Default Water heater install in new home - how would you coment?

Came across this installation in a high end custom home at the one year inspection. Wanted to get some thoughts and then I will post what I said in report.

The room that the units are installed in was originally going to be part of the attic space. According to the homeowners, the decision to finish this room was made at the very end of the build. They are using the room as a treadmill room with children play things present. Based on meeting the parents, I doubt that the kids use this room alone, but are present here when a parent is exercising.

My first concern was that the gas units are located in a unconfined room that is part of the home ventilation and is not separately ventilated. Checked the books and they seem to indicate that this is allowable except in bedrooms and bathrooms. However, I have never run into this in a newer home around here and do not particularly like it. Recommended that they install carbon monoxide detectors in here and consider either isolating the water heaters or changing the room to more of a storage room.

The TPR valves are plumbed straight down to the drain pans. I reported this as not allowed and dangerous to the residents in the event that the valves ever activated while people were in the room.

The pans, there are two typical low end pans, are plumbed together, but if you look closely you will notice that they are not plumbed out of the home. I reported this as wrong.

In lieu of properly plumbing the pans out, as best I can figure, they have installed the WAGS safety solenoid valves in the pans. Theoretically these valves would sense water in the pans and turn off the supply. I also did not like that they only ran the inlet plumbing for the right unit through the solenoid safety valve. The left unit, the second in series, solenoid valve is only connected to the gas control of the left unit. Therefore, the system is depending on the right unit solenoid for cutting off water. I feel that they should properly connect both solenoids to inlet lines for the best level of protection. Could it be argued that the installation of these solenoids valves can take the place of plumbing the pans to the exterior from this location inside the home?

I suspect that the plumber forgot to plumb the TPRs and the pans to the exterior and that they installed the solenoid valves as a way to fix it. The home has had a number of plumbing issues, including leaks and mold remediation already, so the quality of the plumbing work was already in question.

Opinions? Anything I missed? Codes that would not allow these units in this areas, rather than it just being unusual and not a good idea?
Attached Thumbnails
water-heater-install-new-home-would-you-coment-water-heaters.jpg   water-heater-install-new-home-would-you-coment-water-heaters-1-.jpg.jpg
Views:	138
Size:	79.4 KB
ID:	26079   water-heater-install-new-home-would-you-coment-water-heaters-2-.jpg.jpg
Views:	129
Size:	83.6 KB
ID:	26080   water-heater-install-new-home-would-you-coment-water-heaters-3-.jpg.jpg
Views:	133
Size:	79.7 KB
ID:	26081  




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #2  
Old 1/9/09, 5:02 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Water heater install in new home - how would you coment?

Don't know about the solenoid, might want to consult with a plumber. As to the rest I don't have a problem with it.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 1/9/09, 5:03 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Water heater install in new home - how would you coment?

You don't have a problem with the installation or you don't have a problem with my comments?




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #4  
Old 1/9/09, 5:16 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Water heater install in new home - how would you coment?

I don't have a problem with the location or the TPR.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 1/9/09, 5:20 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Water heater install in new home - how would you coment?

Quote:
Originally Posted by kweiss View Post
You don't have a problem with the installation or you don't have a problem with my comments?
Those drain pans need a drain.

As far as the solenoids go , I do not recall seeing them other than on HVAC drain pans.

Location is fine.

Gosh I hate when they run flex line that way.

Is that proper B vent on the left. (it looks dis-colored)?

Last edited by belliott; 1/9/09 at 5:25 PM..
Reply With Quote
  #6  
Old 1/9/09, 5:25 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater install in new home - how would you coment?

Quote:
Originally Posted by kweiss View Post
My first concern was that the gas units are located in a unconfined room that is part of the home ventilation and is not separately ventilated. Checked the books and they seem to indicate that this is allowable except in bedrooms and bathrooms. However, I have never run into this in a newer home around here and do not particularly like it. Recommended that they install carbon monoxide detectors in here and consider either isolating the water heaters or changing the room to more of a storage room.

The TPR valves are plumbed straight down to the drain pans. I reported this as not allowed and dangerous to the residents in the event that the valves ever activated while people were in the room.
Maybe its a regional thing, I know where it's warm there are often mechanicals in the attic. Not around here. Anyhow, the CO recomendation is sound, but we often see, around here, mechanicals in unfinished or partially finished basements. Some enclose them (in a "mechanical room") for asthetic reasons, more than anything. They are often, in a ranch home in a "mud room' just off the garage.

