It seems like this water heater has a TPR with a drain going up (instead of horizontal or down), and also an alternative drain valve, which seems too high up from the floor. What do you think of this installation? Thank you. Last edited by barena; 2/6/06 at 3:19 PM.. |
|
#2
|
|||
|
|||
|
OK,
Maybe it is just me but I thought the following needed to apply here...atleast it does where I am from. 1.) The TPR should not drain uphill per ( 2803.6.1-03 IRC ) and (608.5 - 03 UPC ) 2.) If it is a gas water heater ( which it is ) and their is no ability to achieve a gravity drain the use of a Watts 210 shut off is allowed but still has to have a PRV. 3.) Also the discharge pipe on the water heater has to be minimum 3/4" 4.) Since I can't tell...is this TPR within 6" of the top of the tank? Maybe someone else has even more details on this...but I would make a note if it for the fact I cant see the discharge end anyway... Ok....back over to electrical where I belong...Bye Bye Paul W. Abernathy |
|
#3
|
||||
|
||||
|
Please Note:
rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have no idea what they are doing with this, but I can't even see a TPR valve at all, nevermind the pipe going up. And why is the hole at the side of the tank so big?
Is this some goofy attempt at recirculating? I think you should recommend the homeowners call a plumber. Today!!! |
|
#4
|
|||
|
|||
|
I have to agree.......I can honestly say I do not recall ever seeing one done in this manner.
Paul W. Abernathy |
|
#5
|
||||
|
||||
|
Funky set-up.
Is there an end to that piping (in question)? |
|
#6
|
|||
|
|||
|
Here in the Chicago area the TRP drain line must be with 6" of the floor. with no cap.
The flexible gas line has tp go, should be hard piped with drip leg to water heater. Plumber needed quick. Also wondering about large hole? Michael Cotten Cornerstone Home Inspections Inc |
|
#7
|
|||
|
|||
|
lol....the large hole was due to the LAST explosion from this unit...
Paul W. Abernathy |
|
#8
|
|||
|
|||
|
Please Note:
jwortham is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
|||
|
|||
|
Please Note:
Tim Spargo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Plastic for a TPR drain is a no no as well.
Plumbers use flex lines sometimes to connect to the drain line sometimes, but pressure rated flex lines. Copper, braided etc. |
|
#10
|
||||
|
||||
|
Quote:
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#11
|
||||
|
||||
|
Please Note:
jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
CPVC (identified on the piping) is allowable as it is rated for high temperatures. I can't quite tell fromt eh photo, but it appears that there is a yellow band on the pipe (which is the mark of "Flow Gold" brand CPVC.)
I was taught that PVC is not allowable as it is not rated for the high temperatures that could be present at the TPV release, especially if it is a slow leak over an extended time. I have no supporting documentation on that - just what I was taught. |
|
#12
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
the so called ''hole'', looks like some thing covering the tpr rather than a hole. maybe a piece of pipe insulation? or something covering the tpr, if so, that's also a big no no. the pop up mechanism looks like it won't be able to "pop up" if it has to.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Solar water heating + electric water heater | Todd M. Soper | Plumbing Inspections | 20 | 5/30/07 6:31 AM |
| Hot Water Heater | djohnson6 | Plumbing Inspections | 12 | 12/28/06 9:18 PM |
| Venting an oil-fired water heater | mh718 | Inspecting HVAC Systems | 3 | 11/16/06 9:36 AM |
| Hot water heater question | carolinainspector | Plumbing Inspections | 9 | 6/19/06 1:59 PM |