Ripped this off another forum. Found it of value so it's being passed on.

"Peter G. Engle, PE" <Pete@ALMOSTHOME.COM> wrote:

Yeah, that one really got me screwed up when we did it in college thermodynamics. But here goes:

Insulation acts in a linear fashion for heat transfer through the material. In math terms, H=kxT, or heat loss equals the thermal constant (U value) times the thickness of the insulation times the Temperature difference between inside and outside. More simply – if you double the thickness of the insulation, you cut the heat loss in half. This, we pretty much all know intuitively. But it’s only true for flat surfaces. There’s a lot of simplification that goes on to get to that simple formula.

When you start insulating cylinders, you can’t ignore the effect of curvature. If the insulation is thin, the effects of curvature are small, and the formula above works fine. But as the insulation gets thick, the surface area of the outside increases with the square of the thickness while the surface area of the inside stays constant. Effectively, the heat has more “pathways” to escape. And since these pathways increase in a geometric way while the thickness only increases in a linear way, there is a crossover point where the heat loss actually begins to increase with thickness. It turns out that for any given set of inside and outside temperatures, insulation factors, and cylinder geometry, there’s an optimum insulation thickness where heat loss is minimized. If you apply any more or less, the heat loss increases. It really works this way. We worked through the math, and it really does happen. Go figure.

What’s pretty cool is that the water heater manufacturers aren’t dumb – they study basic thermodynamics, too. They already insulate water heaters to the optimum level for the type of insulation used. To get more insulating value in modern water heaters, they haven’t increased the thickness, they’ve changed the insulation. Insulation with a higher R-value gives you more insulation in less thickness, and the magic crossover point moves to a lower total heat loss level, even with reduced insulation thickness. The ideal insulation would have infinite R-value, so the thickness could approach zero, and still have zero heat loss.

But I digress. The bottom line is that with water heaters, if you go slapping on a loosely fitting blanket of fiberglass, chances are that you will actually increase the heat loss. Pretty neat, huh?

Peter G. Engle, PE
Almost Home, Inc.
www.almosthome.com

Replies:

Here in the Water Wonderland of Michigan, the utility companies actually paid people to go door to door and install water heater insulation blankets. As the blanket insulated and held heat on the gas control valve, the "rubber" seals got hotter than designed for and started leaking.

We have found gas leaks on abt 90% of insulated gas water heaters at the top function knob; on - off - pilot knob. I think the valve was designed to be a little above room temp and adding insulation too close raised that temp 20 degrees or so. As a former slum lord it was not uncommon for me to spray the knob with WD-40 and stop the leak, for a couple months.

I like Peter's explaination and it makes sense.



It's never made sense to me to insulate a gas water heater unless it's a direct vent type and then only the tank should be insulated not the control valve.

In order for a gas water heater to work properly, you have to leave off enough insulation blanketing around the draft diverter to allow air in, you can't cover the control valve, the access cover for the burner plate or the air intakes on the underside of the tank or on the sides. Once you've left that much of the tank uninsulated, there's not much point in trying to wrap it anyway.

My point to homeowners is that the tank manufacturers have figured out how they can achieve maximum energy savings with the way they've insulated their tanks. Adding more insulation might give one a warm and fuzzy but it's probably money wasted.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #2  
Old 7/1/06, 12:21 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: WH blanket

Quote:
Originally Posted by badair
The bottom line is that with water heaters, if you go slapping on a loosely fitting blanket of fiberglass, chances are that you will actually increase the heat loss. Pretty neat, huh?
Well I never....

Good article. Thanks.
Reply With Quote
  #3  
Old 7/2/06, 12:02 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: WH blanket

If only the US Dept of Energy aggreed with the aforementioned PE.

Quote:
A tank that's warm to the touch needs additional insulation.
Reply With Quote
  #4  
Old 7/2/06, 1:56 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: WH blanket

If only the US Dept of Energy aggreed with the aforementioned PE.

Quote:
A tank that's warm to the touch needs additional insulation.
Actually, the U.S. Department of Energy does agree with the aforementioned P.E., and the aforementioned P.E. is correct.

But a "tank that's warm to the touch" is an oversimplification. It would depend on where the heat is coming from that causes the tank to be warm to the touch. Here in sunny San Diego over the past week, with temperatures in the 90s and 100s, probably every tank was warm to the touch, especially those in exterior utility closets.

What we need is a tank on a conveyor belt so that when it's cold, the tank gets moved into the insulated utility closet, and when it's hot, the tank gets moved outside to soak up that solar heat and lower utility costs.

However, water heater manufacturers probably did their calculations at their recommended temperatures, so if one runs the water heater at the hottest setting, the insulation probably lets some heat through, causing the tank to be warm to the touch.

So there could be many different factors that go into determining if the water heater needs an insulation blanket. If one buys a modern water heater (one made after 1994, I believe it is) and keeps the thermostat at the manufacturer's recommended setting, and installs the water heater in a protected location (exterior utility closet, garage, interior utility closet), an insulation blanket is probably a waste of money that could better be spent on margaritas .



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #5  
Old 7/2/06, 6:11 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: WH blanket

One reallly never knows who is right or wrong when polar opposite information exists. I'm sticking with the P.E. looks like he's done the math correctly.

I really wanted to stess the issues about the seals leaking at the gas valves and impingement to combustion and draft air when the insulation is improperly installed at a gas WH.

Food for thought when inspecting jacketed units. Just like the pipe insulation needs to be cut back 6" away from draft hood and flue.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #6  
Old 7/2/06, 7:10 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: WH blanket

I have a insulative blanket on my electric hotwater heater. The formula provided by the engineer maybe correct but the curveatuer of a 60 gallon tank would probably not really effect the equation in any great manner. When I put my hand in between the metal jacket and fibreglass jacket you can feel the trapped heat. Heat that otherwise would be disapating to the surronding air.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Space Blanket? bkelly2 Inspecting HVAC Systems 3 8/22/07 1:26 PM
Insulation blankets rray Plumbing Inspections 35 12/9/06 9:38 AM


All times are GMT -4. The time now is 9:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts