InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Plumbing

Notices

Plumbing Contains discussions about plumbing.

Reply
 
LinkBack Thread Tools
  #1  
Old 2/21/09, 5:05 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 667
Default WH vent pipe

I never saw this before - it looks like a dryer hose connected to the wh. All the references I have indicate a single walled metal pipe to be used as a gas appliance vent connector. Aside from that fact that it's not screwed into the collar, this one doesn't seem right. Any thoughts?
Attached Thumbnails
wh-vent-pipe-wh-vent.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 2/21/09, 5:24 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,789
Default Re: WH vent pipe

not even close



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #4  
Old 2/21/09, 5:51 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 667
Default Re: WH vent pipe

Yeah, this one was not double-walled and the ends were cut eliminating any labeling that might signify an approved material. I thought so. Thanks for the replies.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #5  
Old 2/21/09, 5:59 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: WH vent pipe

Quote:
Originally Posted by bsmith View Post
I never saw this before - it looks like a dryer hose connected to the wh. All the references I have indicate a single walled metal pipe to be used as a gas appliance vent connector. Aside from that fact that it's not screwed into the collar, this one doesn't seem right. Any thoughts?
Hi Bill,

Looks like Dura Connect, single wall is fine until it goes through a ceiling. Was there double wall going through the attic?

I see these installations here regularly at newer homes, no problem.
Reply With Quote
  #6  
Old 2/21/09, 6:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: WH vent pipe

Quote:
Originally Posted by dduffy View Post
Looks like Dura Connect, single wall is fine until it goes through a ceiling.
Except for the missing connectors. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 2/21/09, 6:05 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: WH vent pipe

Quote:
Originally Posted by jpope View Post
Except for the missing connectors. . .
I think that was mentioned "Senior Zinsco"----
Reply With Quote
  #8  
Old 2/21/09, 6:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: WH vent pipe

Quote:
Originally Posted by dduffy View Post
I think that was mentioned "Senior Zinsco"----
My point being - the connector is absolutely necessary at the B-vent transition. If it doesn't have the proper connector, well, then it's improper



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 2/21/09, 6:18 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: WH vent pipe

Quote:
Originally Posted by jpope View Post
My point being - the connector is absolutely necessary at the B-vent transition. If it doesn't have the proper connector, well, then it's improper
I cannot see the ceiling in the picture, but your (invisible observations) would be correct if the proper connector(s) is-are missing---

By the way.....what's with NO Zinsco Pictures for the LONGest time?...I truly MISS THEM "Mr. Santa Zinsco Clarita"---Cookin Baby...Cookin---

You still in the "Inspection Business"?---

OK...I'd be happy to see at least one Federal Pacific doing a little cookin-----....work with me ole buddy---
Reply With Quote
  #10  
Old 2/21/09, 6:27 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: WH vent pipe

Quote:
Originally Posted by dduffy View Post
Hi Bill,

Looks like Dura Connect, single wall is fine until it goes through a ceiling. Was there double wall going through the attic?

I see these installations here regularly at newer homes, no problem.
Agreed. (Don't overlook the insulation too close to the draft hood and vent pipe.)



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 2/21/09, 6:30 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 667
Default Re: WH vent pipe

Good call Dale - Dura Connect - a new one for me. Jeff, you got it right too - no connector at top or bottom. So: proper vent connector with improper connections at the wh and b vent. I love this bb!
Much appreciated guys.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #12  
Old 2/21/09, 6:38 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,697
Default Re: WH vent pipe

Quote:
Originally Posted by bsmith View Post
Good call Dale - Dura Connect - a new one for me. Jeff, you got it right too - no connector at top or bottom. So: proper vent connector with improper connections at the wh and b vent. I love this bb!
Much appreciated guys.
Hi Bill...I was just looking at my link...you know, I think that is rated as Type-B....but I am not positive...it says one inch clearance to combustibles as "B"...but I do not know the rating of the material without doing a little more digging.

Jeff Pope may know whether it's "B" rated or not even being single wall.

I know it DOES NOT bend all that easy (i've tried it)....really some tough material.

Oh...and I forgot about the "Twist Lock Connectors" which was cut from the portion you have posted at the draft hood.

From Dura Connect website:

B Gas Vent > 4" Dura-Vent B-Vent

Quote:
SKU: 69222
Dura-Connect Gas Connector Pipe
Check out this revolutionary UL Listed gas appliance connector. It streamlines your installations and is a great timesaver (up to 80% labor savings).
This .012" thick, bendable aluminum connector has built-in, twist-lock fittings for fast, easy, professional installations. It's adjustable in length, providing up to 4" per foot in compression (zero stretch). It only requires a 1" clearance to both walls and ceilings. It is used as a connector between appliances and Dura-Vent Type B Gas Vent. Dura-Connect is available in 3" and 4" diameters in 24", 36", and 48" lengths. It comes with a 10-year warranty.
Reply With Quote
  #13  
Old 2/21/09, 7:33 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: WH vent pipe

Quote:
Originally Posted by bsmith View Post
Good call Dale - Dura Connect - a new one for me. Jeff, you got it right too...
What about me!



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #14  
Old 2/22/09, 1:31 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 667
Default Re: WH vent pipe

Joe - you got it right too!!!



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help - Polybutylene Pipes Rick G Plumbing 39 2/12/09 9:16 AM
Identify ABS defective pipe mcyr Plumbing 6 1/29/09 7:39 PM
Pellet stove help chellickson General Inspection Discussion 22 8/10/08 5:41 PM
Do you put polybutylene in the Summary? jfunderburk Plumbing 36 11/27/07 12:56 AM


All times are GMT -4. The time now is 5:37 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts