#1
|
|||
|
|||
|
What is considered too high of water pressure in a 3 year old home? At the exterior Hose bibs I measured 98lbs pressure. There appeared to be no problems but its a rare thing to see such high pressure so I'm wondering.
Whats the reasonable range? Peter Siposs Absolute Home Inspections Home, Mold, IAQ, Radon, & Lead Based Paint Liberty Lake, WA Serving Eastern WA & Northern ID Nachi# 05100181 peter@absolute-home-inspections.com |
|
#2
|
|||
|
|||
|
Please Note:
Brandon J. Whitmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
80 lbs max. as far as I know. Otherwise, you could blow seals, etc.
|
|
#3
|
||||
|
||||
|
80 psi, regardless of age. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Around here it is not unusual to find excess of 80 psi at exterior hose bibs/sill cocks and the acceptable 40-80 psi at the interior fixtures.
The regulated side is always before the WH so all supplies to fixtures comply within the house. I just note the different readings and go on, most prefer the higher pressure for car washing, landscape and pool usage. Getting the chores done quicker is their logic. I'll see what today brings and post pix if mixed pressure is present. ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#5
|
||||
|
||||
|
P.S. I only test at laundry on new or vacant properties and write untested pressure on the rest...no faucet adapters for me, dismantling fixtures to install an adapter for pressure gauge can and has caused problems with sellers...and tapping the WH drain has also proved disastrous with tank debris clogging my pressure gauge or the tank drain valve not closing properly after testing...I've orphaned/sacrificed more than one gauge so I could finish the inspection and leave with assurance of no leakage...plumbers were nice enough to heed the note I left and return the gauge...sometimes the sacrifice was cheaper then the retrieval
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good Last edited by badair; 6/2/09 at 1:56 AM.. |
|
#6
|
||||
|
||||
|
I like seeing 70-80 lbs on municipal water pressure.
Anything higher needs a pressure reducer....
|
|
#7
|
||||
|
||||
|
Quote:
|
|
#8
|
|||
|
|||
|
If a home is supplied by a pumped system instead of elevated tanks, water pressure can vary considerably with the time of day and usage in the community because centrifugal pumps deliver a pressure that follows a curve, decreasing as the flow increases. In such cases, I would recommend further review with the possiblity of installing (or adjusting if already installed) a pressure regulator. I do agree with the above about disassembling plumbing and exposing the inspector to possible damage problems and/or floods. Consequently, I usually test at a hose bib outdoors. With no waterbeing consumed in the home that will be as accurate as needed in most cases.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#9
|
||||
|
||||
|
Please Note:
bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
It's pretty common around here that exterior bibs are plumbed before a reducer. Thus giving exterior hoses/bibs better pressure and leaving all interior plumbing @ 70-80 psi.
|
|
#10
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
When there is a regulator, do you comment on the need for an expansion tank if there is none?
|
|
#11
|
||||
|
||||
|
Regardless of whether or not there is a regulator, an expansion tank is not required unless the street pressure (building supply pressure) is greater than the relief valve pressure setting. Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#12
|
|||
|
|||
|
Up in Western Maryland (Cumberland) the municiple water supply pressure is 125 lbs. Kinda rough on bubber clad washer hoses, better always use stainless clad. They don't regulate individule properties. The city controls all pressures. May recommend buyer/seller check with local utility as to the acceptable pressures.
|
|
#13
|
||||
|
||||
|
Quote:
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas. |
|
#14
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
||||
|
||||
|
Quote:
Put in above reducer set it at 40 lbs . We are all happy use less water and does not hurt cost about $40;00. Thanks to all good post good answers. ...Cookie If I can answer any questions please send me email Roycooke@hotmail.com On an inspection and need immediate help call my cell 613-827-2011 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Building Science- research from respected sources | Brian A. MacNeish | Ancillary Inspection Services & Additional Topics | 17 | 7/12/11 7:31 AM |
| IAC2 In new residential construction | mcyr | IAC2 Indoor Air Forum | 0 | 10/9/07 7:45 PM |
| TPR & Combusiton Air | thejnicki | Plumbing Inspections | 16 | 9/18/06 9:55 PM |
| Need Help On Chimney Liners | Nick Scibetta | Exterior Inspections | 10 | 1/11/06 10:53 PM |