Default 3/4" separation between chimney & house OK?

I just inspected a house that had a fireplace added in the basement about 25-30 years ago. The chimney has about a 3/4" (2cm) separation from the house. It was not visibly leaning, but there was some cracking noted on one side of the fire brick inside the fireplace.

According to the sellers, it was built as a "free-standing" chimney, not supported by the exterior wall. Obviously it was attached to the foundation at the fireplace itself.

Is this sort of gap between the chimney and the wall normal for such a structure or are the sellers "blowing smoke"?
Attached Thumbnails
3-4-separation-between-chimney-and-house-ok-2007_012035728-richland0042.jpg   3-4-separation-between-chimney-and-house-ok-2007_012035728-richland0052.jpg   3-4-separation-between-chimney-and-house-ok-2007_012035728-richland0054.jpg   3-4-separation-between-chimney-and-house-ok-2007_012035728-richland0050.jpg   3-4-separation-between-chimney-and-house-ok-2007_012035728-richland0041.jpg  


Last edited by fbartlo; 1/20/07 at 9:32 PM..
Reply With Quote
  #2  
Old 1/20/07, 11:21 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: 3/4" separation between chimney & house OK?

I'm no expert on chimneys, but I can certainly see a problem with moisture freezing/expanding in the 3/4" gap, particularly on the front side where rain and snow can go straight down behind the chimney.

Jim King
Reply With Quote
  #3  
Old 1/21/07, 10:18 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: 3/4" separation between chimney & house OK?

I can only imagine that it will get worse, I would defer it to a professional mason.
Reply With Quote
  #4  
Old 1/21/07, 11:02 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,362
Default Re: 3/4" separation between chimney & house OK?

Quote:
Originally Posted by prussell
I can only imagine that it will get worse, I would defer it to a professional mason.
Appears to me that there might be some structural concerns here as to why it is pulling away from the house.
It definitely needs further evaluations.

Marcel
</IMG>




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #5  
Old 1/21/07, 1:37 PM
Russell G. Cloyd Russell G. Cloyd is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Union, KY
Posts: 33
Default Re: 3/4" separation between chimney & house OK?

It appears that the chimney was not properly anchored to the house when it was constructed. Potentially very dangerous. I have inspected the aftermath of a chimney collapse due to the lack of proper anchoring.

Regards,



Russell G. Cloyd
Intra-Spec Home Inspections
& Code Consulting, LLC
859-586-4591
www.intra-spechomeinspections.com
Reply With Quote
  #6  
Old 1/21/07, 2:00 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3/4" separation between chimney & house OK?

Frank,
The gap appears to be consistantly spaced.Not wider at the top than at the bottom.If the gap at the top was wider I might be concerned that the chimney is leaning or pulling away.
Another thing that makes me think it is not moving and is free standing is the area at the soffit and facia.I see no gap there,only a messy paint job.
What did the flashing and shingles look like in that area.
A good poly type caulk would stop any water , wind, and insect intrusion.
That being said , there is absolutely nothing wrong with consulting a fireplace mason for an opinion especially if it helps you sleep better.

Cheremie
Reply With Quote
  #7  
Old 1/21/07, 2:00 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,362
Default Re: 3/4" separation between chimney & house OK?

Quote:
Originally Posted by rcloyd
It appears that the chimney was not properly anchored to the house when it was constructed. Potentially very dangerous. I have inspected the aftermath of a chimney collapse due to the lack of proper anchoring.

Regards,
Just wanted to point out that this fireplace chimney was installed after the fact and the foundation and anchoring to the Home is inadequate. Obviously from it's separation, further evaluation is required.

Marcel
</IMG></IMG>




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #8  
Old 1/21/07, 4:24 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Royal Oak, MI
Posts: 126
Default Re: 3/4" separation between chimney & house OK?

Thanks, everyone.

The fireplace and chimney were obviously designed that way, though it's apparent from the mortar on the inner edge there was not originally such a gap. I had originally suggested the agent check for permits to see that the construction was deemed up to code by the city and see just how long ago it was installed.

A Cheremie points out, the gap does appear to be consistently spaced, and I did not see evidence of significant recent movement, judging from the fascia caulk. If the gap were noticeably wider at the top than at the bottom and/or a noticeable separation of the caulk and the aluminum fascia wrap were evident I would be much more concerned.

My main concern is whether or not the chimney is likely to sink relative to the house, which would cause it to twist out, being attached to the foundation at the fireplace. However, the bottom of the fireplace is more than 42" below grade, which is considered an adequate footing here in Michigan, so I think the soil beneath the chimney is well compacted by now, and it's highly unlikely there will be any more significant movement of the chimney in the near future.
Reply With Quote
  #9  
Old 1/21/07, 11:10 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 419
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3/4" separation between chimney & house OK?

No matter how you look at it, I would still call it out for further evaluation because that gap is a perfect spot for moisture/insects. To me, that gap should be sealed no matter what IMHO.
Reply With Quote
  #10  
Old 1/21/07, 11:22 PM
Jeff Cardile Jeff Cardile is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mckinney, Tx
Posts: 19
Default Re: 3/4" separation between chimney & house OK?

absolutely call it out. CYA!
Reply With Quote
  #11  
Old 1/21/07, 11:57 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,487
Send a message via ICQ to kshepard
Default Re: 3/4" separation between chimney & house OK?

It might be fine if the chimney-supporting foundation is good, but consider how many situations we see every day that result from poor soil compaction. It seems to me that soil compaction beneath this type of structure is critical and tying the chimney to the home near the roof would be a prudent measure.

What is the advantage of a having a heavy chimney like this not tied to the home?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289


Last edited by kshepard; 1/26/07 at 5:06 PM..
Reply With Quote
  #12  
Old 1/22/07, 10:21 AM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3/4" separation between chimney & house OK?

Quote:
Originally Posted by kshepard
What is the advantage of a having a heavy chimney like this not tied to the home?
The fact of the matter is none of us knows wether it is tied in or not.
The block behind the brick veneer could very well be tied in. We just don't know. We werent present when it was built.
As far as soil compaction goes , if the footing was put on undisturbed soil there should be very little , if any , compaction. If the over-dig was so great in that area that fill dirt was required and then that should have been engineered .When something is engineered there is always stamped documentation. But after 20 or 30 years that document is probably long gone.
The brick and mortar joints on the chimney and house line up horizontally which tells us the chimeny is not sinking.The gap is a consistent width from top to bottom with no ill effects at the overhang which tells us it is also not leaning.
I would definately recommend a good quality caulk for obvious reasons and because if one tried to re-tuck point it the mortar would likely not stay bonded.
Personally I think it looks quite good for something that has been there for 20 or 30 years. But its just my opinion , I have no need to be right but if you add all these fine folk's opinions up ,the machine just might work!

Cheremie
Reply With Quote
  #13  
Old 1/26/07, 4:54 PM
Andy Frost Andy Frost is offline
New User
 
Join Date: Jan 2007
Posts: 6
Please Note: Andy Frost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 3/4" separation between chimney & house OK?

or . . . it could be the house that moved, not the chimney! regardless, it should be inspected by an engineer, not a mason.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stupid ASHI legislatin in Washington DEAD. gromicko Legislation, Licensing & Legal Issues 20 1/29/08 10:05 AM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior 6 10/13/07 9:10 AM
Houses for Sale Stand Vacant jburkeson1 Misc. Discussion 2 1/21/07 9:09 PM
Fireplace Enclosure jpope Interior 19 10/25/06 6:08 PM
Family's house is infested with mold rspriggs Ancillary Services & Additional Topics 6 1/28/06 3:05 AM


All times are GMT -4. The time now is 6:21 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147