is the way this water heater is strapped ok?
Its strapped from the top.
|
| Find an InterNACHI certified Maryland Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
I don't believe it meets seismic bracing requirements, check the first article for your zone requirements and instructions on proper bracing
http://www.seismic.ca.gov/faq.html ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#3
|
|||
|
|||
|
Please Note:
ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
It also looks like the TPR valve does not have an extension and the gas supply does not have a drip loop.
|
|
#4
|
||||
|
||||
|
Quote:
Two straps are required. One in the upper and lower thirds of the unit. Straps must be listed and approved for the application. No drip legs required in most parts of CA Linus. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 3/27/09 at 9:41 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Site grading and drainage | wdevries | Canadian Inspectors | 5 | 10/6/09 10:23 PM |
| Sulphur smell | bsmith | Plumbing Inspections | 2 | 6/6/08 8:32 PM |
| TPR & Combusiton Air | thejnicki | Plumbing Inspections | 16 | 9/18/06 8:55 PM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Miscellaneous Discussion for Inspectors | 53 | 8/30/06 5:58 PM |