Default Water Heater Supply Piping

Newer installation (3 years).

What would cause this type of corrosion other than a poor install?



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 4:33 PM..
Reply With Quote
  #2  
Old 10/21/07, 10:13 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Water Heater Supply Piping

Wrong adapter dissimilar metals. Steel???

.... Cookie

....



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 10/21/07, 10:19 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Water Heater Supply Piping

A leak due to not tightening the fitting properly.

A leak due to not using Teflon tape/compound.

Not using a di-electric union.

A little fast but not wiping clean all the flux that may have dripped down from the above sweat fitting. This would speed up the corrosion process and eat away at the metal surfaces due to the acids in the flux.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #4  
Old 10/21/07, 10:23 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Water Heater Supply Piping

Quote:
Originally Posted by rcooke
Wrong adapter dissimilar metals. Steel???
I see that as a possibility. The Heater is 3 years old by manufacture date. The Installation date is suggested 2 years ago.

The amount of corrosion (without leakage present) seemed unusual for being 2 - 3 years.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #5  
Old 10/21/07, 10:25 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Water Heater Supply Piping

Quote:
Originally Posted by jsieg

....not wiping clean all the flux that may have dripped down from the above sweat fitting. This would speed up the corrosion process and eat away at the metal surfaces due to the acids in the flux.
Thanks.

I was not aware that excessive flux (not wiped) could potentially cause the corrosion present.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 10/21/07, 10:58 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Water Heater Supply Piping

Quote:
Originally Posted by jhagarty
Thanks.

I was not aware that excessive flux (not wiped) could potentially cause the corrosion present.
It can but not likely unless their was A Lot of flux.

That is a lot of corrosion, so it would need some help, like not using Teflon tape and having a good leak or high moisture. (a leak or high humidity)



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #7  
Old 10/21/07, 11:02 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Water Heater Supply Piping

Also, how well is the vent working??? That could be a source of moisture (steam) comming up from the burner area in a humid basement, etc.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #8  
Old 10/21/07, 11:11 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Water Heater Supply Piping

Quote:
Originally Posted by jsieg
Also, how well is the vent working??? That could be a source of moisture (steam) comming up from the burner area in a humid basement, etc.
Basement was dry. No indication of water intrusion and/or excessive moisture.

The vent has potential as this is a 150 year old plus home. Chimney was recommended for further review due to other factors (including potential obstructions).

Can leaking flue gas cause this type of corrosion?

I do not have a picture of the outlet pipe. The corrosion was only on the inlet.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #9  
Old 10/21/07, 11:21 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Water Heater Supply Piping

Quote:
Originally Posted by jhagarty
Basement was dry. No indication of water intrusion and/or excessive moisture.

The vent has potential as this is a 150 year old plus home. Chimney was recommended for further review due to other factors (including potential obstructions).

Can leaking flue gas cause this type of corrosion?

I do not have a picture of the outlet pipe. The corrosion was only on the inlet.
That is why I asked about the vent... Cold water lines in a basement get a lot of condinsation, mixed with the hot gasses that may or may not be going up the vent pipe could be a contributing factor leading to the corrosion that we see on that supply pipe.
(notice how the corrosion looks like it is kind of wind blown, away from the vent.)

The corrosion could be from a mixture of all the items we listed in the above posts.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #10  
Old 10/21/07, 11:41 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Water Heater Supply Piping

Quote:
Originally Posted by jsieg

That is why I asked about the vent... Cold water lines in a basement get a lot of condinsation, mixed with the hot gasses that may or may not be going up the vent pipe could be a contributing factor leading to the corrosion that we see on that supply pipe.
(notice how the corrosion looks like it is kind of wind blown, away from the vent.)

The corrosion could be from a mixture of all the items we listed in the above posts.
Thanks for the Help.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater supply piping cpetty Plumbing Inspections 6 3/31/07 3:44 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
TPR & Combusiton Air thejnicki Plumbing Inspections 16 9/18/06 8:55 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 2:10 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts