Old 2/21/11, 12:48 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Water heater inside the house...question

Is the write up for a overflow pan and overflow line
terminate in the pan?



Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/21/11, 2:34 PM
Robert Ernst Robert Ernst is online now
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Water heater inside the house...question

I would say it needs a pan for sure. Some areas allow discharge into the pan. The pipe needs to be 6" above the pan. I would also question that strapping.
Reply With Quote
  #3  
Old 2/21/11, 2:49 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Water heater inside the house...question

Any place that an overflow can cause damage ,needs a pan.
Reply With Quote
  #4  
Old 2/21/11, 3:07 PM
Jered Chandley Jered Chandley is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Orlando, Fl
Posts: 18
Default Re: Water heater inside the house...question

Since the enclosure is on the inside of the home a pan is definitely needed.




Central Florida's Premier Home Inspection
Orlando Home Inspection Florida Home Inspection

Jered Chandley
Vice President
1-888-511-SCAN
info@safescantech.com





Reply With Quote
  #5  
Old 2/21/11, 3:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Water heater inside the house...question

You should recommend a pan and flexible water-line connectors on the tank. In CA, the TPR cannot discharge into a pan, and will be required to terminate at the exterior upon replacement of the water heater.

In addition, the straps are improper by CA standards. They must be located in the upper and lower thirds of the tank.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/22/11, 3:48 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Water heater inside the house...question

Thanks everybody....
Reply With Quote
  #7  
Old 2/22/11, 9:55 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Water heater inside the house...question

2009 IRC allows discharge of the TPR into the pan.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 2/22/11, 10:34 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Water heater inside the house...question

Quote:
Originally Posted by jfunderburk View Post
2009 IRC allows discharge of the TPR into the pan.
CA does not follow the IRC.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 2/22/11, 10:38 AM
clambert2 clambert2 is offline
Active Poster
 
Join Date: Jan 2011
Location: Southern California
Posts: 343
Please Note: clambert2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater inside the house...question

Joe,
We in Calif are not under the IRC.

David,
If the water heater is located where if it leaks it can cause damage the manufacturers requie a pan. The TP is not allowed to discharge into the pan, needs to go outside. If the TP cannot discharge outside then a Watts 210 valve and a Pressure relief valve need to be installed.

The straps top third and bottom third of the tank UNDER the insulation blanket NOT over it. And as Jeff said flexible water connectors with insulation also with proper clearance to the flue.

Chuck
Reply With Quote
  #10  
Old 2/22/11, 10:54 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Water heater inside the house...question

Quote:
CA does not follow the IRC.

What's is going to take?

What's it going to take for everyone so STOP being on the Building Code bandwagon?

Will it take a lawsuit from the Seller?

A home inspection is NOT a Code inspection. When you quote the code, for WHATEVER reason, one needs to be damned sure that 1) it is covered in the Code, 2) the Code Enforcer in the area APPLIES your interpretation of the Code, and 3) the violation deals with SAFETY (IMO).

One can bring up an alternate as to what they have observed, but should refrain from stating that anything is a Code violation.

This discussion is a prime example of what I am saying. Codes are obviously not "one size fits all"
Reply With Quote
  #11  
Old 2/22/11, 11:03 AM
clambert2 clambert2 is offline
Active Poster
 
Join Date: Jan 2011
Location: Southern California
Posts: 343
Please Note: clambert2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater inside the house...question

Quote:
Originally Posted by jfarsetta View Post

What's is going to take?

What's it going to take for everyone so STOP being on the Building Code bandwagon?

Will it take a lawsuit from the Seller?

A home inspection is NOT a Code inspection. When you quote the code, for WHATEVER reason, one needs to be damned sure that 1) it is covered in the Code, 2) the Code Enforcer in the area APPLIES your interpretation of the Code, and 3) the violation deals with SAFETY (IMO).

