Default Water Heater Vent pipe

Forgive me if I am being naive, I just thought the requirement was steel vents not PVC, due to the heat produced. Any objections, comments?
Attached Thumbnails
water-heater-vent-pipe-dscf8394.jpg  



David K. Kraemer
Inspector Catch-it
http://www.inspectorcatchit.com
(661) 948-3375
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #2  
Old 9/10/09, 5:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Water Heater Vent pipe

Quote:
Originally Posted by dkraemer View Post
Forgive me if I am being naive, I just thought the requirement was steel vents not PVC, due to the heat produced. Any objections, comments?
I see a Direct Vent water heater with blower assist.

The PVC looks fine from here though I'm not sure about the hubless connector. Check the mfg specs.


Hey there is no shut off valve.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector


Last edited by mlarson; 9/10/09 at 5:14 PM..
Reply With Quote
  #3  
Old 9/10/09, 5:12 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: Water Heater Vent pipe

http://www.checkthishouse.com/water-...wscr=1280x1024




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #4  
Old 9/10/09, 5:32 PM
David K. Kraemer David K. Kraemer is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Lancaster, CA
Posts: 24
Default Re: Water Heater Vent pipe

Thank you gentlemen, that was very helpful. Michael, there is a ball valve, it just cannot be seen from the angle of the picture.



David K. Kraemer
Inspector Catch-it
http://www.inspectorcatchit.com
(661) 948-3375
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Water heater vent pipe - Is this OK wsiegel Plumbing 6 9/5/09 1:03 AM
Gas Water Heater Flue Pipe Connected To Plumbing Vent Pipe bwilliams Plumbing 6 8/7/09 11:32 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Do you put polybutylene in the Summary? jfunderburk Plumbing 36 11/27/07 12:56 AM


All times are GMT -4. The time now is 6:48 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts