Default Water Heater Amperage? Maybe this is elec.

I was looking at my brother in laws 50 gallon AO Smith electric water heater last night and noticed that the unit was on a 60 amp breaker. Is that correct or is it over amped? I could not find a max amp on the unit similar to the AC compressor nameplate.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #2  
Old 2/4/07, 1:54 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Water Heater Amperage? Maybe this is elec.

Sounds like it is overfused. What gauge wire was used?
Reply With Quote
  #3  
Old 2/4/07, 2:30 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Water Heater Amperage? Maybe this is elec.

Yes, it is over sized.........I have never seen a 60A water heater and most certainly not any made by A O Smith.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 2/4/07, 3:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Water Heater Amperage? Maybe this is elec.

Hint....always take a picture of the nameplate for future reference. Now I know the one you had did not have a nameplate..this is just a general reminder as it is nice for reference later and do it on all appliance nameplates.

Chances are the 50 Gallon water heater is a 4,500W unit, so figuring this for your friend

4,500W/240V = 18.75 x 1.5 = 28A ( next size up rule per 422.11(E) ) 30A breaker is the proper size

Here is the section if you would like to see it...:


(E) Single Non–motor-Operated Appliance.
If the branch
circuit supplies a single non–motor-operated appliance, the
rating of overcurrent protection shall:
(1) Not exceed that marked on the appliance.
(2) Not exceed 20 amperes if the overcurrent protection rating
is not marked and the appliance is rated 13.3 amperes
or less; or
(3) Not exceed 150 percent of the appliance rated current if
the overcurrent protection rating is not marked and the
appliance is rated over 13.3 amperes. Where 150 percent
of the appliance rating does not correspond to a standard
overcurrent device ampere rating, the next higher standard
rating shall be permitted.


Attached Thumbnails
water-heater-amperage-maybe-elec-dsc01553.jpg  



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 2/4/07 at 3:22 PM..
Reply With Quote
  #5  
Old 2/4/07, 3:42 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: Water Heater Amperage? Maybe this is elec.

Another point along this line is; both heating elements are NEVER on simultaneously, hence no need for a huge breaker to handle the load. I found that many people were unaware of this little tidbit of info.
Reply With Quote
  #6  
Old 2/4/07, 3:46 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Water Heater Amperage? Maybe this is elec.

Yeppers......thats why you only use 4,500W in the equation...not the sum of BOTH elements... nice clarrification point as well....



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 2/4/07, 4:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Water Heater Amperage? Maybe this is elec.

Another good point is the NEC defines this as a Cont. load so the conductors have to also be sized at 125% of the non- continuous load.




422.13 Storage-Type Water Heaters






A fixed storage-type water heater that has a capacity of 450 L (120 gal) or less shall be
considered a continuous load.

Ironically enough...422.11(E) says it needs to be 150% on the OCPD and in all Mr. Holts books it desribes it as such....yet 422.13 says it is considered continuous and we know that means 125%....

*Note- if the unit is rated for 100% contin. then that is fine also but I dont see that in standard water heaters....just threw that in.






Part II. Branch-Circuit Requirements

Text was revised to specify that a fixed storage water heater of 120 gallons or less is to be considered a continuous load. This simple change causes feeder/service conductors and overcurrent protection devices to be increased in size.
An electric water heater having a capacity of no more than 120 gallons is considered a continuous load.

Author’s Comment: Circuit conductors and overcurrent protection devices must have an ampacity of not less than 125 percent of the ampere rating of the appliance. Figure 422-1
  • Branch circuit conductors [210.19(A)(1)], overcurrent protection devices [210.20(A)]
  • Feeder conductors [215.2(A)(1)], overcurrent protection devices [215.3]
  • Service conductors [230.42(A)(1)]
Question: What is the calculated load for a 4,500W, 230V water heater?

(a) 15A (b) 20A (c) 25A (d) 30A

Answer: (c) 25A
I = P/E
P = 4,500W
E = 230V

I = 4,500W/230V
I = 20A

Calculated continuous load for conductor sizing and protection = 20A x 1.25 = 25A

The revision to 422.13 ( in 2005 NEC ) specifically identifies an electric water heater with a storage
capacity of 120 gal or less as a continuous load. This revision requires the branch
circuit overcurrent device and conductors to be sized based on 125 percent of the water
heater nameplate rating unless the overcurrent device and the assembly it is installed in
are listed to be used at 100 percent of its continuous current rating. In addition, feeders
and services that supply water heater branch circuits are also impacted by the fact that
this type of equipment is considered to be a continuous load.




Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 2/4/07 at 4:42 PM..
Reply With Quote
  #8  
Old 2/4/07, 6:32 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Water Heater Amperage? Maybe this is elec.

lol....The point is I think mike needed to make the change in his newest book and he probably did already...



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 2/8/07, 1:02 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 802
Default Re: Water Heater Amperage? Maybe this is elec.

Wow. I need to reread this thread again. Holy cow! 30amps max. Thanks Paul



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water Heater Dip Tube Failure jacaron Plumbing 2 2/25/07 12:28 AM
Venting an oil-fired water heater mh718 HVAC 3 11/16/06 10:36 AM
TPR & Combusiton Air thejnicki Plumbing 16 9/18/06 9:55 PM


All times are GMT -4. The time now is 8:47 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts