Hello all,

I'm having a house built in Spring, TX and I hired an inspector to come through and make sure everything was on the up and up.

One of the first things he noticed was inadequate lateral support for the ceiling joists in the garage. Picture below.



I took this to my builder and asked that he install the bridging my inspector recommended. My builder said to me that he's going to install a "strong back" on top of the joists in the center of the garage according to R802.8.1 (I'm no expert, but I can't see any reference made to such a feature when I looked up the code). I went back to my inspector and reported what my builder said, who replied that a strong back isn't a substitute for bridging.

What is correct? Is a strong back or "rat run" adequate for lateral support? I appreciate your input.
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/26/13, 4:03 PM
William T. Misegades William T. Misegades is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 2,447
Default Re: Acceptable lateral support for ceiling joists?

R802.8.1 Bridging. Rafters and ceiling joists having a depthto-
thickness ratio exceeding 6 to 1 based on nominal dimensions
shall be supported laterally by solid blocking, diagonal
bridging (wood or metal) or a continuous 1-inch by 3-inch
(25 mm by 76 mm) wood strip nailed across the rafters or
ceiling joists at intervals not exceeding 8 feet (2438 mm)
.

I do a lot of phase inspections in Greater Houston area. I rarely see blocking anymore. What the builders typically do is place a 2x4 on its wider size, on top of the joists and a 2x6 on its thinner side butted up against the 2x4, which creates the "strongback"



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections

www.redfishinspections.com
Infraspection Institute Certified Infrared Thermographer Level I # 9631
"it's not just about how to turn on and tune the camera to make pretty colored spots!"
David A. Andersen, Woodlawn, TN
Reply With Quote
  #3  
Old 8/26/13, 5:32 PM
Marvin Maizel's Avatar
Marvin Maizel Marvin Maizel is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Palm Beach Gardens, Florida
Posts: 241
Default Re: Acceptable lateral support for ceiling joists?

Bridging for sure. Solid or diagonal. Not talking about code just quality. 8'0 oc min.
Reply With Quote
  #4  
Old 8/26/13, 5:47 PM
Randy Mayo, P.E.'s Avatar
Randy Mayo, P.E. Randy Mayo, P.E. is offline
InterNACHI Member
 
Join Date: May 2006
Location: Rolla, MO
Posts: 726
Default Re: Acceptable lateral support for ceiling joists?

Those joist are too big for a normal garage roof rafter. Is this a extra wide garage or do you plan to use the attic area as a room?





Randy Mayo, P.E.

573-201-8162

www.rlmengineers.com
Reply With Quote
  #5  
Old 8/26/13, 6:05 PM
William T. Misegades William T. Misegades is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 2,447
Default Re: Acceptable lateral support for ceiling joists?

Quote:
Originally Posted by rmayo View Post
Those joist are too big for a normal garage roof rafter. Is this a extra wide garage or do you plan to use the attic area as a room?
Those are very common around here. Typical for a 2 car garage (which is the norm here). No room upstairs, just empty space.



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections

www.redfishinspections.com
Infraspection Institute Certified Infrared Thermographer Level I # 9631
"it's not just about how to turn on and tune the camera to make pretty colored spots!"
David A. Andersen, Woodlawn, TN
Reply With Quote
  #6  
Old 8/26/13, 6:38 PM
Bradley K. Toye Bradley K. Toye is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 2,117
Default Re: Acceptable lateral support for ceiling joists?

Quote:
Originally Posted by rmayo View Post
Those joist are too big for a normal garage roof rafter. Is this a extra wide garage or do you plan to use the attic area as a room?
I saw that too. Looks like the ceiling joists are sized for a storage floor or future room. If used as a floor, I would use bridging. If just for ceiling joists, a rat run is fine. What do the plans say??



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
727-403-5029
Lecsi2@gmail.com
www.LeadingEdgeInspectionServices.com
Reply With Quote
  #7  
Old 8/27/13, 2:29 PM
Gordon Reese Gordon Reese is offline
New User
 
Join Date: Aug 2013
Location: Houston, TX
Posts: 5
Please Note: Gordon Reese is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Acceptable lateral support for ceiling joists?

Thanks again for your input. The builder won't give me the plans, so I have to take him at his word. I went back yesterday and saw that they put up one strong back, but with your comments I asked they install a second one since the garage is 20 feet wide. This is what they put up:



If y'all are good with it, I'm good with it.

I hear the big attics are called "Texas basements" so, everything is bigger here I guess!
Reply With Quote
  #8  
Old 8/27/13, 6:21 PM
Bradley K. Toye Bradley K. Toye is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Clearwater, FL
Posts: 2,117
Default Re: Acceptable lateral support for ceiling joists?

I agree, needs more than one run for that span. Those standard lumber joists will try to warp and pop your drywall nails, without proper bracing. I would install at 48" OC or sheet with plywood.



Brad K Toye
ITC/FLIR Level I Building Investigation Thermographer
FL Certified Building Contractor CBC034303
FL Certified Home Inspector HI 391
727-403-5029
Lecsi2@gmail.com
www.LeadingEdgeInspectionServices.com
Reply With Quote
  #9  
Old 8/27/13, 9:54 PM
Larry Kage, CMI Larry Kage, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: NW, MI
Posts: 12,086
Default Re: Acceptable lateral support for ceiling joists?

Quote:
Originally Posted by wmisegades View Post
R802.8.1 Bridging. Rafters and ceiling joists having a depthto-
thickness ratio exceeding 6 to 1 based on nominal dimensions
shall be supported laterally by solid blocking, diagonal
bridging (wood or metal) or a continuous 1-inch by 3-inch
(25 mm by 76 mm) wood strip nailed across the rafters or
ceiling joists at intervals not exceeding 8 feet (2438 mm)
.



I do a lot of phase inspections in Greater Houston area. I rarely see blocking anymore. What the builders typically do is place a 2x4 on its wider size, on top of the joists and a 2x6 on its thinner side butted up against the 2x4, which creates the "strongback"
Yes, 8' apart would be needed around here for that but we typically like bridging/blocking...different in different parts of the country and depending what it is used for.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/
____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
whis11 @ charter.net
The above post represents my personal opinion.
Reply With Quote
  #10  
Old 8/29/13, 7:25 PM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 582
Default Re: Acceptable lateral support for ceiling joists?

Gordon, I'm not good w/ it. this in reference to your statement above.. You've got the strongback laying on top of the ceiling joists in your last pic, but how well are they fastened? There's obviously no fasteners up from joists to the strongbacks as seen in pic. Even if strongbacks are properly fastened from above and down into, which we can't even verify from pic that is from below, the joists should have fasteners up thru them into strongback(s) to help w/ future seperation. Nails (unthreaded like screws) pull apart, that's why they should be nailed from both sides, for instance just as joist and rafters connections should be nailed together on both sides that are sitting on an exterior wall- to help prevent seperation.

See image below-



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com

Last edited by jkeresztury; 8/29/13 at 8:12 PM..
Reply With Quote
  #11  
Old 8/29/13, 7:37 PM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 582
Default Re: Acceptable lateral support for ceiling joists?

acceptable-lateral-support-ceiling-joists-strongback.jpg
Here is the image I use for strongbacks on my framing (predrywall inspections) in my reports.



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com
Reply With Quote
  #12  
Old 8/29/13, 8:58 PM
William T. Misegades William T. Misegades is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: Houston, TX
Posts: 2,447
Default Re: Acceptable lateral support for ceiling joists?

Hey Joe! How's it going in San Antonio? Long time no see around here
I've got to get down there so we can grab a few drinks (coffee or/and beer)
Hope the phase inspections are keeping you busy. It's been crazy around this part of TX



Where there is a Will there is a Way!

Will Misegades
TREC# 10465
RedFish Home Inspections

www.redfishinspections.com
Infraspection Institute Certified Infrared Thermographer Level I # 9631
"it's not just about how to turn on and tune the camera to make pretty colored spots!"
David A. Andersen, Woodlawn, TN
Reply With Quote
  #13  
Old 8/29/13, 9:06 PM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is online now
InterNACHI Member
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 3,435
Default Re: Acceptable lateral support for ceiling joists?

I think you'd have to do it like Joe says, or use proper bridging to prevent twist. A rat run on top may prevent separation, but not twist.




Michael A Clark, Certified Master Inspector«
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/30/13, 9:56 AM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 582
Default Re: Acceptable lateral support for ceiling joists?

Hey Will, going good. Can't wait for it to cool down some though. Getting old being high 90's or 100 every day. I know you have it about the same there in Htown.
Mike, I don't feel that a rat run will help as much w/ deflection / sagging as will a full strongback.



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com
Reply With Quote
  #15  
Old 8/30/13, 4:14 PM
Michael A. Clark, CMI's Avatar
Michael A. Clark, CMI Michael A. Clark, CMI is online now
InterNACHI Member
 
Join Date: Apr 2012
Location: Almost Heaven, WV
Posts: 3,435
Default Re: Acceptable lateral support for ceiling joists?

Quote:
Originally Posted by jkeresztury View Post
Hey Will, going good. Can't wait for it to cool down some though. Getting old being high 90's or 100 every day. I know you have it about the same there in Htown.
Mike, I don't feel that a rat run will help as much w/ deflection / sagging as will a full strongback.
concurred, Joe, thanks! How the heck ya been? I thought ya mighta fell off the face of the earth!




Michael A Clark, Certified Master Inspector«
Inspection Connection
St Albans, West Virginia

"Always tell the truth,
do what you say you will,
and do it Righter than Right...Always"

www.charleston-home-inspector.com
www.icwvhomes.com

mclark@icwvhomes.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is this an acceptable support?? sfogarty Structural Inspections 7 11/17/09 8:53 AM
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM
Where do I put the Aquarium? mcyr Structural Inspections 3 11/6/07 3:05 PM
Steel beam lateral support Mark Ellison Structural Inspections 10 1/16/07 10:40 PM

All times are GMT -4. The time now is 11:58 PM.
no new posts