Anyone have a blurb about using a vent tee in place of a sani tee?
Attached Thumbnails
vent-tee-kitchen-waste-line-cimg2439.jpg  



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/8/11, 1:48 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent tee in kitchen waste line

That looks wrong.
May be the picture but I see no 1/4 inch per foot slope and also the drain on the left with the dishwasher waste tee should simply go over to the right hand drain up high and connect there and drop down to the horizontal run with a wye connection.
That would be much better than a straight out tee connection.

Sorry but this is just a quick sketch example.
vent-tee-kitchen-waste-line-kitchen-sink-drain.jpg
Reply With Quote
  #3  
Old 3/8/11, 2:35 AM
Darin Redding's Avatar
Darin Redding Darin Redding is online now
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Vent tee in kitchen waste line

Yea your pic is a better way for sure. I was curious about the straight tee connection, where a sani tee is more appropriate since it has directional flow (would help prevent the right sink from backing up into the left).



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #4  
Old 3/8/11, 2:52 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent tee in kitchen waste line

Quote:
Originally Posted by dredding View Post
Yea your pic is a better way for sure. I was curious about the straight tee connection, where a sani tee is more appropriate since it has directional flow (would help prevent the right sink from backing up into the left).
Correct.
Tee connection is OK at top going horizontal to vertical because gravity makes it drop down but it should be angled when going from vertical to horizontal.
Hope that makes sense.

This ppt rocks if you download it.Took me some time to find it online for yo to download.http://www.bestlineplumbing.com/DrainCodes.htm

Last edited by belliott; 3/8/11 at 3:37 AM..
Reply With Quote
  #5  
Old 3/8/11, 9:11 AM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Vent tee in kitchen waste line

Quote:
Originally Posted by dredding View Post
Anyone have a blurb about using a vent tee in place of a sani tee?
I would like too see a plumber comment but I'll weigh in any way.
If my understanding of the plumbing code is correct because the change in direction of flow is vertical too horizontal the fitting is required to be a Wye. A sanitary tee can only be used when the flow direction is horizontal to vertical with the sink located above the fitting the flow direction is horizontal to vertical and because the change of direction is greater than 45 degrees a clean out would also be required. But to address your original point you are correct a straight tee is not permitted for the application identified in your photograph



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #6  
Old 3/8/11, 10:00 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Vent tee in kitchen waste line

Mark is correct - that is not an appropriate location for a sanitary-tee. A wye is required.

Simply report that improper fitting are being used in the drain line and corrections should be made by a qualified plumber.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 3/8/11, 10:59 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent tee in kitchen waste line

Quote:
Originally Posted by jpope View Post
Mark is correct - that is not an appropriate location for a sanitary-tee. A wye is required.

Simply report that improper fitting are being used in the drain line and corrections should be made by a qualified plumber.
Are you stating I am not correct?,because to me it appears Mark said the same thing as myself except I explained the actual reasoning not being a code inspector and all.
Reply With Quote
  #8  
Old 3/8/11, 11:12 AM
Darin Redding's Avatar
Darin Redding Darin Redding is online now
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Vent tee in kitchen waste line

Thanks Mark. Thats what I was thinking. A vent tee is not appropriate for this application.



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #9  
Old 3/8/11, 11:51 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent tee in kitchen waste line

Did you download that ppt Darin?
Reply With Quote
  #10  
Old 3/8/11, 11:54 AM
Darin Redding's Avatar
Darin Redding Darin Redding is online now
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Vent tee in kitchen waste line

Getting it now Bob.



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #11  
Old 3/8/11, 12:02 PM
Darin Redding's Avatar
Darin Redding Darin Redding is online now
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Vent tee in kitchen waste line

Great stuff Bob. Thanks for sharing.

Slide 66:

706.4 Vertical drainage lines, connecting with horizontal drainage lines shall enter through forty-five (45) degree wye branches, combination wye and one-eighth 1/8 bend branches, or other approved fittings of equivalent sweep. Sixty (60) degree branches or offsets may be used only when installed in a true vertical position.

So the lack of a sweep in a typical vent connection is where the "plumber" went wrong.



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #12  
Old 3/8/11, 12:48 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent tee in kitchen waste line

Quote:
Originally Posted by dredding View Post
Great stuff Bob. Thanks for sharing.

Slide 66:

706.4 Vertical drainage lines, connecting with horizontal drainage lines shall enter through forty-five (45) degree wye branches, combination wye and one-eighth 1/8 bend branches, or other approved fittings of equivalent sweep. Sixty (60) degree branches or offsets may be used only when installed in a true vertical position.

So the lack of a sweep in a typical vent connection is where the "plumber" went wrong.
Yep
What you said about the water flow and I think also it has to do with being able to rod out.
Wish these codes would always explain exact reasoning as they always leave us to guess many times.
Reply With Quote
  #13  
Old 3/8/11, 1:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Vent tee in kitchen waste line

Quote:
Originally Posted by belliott View Post
Are you stating I am not correct?
Not at all Bob, you are correct, however, Mark stated that the sanitary-tee is not allowed for this application, which is what I was referring to as being "correct."

Code inspector or not, a sanitary-tee is only allowed to be used in the vertical position in a "horizontal-to-vertical" application. A sanitary-tee is not allowed to lay on its "back."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/8/11, 1:28 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Vent tee in kitchen waste line

Quote:
Originally Posted by jpope View Post
Not at all Bob, you are correct, however, Mark stated that the sanitary-tee is not allowed for this application, which is what I was referring to as being "correct."

Code inspector or not, a sanitary-tee is only allowed to be used in the vertical position in a "horizontal-to-vertical" application. A sanitary-tee is not allowed to lay on its "back."
OK gottya.Clarified.
Reply With Quote
  #15  
Old 3/8/11, 2:26 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Vent tee in kitchen waste line

Quote:
Originally Posted by belliott View Post

This ppt rocks if you download it.Took me some time to find it online for yo to download.http://www.bestlineplumbing.com/DrainCodes.htm
Great PP..240 slides.....thanks Bob.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rust our of vent line??? HELP! bsmith2 Inspecting HVAC Systems 2 3/9/10 1:24 PM
waste line over panel box pcavalcante Electrical Inspections 4 3/3/10 7:25 PM
Kitchen Range Down Draft Vent rnewland General Inspection Discussion 3 2/27/09 10:18 PM
Waste line on OUTSIDE of house gkeene Plumbing Inspections 6 9/18/07 9:15 PM


All times are GMT -4. The time now is 2:05 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts