Default Water Pressure 75 psi .... question

Water pressure test 75 psi at the outside faucet where the house cutoff
is located...right by front entry door...Ran all faucets and baths on the inside
house and flushed toilets...did not notice anything abnormal.


Plumber did come out to the house to upgrade water heater. Installed a
TPR pipe, earthrquake straps and a pan. Water heater was located inside
house in a closet.

The buyers been in the house for a week. She saying water pressure is
low...and really gets effected if water is running in more than one place at
the same time.

Such as washing dishes and taking a shower.....

Anybody know what could be causing this .........

Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #2  
Old 4/1/09, 1:54 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Water Pressure 75 psi .... question

Distribution pipe blockage? A section of galvanized supply pipe with the bore reduced by corrosion?

A leak?

That photo looks like screensaver I used to have.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #3  
Old 4/1/09, 2:35 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Water Pressure 75 psi .... question

Quote:
Originally Posted by dnasser View Post
The buyers been in the house for a week. She saying water pressure is
low...and really gets effected if water is running in more than one place at
the same time.

Such as washing dishes and taking a shower.....

Anybody know what could be causing this .........

Low flow
Reply With Quote
  #4  
Old 4/1/09, 10:18 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Water Pressure 75 psi .... question

Galvanized supply pipes. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 4/1/09, 11:58 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Water Pressure 75 psi .... question

Quote:
Originally Posted by jpope View Post
Galvanized supply pipes. . .
After looking at the picture again, this is probably the best answer so far.
Reply With Quote
  #6  
Old 4/1/09, 12:07 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Water Pressure 75 psi .... question

Did you check for functional flow during the inspection? In my states, we are required to. Generally, that means running the shower and flushing the toilet at the same time. If there is no reduction at the shower, then that is considered functional.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 4/1/09, 7:24 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,226
Default Re: Water Pressure 75 psi .... question

did they install a valve at the tank?
Reply With Quote
  #8  
Old 4/1/09, 7:46 PM
Gary Oleski Gary Oleski is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Bridgeport, CT
Posts: 740
Default Re: Water Pressure 75 psi .... question

"Anybody know what could be causing this ........."

Imagination? - had one like that in Connecticut last year. She would take showers at the gym that had a big, no restriction shower head. Just not the same at home.



Gary Oleski Home Inspections
Home Inspections Connecticut
Connecticut . 06610
NACHI04012833
CT#HOI.341
C M I
Reply With Quote
  #9  
Old 4/1/09, 8:03 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Water Pressure 75 psi .... question

Quote:
Originally Posted by goleski View Post
"Anybody know what could be causing this ........."
Any whole house water filters or water softener?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #10  
Old 4/1/09, 11:02 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Water Pressure 75 psi .... question

Quote:
Originally Posted by goleski View Post
...a big, no restriction shower head...
Sounds like the "Commando 450" (Seinfeld episode).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 4/2/09, 12:13 AM
Richard Fitzwater Richard Fitzwater is offline
InterNACHI Member
 
Join Date: Jan 2009
Location: El Paso, TX
Posts: 97
Default Re: Water Pressure 75 psi .... question

Reduction in pipe size is likely the cause. Or too small of a main line to the home. Sellers' Disclosure?

If it worked fine prior, I agree with the interior corrosion of the galvanized pipe.





Richard Fitzwater
FYI Property Inspection
El Paso, TX

TREC#8317
www.el-paso-home-inspector.com
www.fyiproperty.homestead.com
Reply With Quote
  #12  
Old 4/2/09, 12:34 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Water Pressure 75 psi .... question

Odd, I seemed to encounter a flow problem yesterday myself????

Last edited by bkelly2; 6/12/09 at 6:48 PM..
Reply With Quote
  #13  
Old 4/2/09, 4:43 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Water Pressure 75 psi .... question

Mineral buildup in the pipes from all the wonderful minerals in our water supply. At least down here in San Diego.



NACHI 2005 U.S. Member of the Year
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #14  
Old 4/3/09, 10:43 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water Pressure 75 psi .... question

Quote:
Originally Posted by bkelly2 View Post
Odd, I seemed to encounter a flow problem yesterday myself????
Brian, is that some Arizona prehistoric water that's spewing out of that shack??
Reply With Quote
  #15  
Old 4/4/09, 12:49 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,892
Default Re: Water Pressure 75 psi .... question

Looks like a PRV in the line. Has somebody screwed with it???
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Site grading and drainage wdevries Canadian Inspectors 5 10/6/09 10:23 PM
Water Pressure..... David Smfh Plumbing Inspections 7 5/4/08 1:49 PM
Hot Water Heater djohnson6 Plumbing Inspections 12 12/28/06 9:18 PM


All times are GMT -4. The time now is 9:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts