Question Water heater flue vent taped

New construction, about 6 months old. Natural gas water heaters are located in the garage, exiting through the attic and the roof.

Can the flue vent for water heater be taped at the sections?

Isn't there an appropriate connector for single wall to double wall pipe?

Thanks for the help !!
Attached Thumbnails
water-heater-flue-vent-taped-100_2720-medium-.jpg.jpg
Views:	331
Size:	30.4 KB
ID:	20681  



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

(210) 347-1023
TREC #7654
InterNACHI #06032691

Reply With Quote
  #2  
Old 4/26/08, 10:41 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater flue vent taped

http://www.novaflex.com/productcart/...&idproduct=389
Reply With Quote
  #3  
Old 4/26/08, 11:30 PM
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 3,273
Default Re: Water heater flue vent taped

Taping or caulking is acceptable in my neck of the woods. But just because everybody does it, does not make it right. At least it is not duct tape.
Reply With Quote
  #4  
Old 4/26/08, 11:37 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,605
Default Re: Water heater flue vent taped

Quote:
Originally Posted by lfoster
New construction, about 6 months old. Natural gas water heaters are located in the garage, exiting through the attic and the roof.

Can the flue vent for water heater be taped at the sections?

Isn't there an appropriate connector for single wall to double wall pipe?

Thanks for the help !!
I ususaly see screws underneath the tape Linda



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #5  
Old 4/27/08, 12:04 AM
Mark Nicholet's Avatar
Mark Nicholet Mark Nicholet is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 439
Default Re: Water heater flue vent taped

Connections should be made with 3 screws. Why not use B-vent connector from hot water appliance to B-vent flue.




Mark Nicholet
Apple Home Inspections LTD
My Blog

InterNACHI member
Infrared-Certified
CAHPI(BC) member
BC Licence # 47592
Reply With Quote
  #6  
Old 4/27/08, 5:29 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,376
Default Re: Water heater flue vent taped

The high-temperature metallic tape has been approved by many of the AHJ's in my neck of the woods. You'll probably still find screws underneath the tape, though. I always have. It seems the tape is used as a backup system to help keep the screws in place and to help prevent leaks at the connectors. I'm all for backup systems.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #7  
Old 4/27/08, 8:49 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,342
Default Re: Water heater flue vent taped

Quote:
Originally Posted by lfoster
New construction, about 6 months old. Natural gas water heaters are located in the garage, exiting through the attic and the roof.

Can the flue vent for water heater be taped at the sections?

Isn't there an appropriate connector for single wall to double wall pipe?

Thanks for the help !!
It appears they've used a straightened elbo for a length of pipe and I don't see any screws (or tape) at the eblo joints...non-professional.



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 1:26 AM
Venting an oil-fired water heater mh718 HVAC 3 11/16/06 9:36 AM
TPR & Combusiton Air thejnicki Plumbing 16 9/18/06 8:55 PM


All times are GMT -4. The time now is 4:16 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts