Default Air gap 0"

What do ya'll think about this flue? House is 1 YRO... The flue tag clearly states "Caution, 2" gap to combustibles or insulation is required."

Oh yah... Purlin supports are for wimps... We don't need them in Texas, our lumber is stronger... lol...
Attached Thumbnails
air-gap-0-imgp1185.jpg   air-gap-0-imgp1188.jpg   air-gap-0-imgp1186.jpg   air-gap-0-imgp1183.jpg  

Last edited by ccarrington; 5/17/06 at 8:08 PM.. Reason: add info
Reply With Quote
  #2  
Old 5/17/06, 8:50 PM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,394
Default Re: Air gap 0"

Joking aside, the installation could require a drywall chase, isolating the flue from the oxygen-rich atmosphere of the attic. Better check with a local specialist.
Reply With Quote
  #3  
Old 5/18/06, 1:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Air gap 0"

Cortland,

It may have started out with 2" of space....but as I see in may new homes we build and hire the guys to do the fireplaces.....if they dont support the flue correctly it can shift....probably what happened here.

Do as keith stated.....but yes I would call it out most certainly because the required space is no longer their....ALSO most i see will require a metal fire pan between floors.....this also helps to keep the flue centered.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 5/18/06, 2:57 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Air gap 0"

Good info here
http://www.duravent.com/docs/instruct/L204A_apr00.pdf
Reply With Quote
  #5  
Old 5/18/06, 3:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Air gap 0"

Great Stuff Mike......Yep I was right about the metal fire stop.....

If the flue tag states 2" then it must have 2" space.....and from this picture is also as stated does not have a fire stop....I would most certainly write it up.

The vent must be installed by the manufactures requirements...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 6:50 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts