Would this be considered back drafting? The inner cover could not be installed properly because of damage to the bottom of the water heater
|
| Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would check for an ongoing back draft use a match and at least note evidence of past back drafting and recommend further evaluation and repairs as a health and safety concern.
www.mauihomeinspections.com |
|
#3
|
|||
|
|||
|
Flame roll out like that is often caused by inadequate combustion air or a blocked exhaust flue pipe.
"An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#4
|
||||
|
||||
|
Without a internal cover in place I would simply say repair or replace.
It's broke and needs fixing before the house burns down. "Never underestimate the difficulty of changing false beliefs by facts." |
|
#5
|
||||
|
||||
|
Larry and Mike are correct. The condition is referred to as "flame roll-out," commonly caused by inadequate combustion-air, and if the unit is damaged, it should be repaired or replaced.
|
|
#6
|
||||
|
||||
|
Flame Roll out will also cause carbon build up on the burners so they would have to be cleaned as well or you loose effeciency, and because the gas isn't burned cleanly you may have a carbon monoxide situation. So as Michael and Jeff have already said it should be serviced or replaced which ever is cheaper and soon.
Gerry |
![]() |