Default Water Heater strapping, pic included

is the way this water heater is strapped ok?
Its strapped from the top.

Reply With Quote
Find an InterNACHI certified Maryland Home Inspector (and anywhere else in North America)
  #2  
Old 3/27/09, 8:11 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Water Heater strapping, pic included

I don't believe it meets seismic bracing requirements, check the first article for your zone requirements and instructions on proper bracing

http://www.seismic.ca.gov/faq.html



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #3  
Old 3/27/09, 8:42 AM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Heater strapping, pic included

It also looks like the TPR valve does not have an extension and the gas supply does not have a drip loop.
Reply With Quote
  #4  
Old 3/27/09, 9:22 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Water Heater strapping, pic included

Quote:
Originally Posted by dnasser View Post
is the way this water heater is strapped ok?
Its strapped from the top.
Not in CA. . .

Two straps are required. One in the upper and lower thirds of the unit. Straps must be listed and approved for the application.

No drip legs required in most parts of CA Linus.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/27/09 at 9:41 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Site grading and drainage wdevries Canadian Inspectors 5 10/6/09 10:23 PM
Sulphur smell bsmith Plumbing Inspections 2 6/6/08 8:32 PM
TPR & Combusiton Air thejnicki Plumbing Inspections 16 9/18/06 8:55 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 9:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts