Default Water heater TPR extension piping

Any thoughts on this roller coaster to the drain? Would you comment on it? There was a plumbing inspection certification sticker just out of sight on the top of heater.
Attached Thumbnails
water-heater-tpr-extension-piping-1488-riverwood-dr.-unit-defiance-035.jpg  
Reply With Quote
Find an InterNACHI certified New York Home Inspector (and anywhere else in North America)
  #2  
Old 7/9/09, 9:57 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Water heater TPR extension piping

Difficult call. Hard to tell, but if any part of it is flowing uphill, I may call it out for that reason alone. It is supposed to be "installed to flow by gravity."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 7/9/09, 10:03 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Water heater TPR extension piping

I kind of like it. They managed to use the proper material, didn't block the service access for the lower element, kept it out of the way of damage or interference with other components and terminated into an indirect receptor.

Assuming it's properly sloped, doesn't interfere with the ball valve and is well secured/supported (difficult to confirm in the photo) what's not to like?



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 7/9/09 at 10:07 PM..
Reply With Quote
  #4  
Old 7/10/09, 10:07 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water heater TPR extension piping

Better to drip straight down into the drain pan with a visible 6" air gap. Then pipe the drain pan to the floor drain. I'd mention all those elbows.

John Kogel
Allsafehome.ca
Reply With Quote
  #5  
Old 7/13/09, 8:37 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Water heater TPR extension piping

This setup does not violate any of the 13 requirements of IRC 2006, P2803.6.1, Requirements for Discharge Pipe.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #6  
Old 7/13/09, 9:03 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Water heater TPR extension piping

2006 IRC P2803.6.1 Requirements for discharge pipe. The discharge piping serving a pressure-relief valve, temperature relief lve or combination valve shall:
1. Not be directly connected to the drainage system.
2. Discharge through an air gap located in the same room as the water heater.
3. Not be smaller than the diameter of the outlet of the valve served and shall discharge full size to the air gap.
4. Serve a single relief device and shall not connect to piping serving any other relief device or equipment.
5. Discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors
in areas subject to freezing, discharge piping shall be first piped to an indirect waste receptor
through an air gap located in a conditioned area.
6. Discharge in a manner that does not cause personal injury or structural damage.
7. Discharge to a termination point that is readily observable by the building occupants.
8. Not be trapped.
9. Be installed to flow by gravity.
10. Not terminate more than 6 inches (152 mm) above
the floor or waste receptor.
11. Not have a threaded connection at the end of the piping.
12. Not have valves or tee fittings.
13. Be constructed of those materials listed in Section P2904.5 or materials tested, rated and approved for
such use in accordance with ASME A112.4.1



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #7  
Old 7/13/09, 9:59 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Water heater TPR extension piping

Hard to tell from the photo, but is the pipe diameter smaller than the valve discharge? If that is ok, I would not write it up - it is much better than most that I see !



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
flammable vapor ignition resistant dbaucum General Inspection Discussion 35 2/19/08 1:42 PM
NACHI releases a free, online Water Heater TPR Valve Discharge Piping mini course. gromicko Inspection Education & Training 3 5/25/07 11:46 PM
Water Heater Dip Tube Failure jacaron Plumbing Inspections 2 2/24/07 11:28 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 2:10 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts