Default Water Heater Venting

I live in Michigan (cold). I inspected a handy person renovated house today and a new water heater has been installed. The vent goes through the foundation wall and then rises two stories on the outside of the house above the roof line to vent. I know that you cannot vent a water heater as this one has been vented using single wall vent, but can one use B-vent to vent a water heater where the entire vertical length is outside in the cold? Also, if anyone knows a code reference it would be appreciated.

kevin
Reply With Quote
  #2  
Old 3/8/07, 10:51 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Water Heater Venting

Are you asking if a B-vent can be outdoors?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 3/9/07, 7:09 AM
Kevin R. Goff Kevin R. Goff is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Holt, MI
Posts: 98
Default Re: Water Heater Venting

Yes, but also givin the situation where so much of the vent is going to be exposed to the cold (approximately 25' of vertical rise). It seems to me that the hot flue gases would cool too quickly and form condensate. The condesate would cause the vent to rust and allow condensation to flow back to the water heater (via the vent). I think! My reasoning would also lead me to conclude that the cooling of the vent gases would cause backdrafting of the flue gases at the vent hood. So my reasoning says that you cannot use exposed B-vent as I've described, but I'm looking for validation from others (especialy those with a plumbing/mechanical background) and any code information to back me up?

Kevin
Reply With Quote
  #4  
Old 3/9/07, 9:12 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Water Heater Venting

I'm not aware of anything that limits the length outside, as long as it was secured from movement, but let's get a plumber to comment about it. A photo would help. Was there proper clearance from the eaves and house siding?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 3/9/07, 9:47 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Heater Venting

Check the manufactuer's instructions, they will specify that in cold climates vents run up the exterior of a strucutre should to be in an insulated chase. For an example, see "Outdoor Vents" on page 20 here:

http://www.duravent.com/docs/instruct/shbook.pdf
Reply With Quote
  #6  
Old 3/10/07, 9:18 AM
Kevin R. Goff Kevin R. Goff is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Holt, MI
Posts: 98
Default Re: Water Heater Venting

Thank you Michael - the handbook is just what I was looking for. My father is a retired mechanical inspector for the same city the house in question resides, but he's in retirement land and I haven't been able to reach him.

When I ran into the same issue with a B-vent running vertically for about 25' on the exterior of a house (not enclosed in a chase), for a floor furnace, he said there is no way the city would allow this type of uninsulated installation for exactly the same resons listed in the handbook.

I wanted to make sure it also applied to water heaters and it appears it applies to all B-ventied flues, regardless of the appliance.

Thank you again,

Kevin Goff
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Client wants a new water heater adirienzo General Inspection Discussion 47 7/14/10 2:03 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
TPR & Combusiton Air thejnicki Plumbing Inspections 16 9/18/06 8:55 PM


All times are GMT -4. The time now is 9:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts