Default Is this acceptacle????

I found four of these post installed this way today, why would you do this??

Thanks!
Attached Thumbnails
acceptacle-incorrect-post-1.jpg  



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
Find an InterNACHI certified Nebraska Home Inspector (and anywhere else in North America)
  #2  
Old 8/19/09, 3:06 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Is this acceptacle????

Quote:
Originally Posted by bhartley View Post
I found four of these post installed this way today, why would you do this??

Thanks!
Overkill?

Isn't that already a 2 x6 wall spaced 12" on center?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #3  
Old 8/19/09, 4:48 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Is this acceptacle????

Quote:
Originally Posted by mlarson View Post
Overkill?

Isn't that already a 2 x6 wall spaced 12" on center?
Probably a point load but typically the lally columns are anchored to the floor and the wall built around them or on footings and the floor poured around them.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 8/19/09, 4:52 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Is this acceptacle????

Quote:
Originally Posted by lkage View Post
Probably a point load but typically the lally columns are anchored to the floor and the wall built around them or on footings and the floor poured around them.
Maybe the safe is above there.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #5  
Old 8/19/09, 5:49 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Is this acceptacle????

No safe. The whole house is above.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #6  
Old 8/19/09, 6:07 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this acceptacle????

In order to comment, we would need to see what that post supports. A post of that configuration is acceptable if it is welded so that it no longer "jacks", and if it is anchored to the floor or to a footing. It doesn't matter to the post whether it's upside-down or right-side-up. If that post supports a center girder, generally such posts on 7-foot centers are sufficient. If it supports a steel girder, the spacing may be increased a great deal, depending on the depth and weight-per-foot of the goirder. The other end of the post should have a bearing plate that is either bolted or welded to the girder.

By the way, were there any electric receptables nearby?? =)

Last edited by Richard A. Hetzel; 8/19/09 at 6:09 PM.. Reason: wanted to poke fun
Reply With Quote
  #7  
Old 8/19/09, 6:53 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Is this acceptacle????

Richard, doesn't the slab need to be reinforced beneath a point load like that?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #8  
Old 8/19/09, 6:58 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Is this acceptacle????

Kenton,

I have never seen them installed in this way. They were fastened at the top to a steel beam. I deferred them.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #9  
Old 8/19/09, 7:11 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Is this acceptacle????

Quote:
Originally Posted by bhartley View Post
Kenton,

I have never seen them installed in this way. They were fastened at the top to a steel beam. I deferred them.
I see. It is supporting the end of steel beam.

Now how do we know if a real footing exists and not just the cement floor?



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #10  
Old 8/19/09, 7:39 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Is this acceptacle????

Interesting picture Buck.
Would you have a picture of a bigger spectrum view?

That's ok, I'll guess.

To me, that appears like a renovation project in the happenings.

A new wall is being constructed and a support column had to be moved.
The new plate was installed, using what appears to be a PSL member that I can't tell if it is treated or not, and the adjustable post was added to support the load above.
Now since this is an adjustable post, it means temporary, right?
Maybe not. The real lally column is sacraficial now and this one is picking up the load until that new wall is built.

Whether this adjustable column screw is down or up, dose not matter, the capacity that we do not know is still there.

Installing it over that PSL plate more or less distributes the weight on the assummed concrete floor, cause there is no footing underneath to pick up this load.

Now if the total picture shows that this new wall, once constructed, is picking up the load above, that adjustable column becomes a moot item of discussion.

It is obvious to me that this type of modification to framing, is not being done under the supervision of an Architect or Structural Engineer.

I would also question as to whether or not a permit was pulled for the work we see.

More pics would be helpful.

Hope my guess work makes sense.
Reply With Quote
  #11  
Old 8/19/09, 9:55 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Is this acceptacle????

I'd disclaim it and if I saw much of a load, or couldn't tell whether there was a load or not, recommend an SE.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #12  
Old 8/19/09, 10:06 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Is this acceptacle????

I would also Kenton, but I love to figure it out.
Reply With Quote
  #13  
Old 8/20/09, 4:29 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this acceptacle????

Quote:
Richard, doesn't the slab need to be reinforced beneath a point load like that?
Sure. There should be a footing, or at least a thickened slab, depending on the load coming down on the post.
Reply With Quote
Find an InterNACHI certified Nebraska Home Inspector (and anywhere else in North America)
  #14  
Old 8/20/09, 7:15 PM
jsupley jsupley is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Port St. Lucie, Fl
Posts: 34
Default Re: Is this acceptacle????

I blew up the picture, if it is supporting a steel beam, it is absoultely incorrect. IT should be attatched directly to the floor and should have a footer below it.
Toe nailing to a sole plate that WILL settle won't work. As someone else stated, looks like some do it your selfers hard at work. By the way, the colom looks to me like a floor jack seeing as how it has a smaller diameter where it attatches to the bottom plate. See if it has threads visible, all the coloms we install are purpose biult. Meaning they are built to an exact spect so as to bear from top to bottom, not adjustable.
Reply With Quote
  #15  
Old 8/20/09, 7:56 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Is this acceptacle????

It was wrong!! I sent it to a SE.

THANKS!!



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 11:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts