Obvious but tired.
3.5 bathrooms and i vent stack. Attachment 47501 What makes it worse is 2" inch ( master bath ) PVC is taped into a 2" PVC off tyhe main 3rd floor bath, then expanded into one 4" PCC 12 inches before the exit through the roof deck. Washer dry , powder room with shower cabinet. 1/2 bath on first floor. Kitchen with island and double sink. Attachment 47502 here is the 4" enlarged PVC fitting and exit. Attachment 47503 montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 Last edited by ryoung7; 10/5/11 at 10:36 PM.. |
| Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Not proper and not allowed you can end up with a bath exhaust discharge circling in the home and none of the moisture vented to the out side . All require there own discharge to the out side . The 2 inch is just another incorrect concern . Roy Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#3
|
||||
|
||||
|
Quote:
Take a look. Engineered vent stacking. Attachment 47511 montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 Last edited by ryoung7; 10/5/11 at 10:36 PM.. |
|
#4
|
||||
|
||||
|
Sorry I was still a sleep I thought you where talking about Bath room and Kitchen power exhaust vents .
Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#5
|
||||
|
||||
|
Robert,
The black pipe is ABS and increase to 4 inches in unconditioned area to prevent frost closure. Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ |
|
#6
|
||||
|
||||
|
Quote:
Metal will conduct cold faster than ABS. No main waste ( wet stack ) in the attic. Only venting. The main wet stack can not be seen Marcel. That is the only venting exiting the roof. I thought the main waste or wet stack must continue through the unit exiting the building through the roof, not the wall. Link please. montrealbuildinginspectionservice.com montreal-home-inspection-services.com home-inspections-montreal.com homeinspectionsservicesmontreal.com ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC. Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI) OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816 |
|
#7
|
||||
|
||||
|
Individual fixture vents need to be at least 1-1/4", branch vents need to be at least 1/2 the corresponding branch drain size and sized for the drainage fixture units (typically 2" pipe), there needs to be at least one vent thru the roof, and the size of the vent on the exterior needs to be at least 3", where subject to freezing, with that transition at least 12" below the room. See IRC Chapter 31 or Code Check for an HI's POV. Your local mileage may vary ...
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 8/20/11 at 9:24 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Sump Pit/Pump Question | Joey D'Adamo | Plumbing Inspections | 4 | 11/26/08 1:04 PM |
| Question about a gas fireplace vent | jvogan | Inspecting HVAC Systems | 10 | 3/20/07 8:46 PM |
| Plumbing vent Routing Question | kweiss | Plumbing Inspections | 7 | 11/1/06 9:57 PM |
| Venting question | bsmith | Inspecting HVAC Systems | 6 | 2/14/06 7:14 AM |