Remember they need air to burn too!

As far as the valves go, into the pan is fine or into a floor drain, ok too. I never understood the pipe to the exterior (again, a regional thing, I guess) because how would you readily know if it was discharging?

Check out http://education.nachi.org/show.php?course_id=28 for more.
Reply With Quote
  #7  
Old 1/9/09, 5:34 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Water heater install in new home - how would you coment?

It can freeze up around here.
Texas is different.
They need a place to drain because they are in the attic,and why even have a drain pan at all otherwise
Reply With Quote
  #8  
Old 1/9/09, 5:36 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater install in new home - how would you coment?

Quote:
Originally Posted by relliott View Post

It can freeze up around here.
Really?




Quote:
Originally Posted by relliott View Post
Texas is different
No sh**!
Reply With Quote
  #9  
Old 1/9/09, 5:38 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Water heater install in new home - how would you coment?

Quote:
Originally Posted by rmaday View Post
Really?






No sh**!
I understand the Mexican Language better than southern drawl.

(just kidding)( sorta
Reply With Quote
  #10  
Old 1/9/09, 5:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Water heater install in new home - how would you coment?

You need to consider the issue of makeup/combustion air for the fuel burning appliances.

Take NACHIs water heater tanks course for a better explanation and requirements.

Read the Course materials HERE



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 1/9/09, 6:03 PM
Jonathan T. Hittle's Avatar
Jonathan T. Hittle Jonathan T. Hittle is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Eaton, OH
Posts: 102
Red face Re: Water heater install in new home - how would you coment?

In ohio the pan is required in a finished room. The drain are supposed to be pipe to an indirect drain visable in the room or a floor drain. I am a licensed plumber and have never seen the solenoids piped in this manner, mostly HVAC. Home security systems can place a contact sensor that will shut off the water. The location is fine (if you like them in a finished room). The carbon monoxide detectors are always my advice no matter where. The tprvs are to be piped 2" from floor(in this case pan). I ran into a lot of plumbing problems yesterday as well.(INSPECTING)I never do work on any house I inspect, mostly commercial and industrial. I hope this helps but ever locality has its own rules and regs. Was there a expansion tank?
Reply With Quote
  #12  
Old 1/9/09, 6:44 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Water heater install in new home - how would you coment?

TPR piping here either is plumbed to the exterior and visible, or plumbed to a drain with an air gap.
Reply With Quote
  #13  
Old 1/9/09, 7:58 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,917
Default Re: Water heater install in new home - how would you coment?

Quote:
Originally Posted by jhittle View Post
In ohio the pan is required in a finished room. The drain are supposed to be pipe to an indirect drain visable in the room or a floor drain. I am a licensed plumber and have never seen the solenoids piped in this manner, mostly HVAC. Home security systems can place a contact sensor that will shut off the water. The location is fine (if you like them in a finished room). The carbon monoxide detectors are always my advice no matter where. The tprvs are to be piped 2" from floor(in this case pan). I ran into a lot of plumbing problems yesterday as well.(INSPECTING)I never do work on any house I inspect, mostly commercial and industrial. I hope this helps but ever locality has its own rules and regs. Was there a expansion tank?
Hi John
I believe the tanks only need the expansion bladder if there is a check valve upstream.
Correct?
Reply With Quote
  #14  
Old 1/10/09, 12:45 AM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Water heater install in new home - how would you coment?

I would have a lot of difficulty accepting those TPR's being dumped into those pans without a drain. The TPR's would fill those pans in a heart beat (even just one) and in a finished room, well it would be unfinished and wet.
Bob I don't like the flex either, but what can you do.



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #15  
Old 1/10/09, 6:51 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Water heater install in new home - how would you coment?

As to the secondary drainage pans, I like to see them piped to the soffit area (centered over the front door) so if they ever did leak, the homeowner knows that there's a problem in the attic when they observe dripping over their front door.

If they are not piped to a better location (garage area, basement, soffit area) and there is a water detection system in place, I let it go.

As to the WH's being installed in a living area (or vise versa), I simply remind my clients to NEVER box these in as they will always need combustion air to prevent CO poisoning.

CO detector installation is going to be required by the fire dept. on the Sellers close of escrow mandated walk-through.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspector Listings jbowman Miscellaneous Discussion for Inspectors 230 3/21/12 9:35 PM


All times are GMT -4. The time now is 2:09 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts