Default Water in floor vents

How does water get into floor HVAC vents during periods of heavy rain? Floor is on slab. Seller installed sump pump under outside deck, but it's not draining all the water. Possible causes and suggestions to alleviate problem appreciated.
Reply With Quote
  #2  
Old 1/4/09, 1:33 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,765
Default Re: Water in floor vents

Erol,

Very strange as I just had a slab inspection last week with the same exact problem. I went and pulled the cover off a return vent (because I was just curious as to why the return vents were installed on outside walls) in the living room and viola...3 inches of standing water in both return vents in this room.

It appears that water from the outside perimeter of the house has seeped through cracked areas of the return ducts. Every return in this house was a solid concrete tunnel (no liner whatsoever) molded into the slab from the furnace location.

I simply told my client that the HVAC return air system (within the slab) may have to be abandoned, but I would rather see him get an HVAC professional opinion.
Reply With Quote
  #3  
Old 1/4/09, 1:38 PM
Erol Kartal Erol Kartal is offline
Active Poster
 
Join Date: Feb 2008
Posts: 858
Please Note: Erol Kartal is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water in floor vents

Thanks, David.

In a perfect world then, if ducts were removed then the ground water would stay outside?
Reply With Quote
  #4  
Old 1/4/09, 1:42 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,765
Default Re: Water in floor vents

Quote:
Originally Posted by ekartal View Post
Thanks, David.

In a perfect world then, if ducts were removed then the ground water would stay outside?

Not if the water is seeping in through hairline cracks in the slab.

The old ducts probably rusted away from the water seepage, so someone simply removed the rusted material, which left a round tunnel for the return.

No they have standing water and a natural humidifier.
Reply With Quote
  #5  
Old 1/4/09, 2:55 PM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 6,796
Default Re: Water in floor vents

Many homes on slabs had asbestos transite pipe used for return ducts. I've seen it many times on demolition jobs.



Linas Dapkus, CMI
Infraspection Institute Certified Infrared Thermographer Level III # 8510
Dapkus Home Inspections
Dapkus Home Inspections Inc. - No Gimmicks, No Kickbacks, Your personal contact information will not be sold to third parties. For 8 years & counting, quality home inspections is all we sell.
Reply With Quote
  #6  
Old 1/4/09, 3:00 PM
Linas Dapkus, CMI's Avatar
Linas Dapkus, CMI Linas Dapkus, CMI is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL.
Posts: 6,796
Default Re: Water in floor vents

I had an inspection last month that had water in the ducts after the water was turned on to the home (foreclosure). The ducts leaked water onto the kitchen ceiling.
Attached Thumbnails
water-floor-vents-imported-photos-00002.jpg   water-floor-vents-imported-photos-00001.jpg  



Linas Dapkus, CMI
Infraspection Institute Certified Infrared Thermographer Level III # 8510
Dapkus Home Inspections
Dapkus Home Inspections Inc. - No Gimmicks, No Kickbacks, Your personal contact information will not be sold to third parties. For 8 years & counting, quality home inspections is all we sell.
Reply With Quote
  #7  
Old 1/4/09, 5:09 PM
Mike Huppi Mike Huppi is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Aloha Oregon
Posts: 15
Default Re: Water in floor vents

I had one of those a few years ago and the ducts were rusted out in the slab, there was no visible water but I still recommended a HVAC. In the end they needed to redo the entire system and it made the deal go south because it was a 2 story home and the heating was going to be too expensive for the buyer to redo. They were going to have to tear walls out to install ducts to the different rooms and levels.

One thing I suggested so that they could get a better look was to use a sewer scope camera.



Mike Huppi
The HomeTeam Inspection Service
503-530-8306
Reply With Quote
  #8  
Old 1/4/09, 5:27 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 12,377
Default Re: Water in floor vents

Kick me if i am wrong, If the duct has been rusted or Damaged and full of water would there not be a chance the floor (slab )be weakened to the point of cracking and fallen in ). I would think it would be advisable to fill the void either with pumped in concrete or a injection system like they use for cracked sewers. If water comes in it will go out causing erosion
Reply With Quote
  #9  
Old 1/4/09, 10:24 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,897
Default Re: Water in floor vents

I have to deal with this on a daily basis 95% of all homes constructed in Oklahoma since the early 60's are all slab on grade foundation. Not uncommon to see water in the ducts here I am always on guard for this. It most usually starts here by the builder not understanding the 6X10 rule for foundation pads. The word pad to me means elevated most builders here dig a hole build a house in the hole and expect water to run away from the foundation????

