Default Warm Cold Water

Just looking for a second opinion. Had a inspection today and the cold water seemed warm so I took temperatures and it ranged from 88 to 90. I let the water heater heat back up and retested with the same results. The water would go from cool about 75 then rise to 88 to 90. The only conclusion I can come up with is there is a cold and hot water line crossed somewhere. This is a slab foundation.
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/10/11, 9:50 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Warm Cold Water

Had this problem on a house I inspected the plumber found a shower/tub faucet that was leaking internal causing a cross connect and mine was a slab floor also these can be a B**** to find sometimes



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 8/14/11, 12:56 AM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Warm Cold Water

Definitely reads like a cross connection. Was that one particular fixture or room, or the entire building?
Reply With Quote
  #4  
Old 8/14/11, 7:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Warm Cold Water

It may be difficult to isolate, but easy to verify if it's a "cross-connection" from a bad mixing valve or similar.

Turn off the supply to the water heater and run the cold-water for several minutes, then check it's temp. Continue running the cold-water while you restore the supply to the water heater. If the cold-water rises in temp, there's a cross-connection somewhere.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Pressure Problem dcossar Plumbing Inspections 19 11/21/09 8:47 PM
Hot water heater Hot and Cold hookup phughes Plumbing Inspections 20 5/11/06 1:04 AM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 2:07 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts