Default water heating venting

This state water heater, natural gas, 1998, has a vent through the sill plate to what looked like a gas fireplace type termination. but it appears to me from the size that someone just brought the old gas chimney down to the water heater. It doesn't seem to have a power vent.

Anyone seen one like this? Should it have a standard open draft chimney fitting and go above the roof?2008 3 13 cobb and montfort 005.jpg
Attached Thumbnails
water-heating-venting-2008-3-13-cobb-and-montfort-005.jpg  
Reply With Quote
  #2  
Old 3/17/08, 3:04 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: water heating venting

Quote:
Originally Posted by tglover
This state water heater, natural gas, 1998, has a vent through the sill plate to what looked like a gas fireplace type termination. but it appears to me from the size that someone just brought the old gas chimney down to the water heater. It doesn't seem to have a power vent.

Anyone seen one like this? Should it have a standard open draft chimney fitting and go above the roof?2008 3 13 cobb and montfort 005.jpg
Ted, I have never seen this setup.
I highly doubt that heater is intended for sidewall termination.
The lack of a draft hood makes me question how well it drafts to the exterior.
Consult the mfgs. documents or rep.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 3/18/08, 1:41 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: water heating venting

Quote:
Originally Posted by mlarson
Ted, I have never seen this setup.
I highly doubt that heater is intended for sidewall termination.
The lack of a draft hood makes me question how well it drafts to the exterior.
Consult the mfgs. documents or rep.
Without a draft hood it would vent "too well" to the exterior on certain days. The draft hood performs the same function as a barometric damper on an oil fired appliance......reduces overdraft on windy days. Overdrafting sucks exhaust gases out of the appliance too quickly and they don't give up the amount of heat they should to the intended function of water or air heating....thus the appliance efficiency drops.

But unless this unit is certified for sidewall venting and that is the approved vent system, all installed properly, some yahoo is putting a family in danger.
Reply With Quote
  #4  
Old 3/18/08, 2:37 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: water heating venting

A natural draft appliance WILL NOT vent properly without a draft hood. This installation is wrong, no matter how you look at it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 3/18/08, 12:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: water heating venting

Brian. I wasn't very clear in my draft statement. My concern was indeed that ther would be draft problems resulting in flame lifiting from the burner. In short, it's a mess.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #6  
Old 3/18/08, 2:22 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: water heating venting

Quote:
Originally Posted by jpope
A natural draft appliance WILL NOT vent properly without a draft hood. This installation is wrong, no matter how you look at it.
A DIRECT-VENT SERIES does not need a draft hood....

It has a Direct-vent design that draws combustion air from outside
the home ensuring a sufficient air supply for proper heater operation.

The "Coaxial” direct-vent system combines venting and air intake channels in a single pipe, requiring only one opening in the outside wall.
Reply With Quote
  #7  
Old 3/18/08, 2:25 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: water heating venting

Reply With Quote
  #8  
Old 3/18/08, 2:32 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: water heating venting

Quote:
Originally Posted by dvalley
A DIRECT-VENT SERIES does not need a draft hood....
Some direct vent types have draft hoods.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #9  
Old 3/18/08, 2:34 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: water heating venting

Quote:
Originally Posted by mlarson
Some direct vent types have draft hoods.
I never said they didn't.
Reply With Quote
  #10  
Old 3/18/08, 8:28 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: water heating venting

In any case, the vent flue appears to be too big for that size water heater.

Ditto, no draft hood, side vent, etc.

DIY special, always dangerous



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #11  
Old 3/18/08, 8:46 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 696
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: water heating venting

A close-up pic of the outside vent cap would help. It could be drawing air thru the outer lining as proposed already. Page 3-5 of this manual shows a DIY installation.

http://www.gsw-wh.com/pdfs/products/...directvent.pdf


Last edited by jkogel; 3/18/08 at 8:58 PM..
Reply With Quote
  #12  
Old 3/18/08, 9:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: water heating venting

Quote:
Originally Posted by dvalley
A DIRECT-VENT SERIES does not need a draft hood....
A direct vent is not a natural draft.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 3/19/08, 6:53 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: water heating venting

Quote:
Originally Posted by jpope
A direct vent is not a natural draft.
Where did I say that it was?
Reply With Quote
  #14  
Old 3/19/08, 5:39 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 499
Default Re: water heating venting

I don't know of any Direct-Vent Water Heaters that are not induced fan forced. They also have limitations on elbow design and length of total H/V run.
Your pic, and unit shown just can't be legal/safe.

IMHO
Reply With Quote
  #15  
Old 3/19/08, 5:53 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 197
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: water heating venting

Bradford White do a direct vent water heater without a power vent. As proposed several times now, it could be drawing air through the outer lining of a dual-lined flue.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues 293 2/10/08 2:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 12:44 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts