.
Reply With Quote
  #11  
Old 10/2/06, 11:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Vent Stack with Condensate Lines

This could arguably be considered a wet-vent with this type of application, which is why appropriate fittings would be required.

Condensate drain lines are commonly tied to vents and/or drains.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 10/2/06, 11:12 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Vent Stack with Condensate Lines

Quote:
Originally Posted by jpope
This could arguably be considered a wet-vent with this type of application, which is why appropriate fittings would be required.

Condensate drain lines are commonly tied to vents and/or drains.
I understand what you are saying Jeff but do not see the section of code to support this.??
Reply With Quote
  #13  
Old 10/3/06, 12:51 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Vent Stack with Condensate Lines

Quote:
Originally Posted by jpope
This could arguably be considered a wet-vent with this type of application, which is why appropriate fittings would be required.

Condensate drain lines are commonly tied to vents and/or drains.
I write up every condensate drain line I observe piped into a vent or drain line that does not have a air gap and I state the reason for this as being not a code violation as we are not code inspectors but simply it allows sewer gas into the air stream of the furnace even when there is a P-trap installed because this P-trap will and does remain dry during the heating season unless the furnace is a high efficiency and producing its own condensate.
Reply With Quote
  #14  
Old 10/3/06, 1:07 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Vent Stack with Condensate Lines

Quote:
Originally Posted by cbottger
I write up every condensate drain line I observe piped into a vent or drain line that does not have a air gap
As you should.

This is an indirect waste line which requires an air-gap and a trap.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 10/3/06, 12:14 PM
jinvernizzi jinvernizzi is offline
New User
 
Join Date: Jun 2006
Location: Washington, PA
Posts: 33
Please Note: jinvernizzi is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Vent Stack with Condensate Lines

Could be a "combination vent and waste system."

Aside from that, and what has been mentioned by others:

Looks like a nice job of compromising the integrity of the truss. I guess they made up for it with that "approved" duct tape, metal lath or plumber's strap wrapped around the pipe. I'm not sure if the truss is supporting the pipe or the pipe is supporting the truss! By the way, is that cotton candy all over the place?

Off the top of my head:

Drilling a hole in the pipe to make an access would fall under the same heading as a saddle tap, which is prohibited by code.

Joints in plastic piping are to be made with approved fittings by solvent cementing, elastometric gaskets or other approved manufactured system.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 10:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM
Trap Cover on vent stack? hspinnler Plumbing Inspections 9 10/8/06 11:35 AM
Condensation drain vent abishop Inspecting HVAC Systems 9 8/4/06 2:59 PM


All times are GMT -4. The time now is 7:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts