Question Water Heater Location

This gas water heater is located in the laundry room. The laundry room is upstairs. 9-10 yr. old home. The dryer is also gas. I saw no vents in the room and the door is hollow door (no vents). Is this acceptable?
Attached Thumbnails
water-heater-location-stines-017.jpg  



Patrick J. Cloninger



Serving Knoxville and surrounding counties
Reply With Quote
  #2  
Old 6/6/08, 3:01 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Water Heater Location

Patrick, you may want to consider taking the advanced water heater course


Check the course material pack located HERE
Calculation of necessary venting requirements are covered in the course.

See section 11 in the course pack.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 6/6/08, 3:33 PM
Patrick J. Cloninger's Avatar
Patrick J. Cloninger Patrick J. Cloninger is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Knoxville, TN
Posts: 288
Default Re: Water Heater Location

Thanks Michael. I mainly wated to know how much vent space is needed, ie. louvered door, vent at top and bottom of door, etc. I will check that out.



Patrick J. Cloninger



Serving Knoxville and surrounding counties
Reply With Quote
  #4  
Old 6/7/08, 10:04 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: Water Heater Location

check out the TPR drain...
Reply With Quote
  #5  
Old 6/7/08, 10:14 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Water Heater Location

Quote:
Originally Posted by rromoser
check out the TPR drain...
OK, I'll bite. What's wrong with the TPR drain?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #6  
Old 6/7/08, 10:38 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Water Heater Location

Quote:
Originally Posted by sstanczyk
OK, I'll bite. What's wrong with the TPR drain?
It may be running uphill, but that could be the angle of pic.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 6/7/08, 10:49 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Water Heater Location

"Combustion air ("make-up air") is required for gas burning appliances at a rate of 50 cu ft / 1000 BTU or else external ventilation is required. Due to the room size, that requirement may not be met (formal sizing calculations were not conducted). External ventilation openings should be within 12 inches (305 mm) of the top of the enclosure, and one within 12 inches (305 mm) of the bottom of the enclosure. No external ventilation was provided. Inadequate supply of combustion air results in incomplete combustion; products of incomplete combustion include carbon monoxide. The room housing the water heater may be inadequately ventilated for the purposes of providing combustion air and we recommend an evaluation and repair by a licensed plumbing contractor."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 6/7/08, 10:53 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Heater Location

I have never seen a calculation to take into consideration the fact that the clothes dryer is actually creating a negative pressure (it is blowing air out of the room). The presence of a clothes dryer vented to the exterior makes it especially important for the appliance to have sufficient combustion air.

The amount of ventilation is fairly complicated. Check your Code Check Plumbing book. If you don't have one, you really should get one.
Reply With Quote
  #9  
Old 6/7/08, 10:56 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Water Heater Location

Quote:
Originally Posted by ccurrins
It may be running uphill, but that could be the angle of pic.
Nooo. The photo? Aren't they supposed to install the water heaters at an angle like that?

Nice seismic straps also. oops.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #10  
Old 6/7/08, 11:08 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Water Heater Location

Quote:
Originally Posted by sstanczyk
Nooo. The photo? Aren't they supposed to install the water heaters at an angle like that?

Nice seismic straps also. oops.
I thought maybe the wall was leaning.. Just trying to give the guy the benefit of the doubt.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 6/9/08, 7:29 PM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Heater Location

Not to mention the ignition source is not elevated to the necessary 18".
Reply With Quote
  #12  
Old 6/9/08, 7:50 PM
Jack L. Gilleland's Avatar
Jack L. Gilleland Jack L. Gilleland is offline
InterNACHI Member
 
Join Date: May 2007
Location: Clayton, OH
Posts: 1,173
Default Re: Water Heater Location

Stephan - 3 elbows to many.
Is it PVC or CPVC?
Does AHJ in Knoxville, TN require seismic straps?



In the world view we are all important and our mere existence effects all life.

Jack Gilleland
Home Inspection Services Clayton
Commercial, Multifamily, and Residential
jgilleland1@att.net
Ohio_Commercial and_Home_Inspections
linkedIn
activerain
Reply With Quote
  #13  
Old 6/9/08, 7:52 PM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Heater Location

Quote:
Originally Posted by dbucknavich
Not to mention the ignition source is not elevated to the necessary 18".
Oh wait...nevermind. It is on the second floor, so it plenty elevated.
Reply With Quote
  #14  
Old 6/9/08, 9:39 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,225
Default Re: Water Heater Location

Quote:
Originally Posted by mlarson
Patrick, you may want to consider taking the advanced water heater course


Check the course material pack located HERE
Calculation of necessary venting requirements are covered in the course.

See section 11 in the course pack.
Alright! Thank you! I'm sending you a gift, dude!
In the video, we calculate combustion air in a couple different situations.



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
  #15  
Old 6/9/08, 9:54 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Water Heater Location

Wasn't begging for a gift Ben but thanks.

The course was well done and useful.

I found the info on FVIR water heaters helpful.

Kenton did a fine job and Paige with the Bradford technician was a nice addition.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
TPR & Combusiton Air thejnicki Plumbing Inspections 16 9/18/06 8:55 PM


All times are GMT -4. The time now is 2:09 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts