Default Water heater exhaust venting

The house I was at today had taken the bathroom exhaust fan and connected it into the WH flue for venting to outside. I fired up the WH and when WH fan started it sent fumes into the bathroom next door through the exhaust fan. I told client this was not a good thing, plus it had flexible tubing connected to WH flue. Just wondering if any one else had ever seen something like this? Working on the report right now will check back in awhile. Mark
Attached Thumbnails
water-heater-exhaust-venting-img_4726.jpg   water-heater-exhaust-venting-img_4730.jpg   water-heater-exhaust-venting-img_4737.jpg   water-heater-exhaust-venting-img_4738.jpg  
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/3/10, 5:15 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Water heater exhaust venting

Yes, that's bad! Good catch Mark.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #3  
Old 12/3/10, 5:18 PM
Robert Ernst Robert Ernst is online now
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Water heater exhaust venting

Wow people can really be stupid sometimes. Nothing like killing off the whole family.
Reply With Quote
  #4  
Old 12/3/10, 5:18 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Water heater exhaust venting

That can KILL!!!!!!!!



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #5  
Old 12/3/10, 5:22 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Water heater exhaust venting

Way to keep your eyes peeled!

Often there are issues with the homeowner built basement bathrooms.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 12/3/10, 5:24 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Water heater exhaust venting

Quote:
Originally Posted by mthiltgen View Post
The house I was at today had taken the bathroom exhaust fan and connected it into the WH flue for venting to outside. I fired up the WH and when WH fan started it sent fumes into the bathroom next door through the exhaust fan. I told client this was not a good thing, plus it had flexible tubing connected to WH flue. Just wondering if any one else had ever seen something like this? Working on the report right now will check back in awhile. Mark
OMG
Reply With Quote
  #7  
Old 12/3/10, 5:44 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater exhaust venting

Quote:
Originally Posted by bkelly2 View Post
OMG
I am quite sure that Darwin's Theory of Evolution was wrong. The smarter/stronger/faster are not the majority surviving.....more of the others are!......it's called devolution! In about another 200-300 years, another Neanderthal man may be seen.
Reply With Quote
  #8  
Old 12/6/10, 2:13 PM
Clint a. McKie Clint a. McKie is offline
InterNACHI Member
 
Join Date: Aug 2010
Location: carlsbad,n.m.
Posts: 433
Send a message via Yahoo to cmckie
Default Re: Water heater exhaust venting

Unreal, did the homeowner do the new w/h? they probably thought that it would save time when it would end it instead.



It's up to us as inspectors to find the best results for the clients, even if they don't like it.

www.carlsbad-home-inspector.com
www.activerain.com/clintmckie
clintmckie@yahoo.com
Reply With Quote
  #9  
Old 12/7/10, 4:54 PM
Mark Thiltgen Mark Thiltgen is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: St Michael, MN
Posts: 73
Default Re: Water heater exhaust venting

It's hard to say, it's bank owned and looks like someone came in painted, new carpet and cleaned it up to flip it. They may have even finished the bathroom at that time, client backed out and is looking elsewhere.
thanks for all the feedback from everyone!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
hydronic radiant floor heat on hot water tanks mnicholet Plumbing Inspections 7 4/14/10 5:48 PM
Draft induced furnace venting with water heater jprince1 Inspecting HVAC Systems 8 12/15/08 8:56 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Hot Water Heater djohnson6 Plumbing Inspections 12 12/28/06 9:18 PM
Exhaust fan in room with gas water heater and furnace jweinberg Inspecting HVAC Systems 7 2/18/06 1:23 PM