Default 13/16" out of level over 32 feet... Acceptable?

Upon completion of a bottom of a 2 storey garage and employing a water line hose (5/16" I.D. clear hose) to ensure level accuracy however the outside temperature was approx. -5 degree C. therefore I used a bit of glycol car antifreeze mixed with the water and the water glycol mix did not balance out... Weird. A 5/16" I.D. 35' long hose filled with water/glycol and holding the two ends together and all the air was out and it was almost an inch different from the other. What the heck?
I found this out after the walls were built on a somewhat uneven foundation so each stud had to be 'custom cut' and now the building is out of level 13/16" over 32 feet. Is this within a tolerance? should I adjust each stud/jackstud over the the three 32' walls before I continue with the top floor? Or should I leave it and go with it? What would a normal person do?
Any response would be appreciated.
-Mark
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/12/11, 11:12 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: 13/16" out of level over 32 feet... Acceptable?

I'm a mason and that is unacceptable to me.

The problem comes from the industry's use of laser levels. Don't be impressed by the laser. A laser level still relies on trying to center a little bubble between two lines, by eye. If you are off a human hair at the level, you could be off several inches, 32 feet away. It's just like the sights of a gun.

I love the liquid line level you used, BTW. Here is how to make one: http://www.nachi.org/liquid-level.htm

If you tell me what you want your ceiling height to be, I'll tell you exactly how to fix it. It is a big deal, but not a big deal to correct.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 1/12/11 at 11:24 PM..
Reply With Quote
  #3  
Old 1/13/11, 6:53 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,492
Default Re: 13/16" out of level over 32 feet... Acceptable?

Before I would adjust each stud (p.i.a.) I would adjust it a the floor....cut the bandjoist
and joist as needed.
Reply With Quote
  #4  
Old 1/13/11, 12:18 PM
Randy L. Mayo, PE's Avatar
Randy L. Mayo, PE Randy L. Mayo, PE is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 372
Default Re: 13/16" out of level over 32 feet... Acceptable?

Mark

The difference in reading is due to a non-uniform mixture of ethylene glycol and water. Pure ethylene glycol is 12% heaver than water. If you were to pour pure ethylene glycol in one end and pure water in the other end as shown in the drawing the difference in reading will be 12% of the height measured. The more uniform the mix the less the difference will be. It would be very difficult to get a perfectly uniform mixture. Its best to use one type of liquid, I suggest using rubbing alcohol in lieu of water if you need some antifreeze protection.
Attached Thumbnails
13-16-out-level-over-32-feet-acceptable-waterlevel1.jpg  





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #5  
Old 1/13/11, 3:32 PM
Curtis M. Vilt's Avatar
Curtis M. Vilt Curtis M. Vilt is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Palmetto Florida
Posts: 890
Default Re: 13/16" out of level over 32 feet... Acceptable?

I was taught 1/4" in 100' is acceptable and that standard has stood the test for me.
But level is level not almost.
Reply With Quote
  #6  
Old 1/15/11, 5:02 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: 13/16" out of level over 32 feet... Acceptable?

Is it me or am I seeing more and more people coming to ask building questions on this board.
I shun the idea, because there are construction site for this very thing. Are we builders or inspectors?
When we work girls, I here the builders screaming and is this a MB for home inspection?
He has 1 post and is new.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #7  
Old 1/15/11, 5:23 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: 13/16" out of level over 32 feet... Acceptable?

Quote:
Originally Posted by ryoung7 View Post
Is it me or am I seeing more and more people coming to ask building questions on this board.
I shun the idea, because there are construction site for this very thing. Are we builders or inspectors?
When we work girls, I here the builders screaming and is this a MB for home inspection?
He has 1 post and is new.

I agree and frequently it is a non member who is asking the question .
I am afraid some day this could bite our Bottom ... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #8  
Old 1/15/11, 9:00 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: 13/16" out of level over 32 feet... Acceptable?

Quote:
Originally Posted by rcooke View Post
I agree and frequently it is a non member who is asking the question .
I am afraid some day this could bite our Bottom ... Roy
I agree 1000 percent ROY.
Now I read that government and others where paYing ATTENTION TO ALL STRINGS on home inspection association message boards.
How do you think they feel when we go beyond or practice or craft, profession or trade and help non members by giving them information that might be right or wrong about building?
We are residential or chimerical building inspectors.
Not code inspectors nor contractors. We might be trades men but that is or other job.
I think it is a dangerous practice and must-be stopped.
It can be misinterpreted by others.
Thanks Roy.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slab floor tolerance bking Structural Inspections 8 11/19/08 8:44 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Thermal Imaging Training / Classes dbowers Thermal Imaging, Infrared Cameras & Energy Audits 31 3/18/08 8:03 PM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM


All times are GMT -4. The time now is 1:23 PM.