4x10 Doug Fir floor joists, spaced 4' o.c. with 2x6 t&g pine decking on top. Is this acceptable for pine? House constructed in 2000. Thanks very much for your input.
Last edited by thance; 3/5/08 at 7:21 PM.. |
|
#2
|
|||
|
|||
|
Please Note:
grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
4x10 Doug Fir floor joists, spaced 4' o.c. are fine depending on the span of the joists.
Table R530.1 2006 IRC Minimum thickness of lumber floor sheathing: Joist or beam spacing 48” to 60” o.c. minimum 1½" T&G hope this helps Gary http://www.hsspropertyinspection.com/ |
|
#3
|
|||
|
|||
|
Please Note:
thance is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is great! Thanks, Gary. I appreciate it.
|
![]() |