Most homes here do get water under the slabs that have poor landscape topography but not always into the ducts. I use a mirror and flashlight to look for past water marks down the duct from the registers to the first turn and then make my call for a camera scan based on what I see.

BTW the duct work is not in the slab it is beneath the slab covered with sand.

You have different sources of water potential under a slab the most common of course is high ground water. Leaking drains and or leaking domestic water supply lines. And don't forget about a leaking A-coil drain pan during the A/C season I have observed the supply air plenum full of condensate water and overflowing to the supply duct all of the way to the floor registers.



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340

Last edited by cbottger; 1/4/09 at 10:35 PM..
Reply With Quote
  #10  
Old 1/4/09, 10:32 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,897
Default Re: Water in floor vents

Quote:
Originally Posted by mhuppi View Post
I had one of those a few years ago and the ducts were rusted out in the slab, there was no visible water but I still recommended a HVAC. In the end they needed to redo the entire system and it made the deal go south because it was a 2 story home and the heating was going to be too expensive for the buyer to redo. They were going to have to tear walls out to install ducts to the different rooms and levels.

One thing I suggested so that they could get a better look was to use a sewer scope camera.
A good contractor does not have to tear out walls if he knows what he is doing. I have re-modeled many 2 stories and never removed any interior wall covering.



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #11  
Old 1/5/09, 3:07 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,765
Default Re: Water in floor vents

Quote:
Originally Posted by cbottger View Post

BTW the duct work is not in the slab it is beneath the slab covered with sand.
Charley,

This may be true in many situations but not in this particular home. The concrete was poured around some sort of cylinder (in order to make a concrete duct) because when I look inside the return area, I see concrete access hole all the way through, to include concrete ducts going right to the opposite side of the room.
Reply With Quote
  #12  
Old 1/5/09, 5:31 PM
Erol Kartal Erol Kartal is offline
Active Poster
 
Join Date: Feb 2008
Posts: 858
Please Note: Erol Kartal is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water in floor vents

It was suggested by an HVAC technician to fill the ducts with concrete. This advice coming without going out to the home to check it out first. Is his recommendation the only method of resolving this sort of issue?
Reply With Quote
  #13  
Old 1/5/09, 6:06 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,897
Default Re: Water in floor vents

Quote:
Originally Posted by ekartal View Post
It was suggested by an HVAC technician to fill the ducts with concrete. This advice coming without going out to the home to check it out first. Is his recommendation the only method of resolving this sort of issue?
No that is not the only option re-landscaping and or French drains is another option but that does not always work either and it is sad to pay for french drains and then on top of that have to convert to an up flow system any way lots of money envolved here. In this area we normally go for the sure kill upflow furnace and fill the boots over with cement. As a Hi I just list the options and let the buyer and seller decide what to do.



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #14  
Old 1/5/09, 6:17 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: North Central Okla
Posts: 7,897
Default Re: Water in floor vents

Quote:
Originally Posted by dvalley View Post
Charley,

This may be true in many situations but not in this particular home. The concrete was poured around some sort of cylinder (in order to make a concrete duct) because when I look inside the return area, I see concrete access hole all the way through, to include concrete ducts going right to the opposite side of the room.
David you are loosing me are we talking upflow or downflow. I have seen upflow furnace with poured return chases built in the slab but are unsual. One can find almost anything out there just depending on what the builder had in mind especially with custom builts. Even I stop and scratch my head sometimes trying to discover what the builder was doing. I have no doubt back east where there is a large amount of really old homes that have been re-modeled 10 times over the years that one can see anything.



http://www.oklahomathermalinfraredimaging.com/
http://www.freedomexpressinspections.com/
Master HVAC Mechanic Retired
Level III Thermographer # 8486 Infraspection Institute
CMI Certified Master Inspector
Residential/Commercial Inspections
Moisture Intrusion Expert Witness
580-268-3340
Reply With Quote
  #15  
Old 1/6/09, 6:16 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,765
Default Re: Water in floor vents

Quote:
Originally Posted by cbottger View Post
David you are loosing me are we talking upflow or downflow. I have seen upflow furnace with poured return chases built in the slab but are unsual. One can find almost anything out there just depending on what the builder had in mind especially with custom builts. Even I stop and scratch my head sometimes trying to discover what the builder was doing. I have no doubt back east where there is a large amount of really old homes that have been re-modeled 10 times over the years that one can see anything.
Charley,

It was an Upflow furnace. It sucked the return air from the slab ducts (below the unit) and sent the warm air into duct work (above the unit) that went through a chase and into the rooms. Only the returns were embedded into the slab.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On