One can bring up an alternate as to what they have observed, but should refrain from stating that anything is a Code violation.


This discussion is a prime example of what I am saying. Codes are obviously not "one size fits all"

I agree, however one code says this is ok and the State we live in and work in says it is NOT ok.
Reply With Quote
  #12  
Old 2/22/11, 11:08 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Water heater inside the house...question

The building boom of 2000 through 2005 saw many structures built...quickly and cheaply...to meet the demand of the seller's market.

The perfect storm has almost fully developed....as these shoddy homes are beginning to crumble, are no longer increasing in value on an annual basis, are harder to sell to buyers who are struggling to qualify through tougher lenders, and banks are acquiring buildings they paid millions to finance and are settling for less to unload.

Sellers and AHJs, alike, are finding themselves being held accountable to an unprecedented degree by those who are stuck with these deteriorating structures.

You don't want to involve yourself in this cluster***** of confusion, interpretation and anger.

The role of a home inspector is to report the present condition of the property....not its compliance with a particular code or standard. If it is unsafe or can create property damage it is to be reported....even if the code at the time it was built, or as interpreted by the particular AHJ who sped by the property fifteen years ago...says it's okay.

Report it and move on....or go ahead and link the future of your business and your assets to the outcome of something you are neither qualified or required to do -- for a mere couple of hundred bucks.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 2/22/11 at 11:12 AM..
Reply With Quote
  #13  
Old 2/24/11, 2:44 PM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater inside the house...question

Quote:
Originally Posted by clambert2 View Post
I agree, however one code says this is ok and the State we live in and work in says it is NOT ok.
Absolutely. We might not quote code in our reports, but it is the basis for what we put in them.

We don't have to report that we follow the IRC, or UPC, or any other standard.

But the fact remains, the rules are different in various locales whether we like it or not.

So, what would you have us do Mr Farsetta? Say that it's OK to allow the TPR to terminate into a pan? We here in CA should abide by the code that applies here for our reporting, not the standard in NY.

When Jeff said CA doesn't follow the IRC, but the UPC, then that means we must say that the TPR cannot terminate in a drip pan. Period.

If that's OK where you live, fine. But we don't have to say the word code in order to apply it in our reports.

Last edited by jhugenroth; 2/24/11 at 7:25 PM..
Reply With Quote
Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/25/11, 7:59 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: Water heater inside the house...question

Mr Hugenroth:

Joe is right. No codes should ever be mentioned in your report. The standards of safety for today. Or according to standards today.
Just because a code in your town allows you to put the TPR into the pan does not mean it is safe and acceptable. Just like some jurisdictions allow a vent exhaust termination closer to door ways and windows. This does not mean we need to tell people they need to change it. Codes are designed for minimum conditions allowed anything less is criminal.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #15  
Old 2/25/11, 9:02 AM
Richard Stanley CMI Richard Stanley CMI is offline
New User
 
Join Date: Feb 2011
Posts: 3
Please Note: Richard Stanley CMI is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater inside the house...question

The entire codes are based on safety.
Everything you write has something to do directly or indirectly with code unless you are nothing but a driveby, realtor worshiping type of inspector.

I have inspected approx 5k homes and probably have a code quote in most of them. The only reason to be afraid of the code is when you don't know it. If a local ahj does not enforce some items in the code, then they just do not have any regard for the safety of their citizens that are paying them - especially when it involves their personal safety or destruction of their personal property.

As for the posted picture - I do not see access to exterior combustion air.
Is that a self closing, weather stripped door? It definitely should have a pan w/a drain from the pan to the extterior or to a waste receptor.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Coming soon. Free, online, fireplace and chimney inspection course. gromicko General Inspection Discussion 15 12/14/09 4:19 PM
Hot Water Heater Question mpeterson Plumbing Inspections 8 3/31/07 1:59 PM
Hot water heater question mgeddie General Inspection Discussion 15 6/7/06 1:00 PM